Anonymous Poster

why this occure

06/09/2007 8:45 AM

we have 12 v dc come from instrument used to measure flow and when we put 12 vdc on the coil of relay which working with 12 vdc the coil not energize and at the same time when we measure the volt between the coil termnal we found it become 2 mv and when we remove the tow teminal from the coil and measure dc volt we fond it 12 vdc so we need why this occure

coil restance =250 ohm

intrument can drive load at 100 mA

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: why this occur

06/09/2007 12:53 PM

You may have a bad switching device. Not knowing what is switching to provide power to the coil. Look to that device for bad contacts. Carbon build up on the tips of contacts can in a no load situation show full voltage at the device it is operating. Under load may heat up dropping the voltage. Maybe even create an open.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#2

Re: why this occure

06/09/2007 1:07 PM

You connect the coil at no load and measure the voltage.Then we can say this reason

Reply
Anonymous Poster
#3

Re: why this occure

06/09/2007 4:00 PM

You say your instrument can drive loads up to 100 mA. and your coil resistance is 250 ohms 12x12 divided by 250 thats 0.576A 576mA . you are choking your power supply.

Reply
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#4
In reply to #3

Re: why this occure

06/09/2007 7:17 PM

You wrote 12x12 divided by 250 thats 0.576A

This is incorrect. 12/250 = .048A well within his power supply spec. Your formula calculates the watts (V2/R=Watts). However your statement regarding choking the supply still sounds like the logical answer.

To the POSTER: I would try a purely resistive load (around 150 ohms) and proove the power supply can source 80% load. The inrush to the relay coil (inductive load) could be triggering the short circuit (crowbar) protection of the flow device power supply, meaning you can not use the flow device to drive the relay directly.

Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#5

Re: why this occure

06/10/2007 12:55 AM

The 2mv looks like your instrument was only good for a few milliamps, or perhaps you have a 12vdc coil with a diode as a suppressor around it and you have the polarity backwards. Follow suggestion of using a known purely resistive load to verify drive capability of instrument.

Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#6
In reply to #5

Re: why this occure

06/11/2007 2:48 AM

The diode would generate approx 0.6 V.

__________________
"Here we are now, entertain us"
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#7
In reply to #6

Re: why this occure

06/12/2007 12:16 PM

Only if he has some drive capability. I think his instrument is saddly lacking for the load he is attaching.

Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#8
In reply to #7

Re: why this occure

06/13/2007 3:09 AM

He should be able to drive 100mA and still giving its nominal power.

It looks to me that there is a short somewhere.

What they can do is take a power supply module and try to attract the coil from the leads that are connected to the instrument. measureing the voltage at the power supply, the coil and measuring the current.

How long is the connection between the coil and the instrument, what is the section of the connection cable.

__________________
"Here we are now, entertain us"
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#9
In reply to #8

Re: why this occure

06/13/2007 12:45 PM

We are in full agreement.

There is something fishy, and it needs to be systematically troubleshot.

1) Instrument is nfg?

2) short?

3) load is not what it appears?

4) (long shot) power supply for instrument is nfg?

Reply
Active Contributor

Join Date: Jun 2007
Posts: 16
#10

Re: why this occure

06/16/2007 9:33 AM

it looks like you have a Short circuit on the relay coil, may be caused by dirt or moisture, you need to check the relay coil again to confirm the correct resistance of the coil.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: why this occure

06/18/2007 4:15 AM

Is this instrument an analog device, doing flow measurement, or a switching device? The query arises from the mix of "measure flow" and "coil not energise" in the posted question.

What is the maker and part number of the device, and what is the measurement technique used to convert the flow to an electrical signal? Moving vane? Pelton wheel? Variable area? Electromagnetic? Ultrasonic? Mass flow? Vortex shedding?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#12

Re: why this occure

06/21/2007 10:00 PM

What do you mean by: ************ Quote ************* we have 12 v dc come from instrument ... .. instrument can drive load at 100 mA ************ Un-Quote ************* 1. I assume that battery of your flow-meter is connected directly from its terminals to coil. 2. you are measuring voltage across coil terminals when connected to the battery of your flow- meter & it is 2 mV on-load. Then it is clear that the battery is either of low capacity to handle load more than say 5 ma[can just work with flow-meter] or if it is at least 1AH capacity it has gone bad. What I could make out from your post that You have: 1. a Flow-Meter whose internal battery is 12V & can deliver 100ma. To which load? [12/100]*1000 =120 ohms It means your battery is capable to deliver 100 ma to 120 ohms load. How you calculate this? 2. The coil you are testing is [coil resistance =250 ohm]. But the current of the coil @ which it energizes is not mentioned by you. 3. What is the Type & capacity and how long you have used it?

Reply
Anonymous Poster
#13

Re: why this occure

07/03/2007 3:31 AM

It seems there a large voltage drop acros the cable from the instrument to the relay coil.There maust be approx 12 V drop across the cable. Or simply you should go for 120 or 100 Ohm resitance coil so that akes for 12 V.

he given coil is 250 x 100 MA= 25 Volt sonot menat for a instrument of 12 V .

Any takers

Reply