Anonymous Poster #1

Difference of Power Factor Reading

11/24/2013 8:55 AM

Dear Engineers,

We are facing a problem of diffrent reading of power factor reading in two devices those are installed at Medium voltage switchgear feeding to a synchronous motor.

Analogue P.F meter reading is 0.6 (Leading ) while Digital Protection relay readin 0.1 leading.

Note: Measured input voltage & current magnitudes are same on both devices.

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Difference of Power Factor Reading

11/24/2013 11:07 AM

A difference 0.5° seems like just a tolerance error in measurement to me. You say that the measured input and current magnitudes are the same, I suspect that they really are not. I suspect that the resolution of one or two of the four measurements produces a tolerance window larger than 0.5°.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2
In reply to #1

Re: Difference of Power Factor Reading

11/24/2013 1:17 PM

Red, A power factor of 0.5 translates to an angle of arc cosine (0.5) or 60 degrees, arc cosine (0.1) or 84.25 degrees. Both are lousy power factors but 0.1 is almost all reactive. More than likely OP problem has to do with metering ratio settings on the relay, especially since his actual measurements are consistent.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #2

Re: Difference of Power Factor Reading

11/24/2013 2:23 PM

If the meters are set wrong then how can any of the metrics be considered at all as valid. I tried to interpret the sparse information we do have in a fashion that agrees with itself. If we had the data on the measured current an voltage data along with some phase component then we could identify if these numbers are the dimensionless power power factor values and which or neither are accurate. We still might find that these numbers are the phase angle in degrees or even possibly radians (that would be odd) and that these two meters assume a balance between three phases of currents but the meters are measuring. The difference comes from a single phase current load returning on the neutral.

We have another case of insufficient information to come to any conclusion.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Difference of Power Factor Reading

11/24/2013 10:49 PM

Are there harmonics in load & are both meters reading true pf?.

__________________
pnaban
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5

Re: Difference of Power Factor Reading

11/25/2013 2:30 AM

You should be busy reading the manuals or any other references for the PF metering devices that only you can identify.

Can you borrow a third unit to see if you get any correlation?

If you're really lucky you'll get a third value to really mess with your brain.

Start Googling and learning.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#6

Re: Difference of Power Factor Reading

11/25/2013 7:34 AM

Neither may be correct. An accurate P.F.measurement requires a Schering Bridge or a modified shielded Schering Bridge.

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #6

Re: Difference of Power Factor Reading

11/25/2013 8:00 PM

Schering bridge? That's used for measuring capacitance, usually in RF circuits. Although you might be able to use it to the power factor of cable insulation, it's unlikely that you would use it to measure the power factor of an industrial facility.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Power-User

Join Date: Dec 2008
Location: Anthem, AZ
Posts: 392
Good Answers: 8
#8

Re: Difference of Power Factor Reading

11/25/2013 10:06 PM

This complex number measurement can be made using the average of the complex FFT. You have to trigger each measurement in order to average the single channel FFT. Use at leaset 100 averages.

The result will be the real and imaginary components of EACH harmonic. The ratio of each I over R is the PF for each harmonic (check that; I may have it upside down).

If there are several strong harmonics, they can be vectorially summed using standard complex number addition.

Reply
Associate

Join Date: Jul 2007
Location: São Mamede Coronado - Portugal
Posts: 27
Good Answers: 3
#9

Re: Difference of Power Factor Reading

11/26/2013 1:11 PM

Although the input readings are of same magnitude, you have to check the sequence and phase between voltage and current inputs. For example, with PF 1 the angle between Urs and It are 90º...

__________________
Best regards, SMCTR
Reply Score 1 for Good Answer
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#10
In reply to #9

Re: Difference of Power Factor Reading

12/04/2013 3:34 PM

SMCTR, you are the only one with a plausible answer except that the phase between the line to neutral voltage and the line current is 0 at PF=1.

OP, make sure that the phase A , B, C PTs are connected at the right location on the meter. Same check for the CTs.

Another possibility is the configuration of delta or wye of the PTs or CTs and the power meters. They may be both wrong.

Good luck

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers: