Dear All,
I am new in this forum, but trying to have good technical discusssion. thanks before.
I have a case that electrical equipment inside a gas turbine compressor is suitable for Class 1 division 2 whereas in the specification it shoud be Class 1 Div 1.
So to justify the deviation and to have safety operation on site, there are some item to be consider(as per my study, please cmiiw):
- provide adequate ventilation by natural or artificial means, to know the adequate ventilation rate, we need to know the fugitive emission rate inside the compressor enclosure.
- i calculated the fugitive emission rate and the minimum air changes introduce to the compressor enclosure based on NFPA 30 Annex F.
- from API4589 resulted that from equipment that suppose not to emit during normal condition, actually exist what we call "fugitive emission" and in this standard there are number of fugitive emission rate can be found for onshore and offshore O&G installation.
- in terms of a gas turbine compressor there must be somehow "emission leak", consider that this is a high pressure and rotating machine dealing with gas.
- provide redundant fire, gas and heat detector inside the enclosure, to alarm the system if any flammable vapor or gas concentration 20% of LFL.
to all CR4 experts, please put your inputs on these steps, whether it is the correct procedure to calculate the adequate ventilation. and whether i need to have other safeguards to be considered in the system.
thank you very much,
RS-2013