Cab Use Just One Pole of MCCBs

12/10/2013 7:07 AM

In one panel 1 phase 120v mention that the main breaker must be 300A. Now I want to know it is possible to use a 3 poles MCCB and use just one phase because we cannot find a 300A MCCB 1 phase.

Thank you for your help in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Cab Use Just One Pole of MCCBs

12/10/2013 8:45 AM

Yes. To break line ony, wire line to L1, T1 to L2, T2 to L3, load to T3.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#9
In reply to #1

Re: Cab Use Just One Pole of MCCBs

12/11/2013 1:56 PM

I disagree. It may be ok to do this with a relay. NOT a 100 amp circuit breaker

Register to Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#10
In reply to #9

Re: Cab Use Just One Pole of MCCBs

12/11/2013 2:34 PM

I think the implied question in the OP was to use a 3P 300A MCB, not a 3P 100A.

__________________
Smart as a post and twice as fast.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#11
In reply to #10

Re: Cab Use Just One Pole of MCCBs

12/11/2013 2:43 PM

Same answer. 100 amp or 300 amp. is not a way to use any 3 phase breaker

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#12
In reply to #11

Re: Cab Use Just One Pole of MCCBs

12/11/2013 2:45 PM

Agreed. hopefully it is only an emergency fix until a proper one can be obtained, and the proper safety warnings are posted.

__________________
Smart as a post and twice as fast.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: Cab Use Just One Pole of MCCBs

12/10/2013 1:42 PM

Option two would be to use a three phase 100 amp unit and parallel the three lines to work as a single 300 amp unit.

In most national electrical code books paralleling three, and in some cases as many as six, medium sized units to work as a single larger amperage unit is allowed.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #2

Re: Cab Use Just One Pole of MCCBs

12/10/2013 4:08 PM

Yes, but...

At least in my code (the Canadian one), parallel single phase breakers, operating at 750 Volts or less, must be assembled as such by the OEM. They cannot be field assembled and used.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#5
In reply to #3

Re: Cab Use Just One Pole of MCCBs

12/10/2013 11:58 PM

A next solution could be to turn the 3 phase 300 Amps into single ones. Their levers are mostly connected together with a removable device: be it a pin that connects the 3, or a bridge that fits on top of these.

Leaving this connection in place will make the 300 Amps not correct, since only one action in 1 breaker needs to overcome 3 loads. In a bad scenario this one connected part could catch fire before disconnecting I guess.

A handy electrician can fix this. Just don't know if it is OK with the code. Please advise.

__________________
Plenty of room here
Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#7
In reply to #5

Re: Cab Use Just One Pole of MCCBs

12/11/2013 12:45 PM

Using any 3 pole cb for single phase will work. A 3 phase breaker will not always have a 3 phase fault. Any one of the phases are manufactured to trip all 3 at the rating of that circuit breaker. Whether it qualifies as a single phase disconnecting means is another matter.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#6
In reply to #2

Re: Cab Use Just One Pole of MCCBs

12/11/2013 8:49 AM

TCM - If I did that, ( 3/100 ) I would always worry that sooner or later ( probably sooner, just as I am putting my boat in the water on my first day of vacation ) the weakest of the 100A poles would trip out, and I would be called on the carpet for undersizing the MCB.

If I installed a 3/300 breaker I would series-wire the poles, to occupy the lugs.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#8
In reply to #6

Re: Cab Use Just One Pole of MCCBs

12/11/2013 1:42 PM

I just go by what I have seen done in commercial panel applications. So far tying all three circuits of a three phase breaker together to make a larger single breaker is a very common and acceptable thing to do especially in special application circuits.

Countless home electrical breaker panels have this sort of setup for the primary breaker. Many use four breakers set up as two parallel smaller breakers tied together on each leg ganged together to make a single 150 - 200 map main unit and I have never heard of one false tripping due to just one of the two on a single side getting weak.

To be honest at those current capacities they are rarely ever loaded down hard enough or long enough to trip anyway.

Whereas if you are using three 300 amp breakers all in series you have 6 connections plus three sets of breaker contacts all having to handle up to 300 amps each without getting a hot spot or the combined resistance not creating a overheating issue.

Using three 100 amp circuits in parallel doesn't have a single connection or contact set carrying over 100 amps which means far less peak heat being generated in the unit.

Up front cost and connections wise using a three phase 100 amp breaker as a 300 amp single phase unit cost less and makes for far less wiring work plus distributes the load thee ways instead of no ways.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#4

Re: Cab Use Just One Pole of MCCBs

12/10/2013 11:48 PM

...will it work? yes.

but depending on your code, it may not be allowed. depending on whether your inspector knows the code that well. .....and as for paralleling, that may be against code also, depending on wire size you intend to parallel.

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13

Re: Cab Use Just One Pole of MCCBs

12/12/2013 3:44 AM

Common practice go right ahead. Just label it.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); dvmdsc (1); JohnDG (1); LongintheTooth (3); Munster (3); North of 60 (1); tcmtech (2); Wal (1)

Previous in Forum: Using a Schmidt Hammer   Next in Forum: Vertical Storage Vending Solutions

Advertisement