About Distribution Transformer Characteristics

12/01/2013 10:55 PM

I just want to know how this distribution transformer maintain voltage level in distribution side .if we step up the voltage again and again means current decrease and what is the use of maintain voltage level in constant level.

example:in distribution side we have only 190v then we will use one distribution transformer in there for step up the voltage to 230v in this situation what will be the characteristic of additionally adding transformer.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: About Distribution Transformer Characteristics

12/02/2013 1:06 AM

Who is "we"? Normally when the secondary line voltage is out of specs. (too low), the power company can step this up with the distribution line transformer (the ones on the poles) Call them.

To answer your question: your transformer should have 190 Volts primary and 230 volts secundary with minimal the power rating of your load. It is a cost you can avoid with a telephone call.

You cannot just do that, because the problem can be in the supply by the power company and adding your transformer just makes their (eventual) problem bigger.

__________________
Plenty of room here
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: About Distribution Transformer Characteristics

12/02/2013 1:27 PM

Stepping up the voltage is handy if you have voltage drop issues on site (there are legal requirements about the power transmission company providing voltage regulation within a certain tolerance like 10% for example, but I won't go into this as you have not mentioned your country or site details, so I will assume this is your voltage drop problem to fix and not the power or lines company's).

Be aware however that if you step up the voltage with a transformer by 21% then if the supply voltage jumps back up to 230V (for example the load on the 230V line reduces, which is what is causing the voltage drop in the first place) you will be running your equipment at 278V which is likely to cause damage.

Consider instead using voltage regulators or UPS's on sensitive (light load) equipment that cannot handle the 21% voltage drop (many pieces of equipment will work fine so you shouldn't need to protect everything depending on what is on your site), adding or replacing the high voltage transformer with a suitably sized one to combat the voltage drop on the 230V supply side (if you are talking about a large site), adding voltage regulation or power factor correction (depending on the type and duration of the 230V voltage sags), checking the legal obligations of your power or lines company to see if they have to fix it instead, etc.

__________________
jack of all trades
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: About Distribution Transformer Characteristics

12/02/2013 3:20 PM

From what you stated it seems that you are on the tail end of supplier's transformer and it is the transmission loss and you need to improve conductor size to reduce transmissions loss. If your voltage is fluctuating from 230 to 190 volts, it means the voltage is dropping depending on the load conditions of customers who are ahead of you. In that case solution is to install voltage stabiliser using auto transformer and voltage sensing circuit and operate the position of the transformer by a servomotor operated by voltage sensor. Such servo voltage controllers are available in the market . Buy and install one with correct kVA rating depending on your load.

Register to Reply
Active Contributor

Join Date: Dec 2013
Location: Dubai
Posts: 11
Good Answers: 1
#4
In reply to #3

Re: About Distribution Transformer Characteristics

12/04/2013 11:00 PM

Thanks for your replay

I have one more doubt Mr.abraham if am putting a distribution transformer in single phase 230 voltage sytem due to voltage drop at the end side of distribution sytem. Then what wiil be selection parameters for that transformer?