Dear all friends
I am looking for the formula of centrifugal fan design :
Flow rate : 800l/s
SP : 300 pascal
Please give me an advise.
many thanks
Re: ventilation fan
01/03/2014 7:36 AM
Check GreenHeck fan selection data that is available in a large variety or other standard make fan data/curves available in your area. This will be a within 1HP fan
Good Answers: 137
Re: ventilation fan
01/03/2014 7:54 AM
You've given the main parameters a supplier needs to select a fan, assuming SP is the pressure rise (not suction pressure). If not you need to specify pressure rise.
Also helpful to give inlet pressure and temperature, and gas density. If you don't give these he's likely to assume atmospheric pressure, ambient temperature (say 15°C) and air.
Re: Ventilation Fan
01/04/2014 12:12 AM
0.5HP (half HP) motor would suffice
BHP=cfmxSP(inches)/6356/fan efficiency (0.75say)
Good Answers: 137
Re: Ventilation Fan
01/04/2014 6:43 AM
OK if SP is the pressure rise. OP hasn't confirmed. If so I don't know what the S stands for.
Good Answers: 117
Re: Ventilation Fan
01/04/2014 9:22 AM
are you texting from your seat at the school testing table?
Sorry, I am sounding as frustrated as Lyn! Google IS YOUR FRIEND!
You can find any information you need with only a few minutes searching.