A-Phase Problems

01/03/2014 11:01 AM

Hi

During our Holiday shutdown we were doing some maintenance on (2) Hi-Lo speed cooling tower fan motors. When we opened the bucket on the first one, we noticed the A-phase cable was charred. We also opened up the bucket on the 2nd one and found similar heat stress. Uh-oh.

We then checked every other bucket on the MCC. No other problems. The motors are the same make/model so that would be my first guess, but it's a bit expensive to start swapping out something like that. The cooling tower pumps are on VFDs, which are in the same bucket, but usually if VFDs cause problems it's with the associated motors not something else in the MCC.

Has anyone seen this before...any ideas?

John

__________________
jlfiegel
Register to Reply
Pathfinder Tags: motors phase
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: A-phase problems

01/03/2014 11:14 AM

bigger picture please

Register to Reply
Active Contributor
Engineering Fields - Control Engineering - New Member

Join Date: Oct 2007
Location: Emeryville, CA
Posts: 16
#4
In reply to #1

Re: A-phase problems

01/03/2014 11:28 AM

Not sure what you mean...

These are part of a central plant. Boilers/chillers/towers

__________________
jlfiegel
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#2

Re: A-phase problems

01/03/2014 11:19 AM

In my experience, and by common sense, you have a loose connection on phase A of each fan terminals, if it was an overload in the motors, or VFD's supplying more current, you would have a burnt motor by now; but you surely will if you don't correct the connections.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Active Contributor
Engineering Fields - Control Engineering - New Member

Join Date: Oct 2007
Location: Emeryville, CA
Posts: 16
#3
In reply to #2

Re: A-phase problems

01/03/2014 11:26 AM

We checked the connections. They were not loose.

-

Are you suggesting it is the motors themselves?

__________________
jlfiegel
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#6
In reply to #3

Re: A-phase problems

01/03/2014 12:15 PM

Maybe you got a bad batch of terminal strips/contactors? An IR scan should be real useful here.

Register to Reply
2
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#8
In reply to #3

Re: A-phase problems

01/03/2014 12:17 PM

No I don't think it is the motors, if the connections feel tight, it can be because they're arleady zeized by overheating, corrosion and warping.

It is pretty apparent, what you see is a localized heat mark, right in the connection, I bet you don't see any bubbles or frying in the wire insulation anywhere else along the wire lenght (as would be the case with a current above the wire's specs).

You will have to do a little repair work to replace the terminal strip and run a new wire for that phase, or nip the damaged portion if you're lucky enough to have slack.

I'd never try to save those terminals (nor the extra work involved), unless there's none available, in that case, clean it or hone it 'till you see the contact metal bright, shiny.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#17
In reply to #3

Re: A-phase problems

01/04/2014 5:35 PM

Even though the connection on the A phase did not appear to be loose, it still could have been originally. After overheating several times, the connection has corrosion in place of a good contact. I have taken wires off lugs like you have to find this to be the case. Not a guarantee but possible.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7
In reply to #2

Re: A-phase problems

01/03/2014 12:16 PM

vibration too

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#9
In reply to #7

Re: A-phase problems

01/03/2014 12:29 PM

Of course vibration too ! that one alone is the reason of periodic re-tightening of terminals in load centers and such devices.

If you've ever felt (unwilingly) the 60Hz of a household current running thru your muscles, well, imagine those poor wires that carry it day and night.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #9

Re: A-phase problems

01/03/2014 12:30 PM
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: A-Phase Problems

01/03/2014 12:12 PM

It is good that you posted an image. It allows us to make some WAG. A larger image or better yet a link to a high resolution image (CR4 does not allow for large picture files) might help but you certainly have provided us more information than most with this picture.

I suspect that the short lead length of the A phase wire is somehow part of your problem. It looks to me like this cable has been pulled and the short lead, A, of this has now been pulled taught. When this happened a poor connection to the terminal block happened and excess heating happened at the terminal block. This might have happened when that anchored tie wrap block was tightened.

Another possibility is that the terminal block was grabbing the insulation and not the bare wire end. This would make a poor connection with the not clamped bare end in the terminal block.

I notice that your wire ends appear to not have crimped ferrules. This is fine only if all of your wires are solid conductors. With stranded conductors a variety of mechanisms (mostly vibration related) can break the individual strands and make again a poor conduction point that overheats.

Those are my WAG of your problem. Since you have multiple failures at the same location, there is something wrong with this system. A careful forensic examination of the two failing units and a yet to fail unit are warranted. Pay very close attention to details. Compression markings in conductor and insulation from securing anchors and connectors can show how the units were initially made and what happened over time. Take pictures or at the very least notes on how equipment was found before implementing any repair.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Active Contributor
Engineering Fields - Control Engineering - New Member

Join Date: Oct 2007
Location: Emeryville, CA
Posts: 16
#11

Re: A-Phase Problems

01/03/2014 1:09 PM

Wow! Thank you gentlemen. I know that the field techs replaced the damaged sections of cable (otherwise we would not be running the towers). They did not replace the terminal strips however.

We did some amp measurements this morning:

1st motor:

Phase, Low speed, High Speed

A, 17.4, 60

B, 16.8, 57

C, 17.0, 57

2nd motor:

Phase, Low speed, High Speed

A, 17.5, 62

B, 17.1, 60

C, 17.2, 61

Slightly higher on A, across the board.

