11/18/2013 11:48 AM
I have a pressure transmitter which is on a vertical pipe (10") to measure the fluel gas pressure. The tapping with isolation valve is at about 1.9 meter elevation from Ground. No platforms can be given in the location for accessability and maintanence because of piping all around. Is it possibe to mount the instrument remotely at 1.4-1.5 elevation about 2 meter away from the pipe? what is the normal practice in such a case?
Re: Instrument Mounting for Gas service
11/18/2013 11:54 AM
It is possible, however, consideration needs to be given to the prospect of liquid building up in the pipe and causing the instrument to give a pressure error equal to the difference in elevation multiplied by the density of the liquid multiplied by acceleration due to gravity. If that is tiny in comparison to the signal, it could be ignored. If the tapping line can be regularly drained safely, then that is another option. A third possibility is to mount the instrument off to the side at the same elevation where access can be gained to it more easily.
There is no such thing as <...normal practice...> beyond that in the facility's internally-published Instrumentation Standards Manual and site circumstances will direct the way forward.
11/18/2013 12:21 PM
Adding one more point to the above question.. In case if the instrument is at an accessable height can we directly mount the instrument side ways on a vertical line.( on the isolation valve directly threaded. Or should we have to mount the transmitter also vertically such that there is no condensate at the instrument end?
11/18/2013 12:40 PM
Follow the instrument manufacturer's recommendations.
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member
Good Answers: 73
11/18/2013 7:54 PM
"Follow the instrument manufacturer's recommendations."
I completely agree PW. All of the manufacturer's of this type instrument publish extensive support information, usually available on-line. There's really no other way to go than their recommendations. Here, for example, is a file I pulled up in about 10 seconds:
https://www.honeywellprocess.com/library/support/Public/Documents/34-ST-25-35.pdf
I've installed many pressure transmitters in the last 39 years, and I ALWAYS read and follow the information provided. If I can't get the info I need, I call tech support.
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
11/18/2013 8:59 PM
Did they transmit the data with symaphores 39 years ago?
Good Answers: 73
11/18/2013 9:50 PM
Almost:
or:
Good Answers: 176
11/18/2013 1:36 PM
Install a Tee at the end of the extended impulse line, with the Tee in a vertical direction.
Install a drip leg on the bottom port of the Tee where condensate can collect away from the transmitter.
Pipe the pressure transmitter from the top port of the Tee.
Pressure transmitters with small DP (draft range) or absolute ranges are sensitive to mounting orientation which has an zero shift effect on calibration. Somewhere on a gauge pressure transmitter there is an atmospheric reference port that needs to be kept clear of ice or dirt. You'll have to check the manual to see about those points. But digital displays are made to rotate since it is not uncommon to mount the transmitter sideways and the display needs to be readable.
The condensate doesn't disappear over time, it accumulates, so a maintenance schedule is needed to empty the drip leg.
Good Answers: 73
11/18/2013 7:57 PM
That's good info Iris.