Hello every one!
it is requested to reconfigure the upper range value of a flow transmitter to a higher value, which is ok by the transmitter (the maximum dp limit by the transmitter is greater).
from data sheets:
- flow range : 0 - 150 m3/hr
- dp range : 0 - 250 mbar
the required values:
- flow range : 0 - 400 m3/hr
- therefore the calculated dp should 1.78 bar!
some data are confusing me :
- in data sheets it is mentioned that the maximum flow rate is 209.2 m3/hr(dp 448mbar).
- in orifice plate calculation sheet the max. flow rate is 70 m3/hr, temp. 25 C, viscosity 0.72 cP, flowing pressure 9.3 Bar, dp 250 mbar, densty 994.3 kg/m3.
what does it mean that the flow rate is 70 m3/hr at dp 250mbar (through calculation from datasheets it should be 150 m3/hr) ?
the pipe size is 8'', d/D is 0.35858938.
what is the max dp and flow accepted by the line?