__________________
jlfiegel
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #11

Re: A-Phase Problems

01/03/2014 2:01 PM

62 amperes of current! It does not look to me like you have 6 AWG wire in this box. My guess on the cabling I see in the picture is that this is at best 10 AWG wire. I'm also assuming that this is the ubiquitous THHN wire.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor
Engineering Fields - Control Engineering - New Member

Join Date: Oct 2007
Location: Emeryville, CA
Posts: 16
#14
In reply to #13

Re: A-Phase Problems

01/03/2014 5:40 PM

Thanks. I will look into this when I can get the bucket open. I should note that these have been in place ~10 years.

__________________
jlfiegel
Register to Reply
2
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#12

Re: A-Phase Problems

01/03/2014 1:10 PM

One other thing I have run into: An electrician cross threaded the hex screw. That makes it "feel" tight, but it isn't tight on the wire. Grab the wire and see if you can wiggle it.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply Good Answer (Score 2)
3
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#15

Re: A-Phase Problems

01/03/2014 10:35 PM

jlfiegel,

Your posted photo strongly suggests a local cause. This is supported by the posted current readings on the motors. When I do an IR scan (and I have done many for our customers), I have found a third very helpful diagnostic tool is to take my multi-meter and read the voltage drop across the components. In your unit I would read it from the line to the load side of the breaker (trying to get to the terminals, not the wire strands). Then I would read from the wire strands to the terminals. By doing this I can usually pinpoint the exact component that is overheating. --When I say the "voltage drop across the components" I mean you are putting both leads from the meter on the same phase, so the reading will be typically in mV. Do this for each phase, and you can quickly see where the extra heat is coming from.

In your case, it can be a poor connection such as others have posted. However it can also be a loose connection between the terminal lug and the conductor bar that extends out of the breaker's interior. In some cases, I have found it to be the internal contacts in the breaker.

Contrary to some other comments about the wire strands and wire size, the appearance in your photo is of wire suitably sized for the load (#6 or probably #4 AWG). Regarding strands, when tightening a terminal screw, the wire has to be "wiggled" a little as the tightening is done, to help the strands to separate from their compacted round shape to fill the cross-section of the lug under the screw. This ensures that they will remain tight for a very long time. Many times, a few seconds' time taken to remove the twist from the strands before inserting the wire end into the lug will markedly help this process. The comment about crimping a sleeve onto the wire before inserting it into the terminal is also valid, but sleeves are not commonly available in this size and their use is not very widely-known.

Thanks for asking the question. --JMM

Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#16

Re: A-Phase Problems

01/04/2014 1:17 AM

Dear Mr. jlfiegel,

I want to supplement ( in continuation to your Reply to No.2 by Mr.Yahlasit) You may feel the connections were in tact and no looseness observed. If the Strip is already got damaged in course of use, then over heating will occur, and get further damage. This is to be corrected before it dies, and cause break-down.

Pl. check up the strip condition and whether it is correctly sized. If it is not correctly sized, get it replaced with a correct size and use.

Pl. post the information what was the cause of the problem.?

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#18

Re: A-Phase Problems

01/06/2014 9:29 AM

Yes. This appears to be heat damage caused by a loose connection.

This can be prevented by adapting and enforcing a regular PM program wherein all electrical connections including the switchgear buss connections are checked and adjusted to the proper torque value.

The PM results should be recorded by date to identify repetitive issues.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Active Contributor
Engineering Fields - Control Engineering - New Member

Join Date: Oct 2007
Location: Emeryville, CA
Posts: 16
#19

Re: A-Phase Problems

01/07/2014 11:48 AM

Hi everyone

First, let me say Thank You for the many responses. Our client is requesting a followup on this, and I am preparing a report.

It will be difficult to determine the exact cause at this point. The towers are critical to operation so the techs on duty called in a electric shop and had the problem resolved posthaste.

The 2 towers are 701 and 702. I located the old parts and took some better pictures posted here:

http://postimg.org/gallery/q4bmp5o/

http://postimg.org/gallery/drg2cbg/

If these lead to any additional insight, please let me know.

It was also brought to my attention that we have had 2 other failures of equipment for similar reasons, over the last year or so. Maybe coincidence...? One was also an A-phase issue so there's concern that the problem may be something bigger.

Based on what I'm reading, I'm thinking the problem is one of poor connection. I'll need to work on some sort of plan for regular tightening of lugs.

Best

John

__________________
jlfiegel
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#20
In reply to #19

Re: A-Phase Problems

01/07/2014 12:46 PM

Yes, you clearly have experienced a bad connection at the terminal block of your power breaker. Both power breakers show arc damage at the connection point. You can even see a melted conductor bead in the upper right picture of 701.

You should notice the other two wires on this end of the two breakers follow a curved path into the breaker. I still suspect that a part of the problem is a lack of a service loop for this wire from the tie wrap to this breaker. I assume that this chassis is not in a temperature controlled environment. This wire may shorten just enough to pull out of this connection by a small amount every cool down cycle. Add in the mechanical vibrations from operation and the taught wire slowly gets pulled out of the connection point. This is plausible but not what I think is the root of the problem of having this wire entering the connection in a straight path. Without a service loop on this wire, a pull on this wire to test the connection can easily provide a false result.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: