Disconnect BOU Honeywell DCS TotalPlant Alcont

12/19/2013 8:41 AM

Hy, we have a Honeywell DCS TotalPlant Alcont, to which we added a new digital output module BOU. On this module there is a Disconnect or D switch which sets all the channels on the card into a passive state. We put this switch to Connect position, but no outputs are enabled.

Has anyone seen this before? How can we solve this problem?

In the Honeywell manuals it is mentioned: For card replacement the outputs are reliably switched off by turning the front panel DISCONNECT lever to the right. This must be done both to the old and the new card. The lever must not be operated during normal operation, because an erroneous control would be caused by clearing all the output channels.

Thank you

__________________
...anything that can go wrong will go wrong...
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Disconnect BOU Honeywell DCS TotalPlant Alcont

12/19/2013 9:00 AM
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Disconnect BOU Honeywell DCS TotalPlant Alcont

12/19/2013 9:27 AM

As I do not know this equipment, the following is pretty generic to such systems...

Are you replacing a card or adding a new one? You said you were adding a card.

If you are adding one...

The switch you enabled on the card is a "hardware" interlock. Besides the hardware needing to be in the enabled configuration, it is a pretty sure bet that you will need to go over the software configuration for this system to let it know the new card is there.

The software will need to add the physical bus addresses for the discrete I/O points into its operating environment. You may also have to "declare" the I/O points in other areas of the software.

You cannot just plug in the board, enable its hardware portion and expect it to work.

Also... check the card out... it may had address switches on it that must be set properly.

Time to read the manuals...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Disconnect BOU Honeywell DCS TotalPlant Alcont

12/23/2013 9:52 AM

Hopefully you followed the directions: "The lever must not be operated during normal operation, because an erroneouscontrol would be caused by clearing all the output channels.

If you installed the module into a running/operating system you very well may have damaged the module or you have caused a major fault in the system.

I have seen this same error on the Honeywel TDC 3000 DCS systems and normally it is caused by improper configuration instructions.

The Honeywell DCS systems I have worked on are not "Plug and Play" and require configuration parameters to be entered via the engineering node telling the programming where the module is being installed, the type of module, and the address block (tags)assigned to the I/O.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Participant

Join Date: Jul 2019
Location: Indonesia
Posts: 1
#4

Re: Disconnect BOU Honeywell DCS TotalPlant Alcont

07/10/2019 7:57 PM

For the first this BOU card must configuring , by Engineering design computer.

Second step, create any block that use one channel of this new BOU

Try to on and off SCAN or cycle time of this block, and see your BOU now already work properly...

Tq...i am happy can help you...

best regards

Zulyadein34@gmail.com

__________________
My facebook is Zuluzulu
Register to Reply Off Topic (Score 5)
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

lyn (1); North of 60 (1); SHOCKHISCAN (1); Zulyadein (1)

Previous in Forum: South African Low Voltage Distribution Network Configuration?   Next in Forum: Electric Motors

Advertisement