Magnetic Balance Test

01/09/2014 10:53 AM

Is it advisable to carry out the Magnetic Balance Test on the LT side of a 22/0.433 KV 1250 KVA transformer which has tripped on Bucholz by applying 230 Volts on the secondary side between phase and neutral. Since this will induce 22 kv on the primary side of the transformer are we not back charging a probably faulty transformer?

Register to Reply
Pathfinder Tags: Magnetic Balance Test MBT
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Magnetic Balance Test

01/09/2014 11:16 AM

"...are we not back charging a probably faulty transformer?..." Yes you are, your first goal is to find out what the gas composition is in the Bucholz, find out whether the relay is properly calibrated, then find out why/how that gas was generated.

Don't re-energize the transformer until you know what caused the trip and what its condition is.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Jan 2014
Posts: 3
#2
In reply to #1

Re: Magnetic Balance Test

01/09/2014 11:26 AM

The engineer assigned to carry out tests on the transformer started by doing an LV MBT that too at rated voltage. Yes no turns ratio, no winding resistance. In India MBT is used by many utilities as a diagnostic test on transformers. However there are no clear guidelines to carry out the test in any of the standards. So how should one conduct an MBT in this case i.e how much voltage should be applied and on which side??

Register to Reply
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#4
In reply to #1

Re: Magnetic Balance Test

01/09/2014 11:20 PM

RAMconsult: Good answer

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Magnetic Balance Test

01/09/2014 11:52 AM

The MBT will only pick up interturn shorts, it is diagnostic, not definitive, and requires additional tests to get a complete picture of the transformer's ability to return to service. If you have not done a DGA (Dissolved Gas Analysis) and figured out why the Bucholz tripped you are at risk for additional trips and/or further damage.

If you insist on relying on the MBT, try putting low voltage on the high voltage side, at least you probably won't risk any further damage, but you'll need a really accurate voltmeter for your measurements.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5

Re: Magnetic Balance Test

01/10/2014 1:39 AM

I think you are going to the worse case scenario first... are the windings failing!!

Most Buchloz relays have two trips, gas and emergency trip, the later working when the windings do fail, the large volume of gas produced, rushes to the highest point, the header tank, tripping BOTH alarms. So I'm guessing that you had a 'gas trip'. That in itself is nothing to be overly concerned with as air bubbles can stay trapped in the windings for a long time.

As previously mentioned, check the gas, see what it is. If inflammable then you follow either your own test procedures or those of the transformer manufacturer to locate the fault.

Your procedures seem to be lacking in safety, if you have injected 230volts on the secondary side, and a transformer works both ways FYI.. it will step UP voltages and well as stepping DOWN voltages. If there is a fault in the windings, and is detected now, you might have an opportunity to do something about it, rather than hope for the best.

I suggest you do the following

Test the gas - if found to be air.. no problem

If found to be combustible, then call someone to check out your transformer or you replace it now, to be inspected at a later date.

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Jan 2014
Posts: 3
#6
In reply to #5

Re: Magnetic Balance Test

01/10/2014 11:50 AM

I was trying to understand if the fault could have been escalated due to carrying out an MBT at rated voltage before doing any of the other tests like winding resistance and Turns ratio. The transformer in this case had tripped twice on bucholz, once in service and second time again after test charging on no load. After tripping for the first time the testing engineer carried out a rated voltage MBT on the LT side and the variac he was using started vibrating and burnt out. Even after this he again carried out an MBT after the transformer tripped for the second time. This time the variac did not burn and the MBT results were ok. Later on he carried out a winding resistance and got 4ohms, 8ohms , 4 ohms on the HV side while LT side resistances were ok. The transformer was declared failed on the basis of these measurements. BDV was found to be normal . However the DGA showed high electric discharge region in the duval triangle. Moreover can an open HV winding cause high electric discharge in the transformer when the Oil is good??

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7
In reply to #6

Re: Magnetic Balance Test

01/11/2014 2:53 AM

as you have declared the transformer not fit for service, then the whole topic and further comments would not be constructive, however your comment..

Moreover can an open HV winding cause high electric discharge in the transformer when the Oil is good??

How do you know the oil is/was good? when did you test it last?

Any dielectric oil has a dielectric strength value, measure in Mv/m, and while you may not reach the voltage, you will certainly get the fault current on the HV side to earth to break down the oil, causing gas. Once you have tested the gas which really should have been your first step, and it tested positive for gas, the oil is contaminated, and you need to either look at the transformer and complete more tests or again test the oil.

I suggest that you contact your transformer supplier to get further instructions and test procedures before you get another problem transformer.

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#8

Re: Magnetic Balance Test

01/11/2014 5:56 AM

A sweep frequency resonance will reveal any winding problems

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

beentheredonethat (2); Berserker (2); brich (2); RAMConsult (2)