3-Phase to Single Phase

06/07/2007 4:53 AM

I have a 3-phase delta supply with 208vac. I want to use the supply for a single-phase motor. How do I calculate the single phase voltage? Can anyone show me the way of calculating?

Thanks!!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: 3-PHASE TO SINGLE-PHASE

06/07/2007 5:12 AM

In Delta formation the Singe phase voltage is the same as the line voltage(3 phase)

So if you have a 3 phase 208v supply, then your single phase voltage is also 208v.

If you wish to change this voltage you can either use a single phase to single phase transformer, or a 3 phase to single phase transformer or a 3 phase Delta/ Star transformer to create a mid point and neutral on the secondary side.

I could show you easier with a drawing but I haven't found out how to import it in here yet.

Can any tell me how to import a drawing or picture into these posts.

Register to Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#3
In reply to #1

Re: 3-PHASE TO SINGLE-PHASE

06/07/2007 11:24 AM

In the editor window look for the small green camera.

Click on it, and in the next window click on browse.

Find your picture and Open

After it is inserted, you can mannually move it around within your text using your mouse

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Associate

Join Date: Mar 2007
Posts: 47
#6
In reply to #3

Re: 3-PHASE TO SINGLE-PHASE

06/07/2007 11:27 PM

Single phase to ground or neutral will be 120volts

Thanks for the tip on the Editor window I never noticed it before!

Don

Register to Reply
Guru
United States - Member - I am a Yankee Doodle Boy. Engineering Fields - Manufacturing Engineering - Old School is the best school. Safety - ESD - Safety Mgr that keeps the peace Hobbies - DIY Welding - My Motto:

Join Date: Jan 2007
Location: Broken Arrow, OK, USA
Posts: 838
Good Answers: 26
#10
In reply to #6

Re: 3-PHASE TO SINGLE-PHASE

06/08/2007 10:36 AM

On delta only 2 legs will go 115 to ground or neutral the third usually the center phase will read 208 to ground

__________________
If necessity is the mother of invention then is laziness the mother of necessity?
Register to Reply
Participant

Join Date: Jun 2007
Posts: 3
#7
In reply to #1

Re: 3-PHASE TO SINGLE-PHASE

06/08/2007 1:01 AM

can u send me the drawing to ma email directly?

tanbch@gmail.com

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: 3-Phase to Single Phase

06/07/2007 10:58 AM

You should all so have 110 single phase voltage. One leg to neutral

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Anonymous Poster
#4
In reply to #2

Re: 3-Phase to Single Phase

06/07/2007 12:13 PM

HA HA

V= I*R

Otherwise be more indeath with what you want!! there lots of formulas out there.

_______________

Thank you and good night

Register to Reply
Associate

Join Date: May 2007
Posts: 27
#5
In reply to #4

Re: 3-Phase to Single Phase

06/07/2007 12:21 PM

Star connection

Ip = IL

VL = 3 square root * IP ( or reverse if you have the line voltage)

Detla connections

VL = VP

IL = 3 square root * IP

3 phase power = 3 * VL * IL * cos (PF)

need more info on what you try to achieve!!

___________________

Thank you and good night

Register to Reply
Active Contributor

Join Date: Mar 2007
Location: US
Posts: 18
#8
In reply to #5

Re: 3-Phase to Single Phase

06/08/2007 7:59 AM

Normally, if you have 208 v 3 phase it comes from a Y connected secondary, which has 120 to ground/neutral. For a single load you can go from phase to phase (208 v) or if Y connected, phase to neutral.

There is a formula for 3 phase Y connected transformers. Phase to phase voltage over (constant) 1.732 equals phase to neutral voltage, (208/1.732=120). Conversly, single phase voltage times 1.732 equals phase to phase voltage (120 X 1.732 = 208).

TA TA

Register to Reply
Anonymous Poster
#9

Re: 3-Phase to Single Phase

06/08/2007 9:16 AM

First, is the single phase motor a 208vac motor? You don't say. If so, all you need to do is to use 2 phase legs of the delta connection to connect the motor. If it's 120vac motor, see if your/the transformer has a center tap (bastard leg) which can be used as a false neutral/ground and give you 120vac. Or use a 208vac primary to 120vac secondary single phase tranformer to get 120vac.

Typically delta connections at 240 volts nominal (where I'm located) are 240vac and wye connections are 208vac.

Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#11

Re: 3-Phase to Single Phase

06/08/2007 7:49 PM

Single phase 208 v is line to line, no neutral. Most 240 v motors are rated 200 to 240 volts. 208 runs higher amperage at load, same power. Check the motor nameplate.

RichH

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#12
In reply to #11

Re: 3-Phase to Single Phase

06/08/2007 7:50 PM

At 208 v, don't forget that you need a 2 pole switch to kill both lines.

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#13

Re: 3-Phase to Single Phase

06/21/2007 10:07 PM

Are you sure you have Delta-Connections NOT "Y" or "STAR" connections? Note: "Y" or "STRAR" have "Neutral-connection" also & Voltage between "Neutral-connection" & any Ph will be what will be Ph-to-Ph in "Delta", In your case you have to run your motor on 208V & it should be so rated.

Register to Reply
Anonymous Poster
#14

Re: 3-Phase to Single Phase

07/15/2008 2:37 AM

how we can calculate maximum demand of 300 kva connected load and devercity factor is 0.8.

Register to Reply
Register to Reply 14 comments
Copy to Clipboard

Users who posted comments:

Alvin (1); Anonymous Poster (3); double_j_b (1); Extremist (1); Haajee (1); NoSciFi (2); ozzb (1); Snakemike (1); tanbch (1); techno (1)

Previous in Forum: Thermal Overload   Next in Forum: Transformer Winding Temperature Indicator

Advertisement