Stability Room Design

12/22/2013 3:10 AM

If any could help about the the arrangement of heater, humidifier and volume damper at the end of supply duct.

Is there any standard arrangement of these three equipment at the end of supply duct or no matter if they put randomly.

else, if any would gratefully send useful links about room design.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Stability room design

12/22/2013 10:07 AM
Register to Reply
Member

Join Date: Apr 2012
Posts: 8
#2
In reply to #1

Re: Stability room design

12/22/2013 10:21 AM

Thank you very much

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: Stability Room Design

12/22/2013 8:42 PM

putting the heater upstream of the humidifier isn't desirable

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#4
In reply to #3

Re: Stability Room Design

12/22/2013 11:00 PM

Fredski-

Correct me if I'm not correct. Aren't humidifiers put downstream of the heaters (heater upstream of the humidifier)? The air goes through the heater and then the humidifier. The heater heating the air reduces the relative humidity and the humidifier raises it back up somewhat.

A simple example would be a residential forced air furnace. The return air is heated and then goes through/adjacent to the humidifier. From there it goes through the distribution air ducts to the room registers.

Perhaps a typo error? I have them too.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6
In reply to #4

Re: Stability Room Design

12/23/2013 8:01 AM

you most certainly have it correct

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#5

Re: Stability Room Design

12/23/2013 3:35 AM

At the end of supply duct???. Please check it. Generally Air Handling unit is the device which is used to condition the air based on heat load calculations and Psychrometry analysis.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abueed (1); Fredski (2); lyn (1); mrswamy (1); old salt (1)

Previous in Forum: Single Pump or 2 Pumps Running with VSD?   Next in Forum: "5IK40GN-A" Oriental Motor Induction Motor: Wiring Diagram

Advertisement