Hi, I'm new here
I've come here becuase i find promising answers in this site :)
Here in India, we have 230V AC,
I have a 3 phase digital energy meter to record my KWH readings.
we have 2nos 3-Phase 11-ton Ducted Split AC's and they run fine
we have driven two ground rods at the utility entrance and connected
to the neutral, fearing a neutral disconnected situation will damage all
out appliances
=============================
ok let me describe you my problem
i recently installed 2nos 2 KVA Pure Sinewave 24v inverters. that too
from ebay, i trust it really..It is from a company Called Medi
the inverter has
-INPUT PHASE
-NEUTRAL (COMMON TO INPUT AND OUTPUT)
-OUTPUT PHASE
-NO GROUND TO BE CONNECTED AS TOLD BY THE INVERTER COMPANY
it has a digital LCD display at the front, which gives input voltage, output voltage on battery mode, charging status and heat
(it gets upto 70degrees celcius and fan starts to run to cool down)
I has been installed like the diagram i have attached/linked(just the reference drawn in paint, not the original)
http://imageshack.us/a/img801/2559/7n50.png
the problem is when i switch off the mains(isolator) the neutral floats as it has no EB neutral connected and this is normal...
BUT, when i switch off the 2Pole input MCB's at any of those 2
inverters(or both), the inverter powers the load with battery
power(normal)
it shows "INPUT=060V" THIS SEEMS ODD!
I am not disconnecting the neutral as, it receives the neutral from the output wiring side, as shown in the picure
at that time the input voltage was arounf 270V....so i asked my
lineman to adjust at the transformer side and after repeated shouting at
him, he reduced it to 230V-240V
NOW, when i switch off the 2Pole input MCB's at any of those 2
inverters(or both), the inverter powers the load with battery
power(normal)
it now shows "INPUT=023V" THIS SEEMS ODD! after the voltage reduced
THIS OCCURS ONLY WHEN THE INPUT IS OFF AND THE INVERTER POWER SWITCH
is on (OR the inverter dc->AC power switch/ is on (at the front
panel).that is inverter runs on battery. if it is off, THEN "INPUT=000V"
THIS IS FROM THE DATE OF INSTALLATION
---
now I have observed that I'm getting shock from the battery (+) or (-)
terminals if the input MCB is on (if inverter 1 INPUT 2P MCB is off,
then i dont get any shock, same with inverter 2)
I have not checked this at the time of installation of the inverter(2
months back), as everything is working perfectly(very good backup too)
except this odd thing i have described.
I contacted the inverter manufacturer (NIXOWN, the inverter motherboard is from MEDI)
they said to check
-input neutral,(if this fails, lights will not work, only blinking)(and i have 2 extra neutrals at service entrance)
-if phase - neutral is reversed or not (will check tomorow)(though
the inverter can detect if it has been reversed, and notify via the LCD
display, and stop functioning temporarily, they asked me to double check
it)
I have inverter manual and whole circuit board working and schematic detaliks in a pdf, in case you need it i can link to it
and i have seen video of the same inverter in youtube, it shows "INPUT=000V"
so i hope you people to help me and solve my problem help me troubleshoot the problem?