01/26/2014 11:55 PM
How to determine the Service Factor of a motor? Manufacturers provide this info in a nameplate of a motor, but how to validate this?
Pathfinder Tags: Service Factor
Good Answers: 444
Re: Service Factor of Motors
01/27/2014 12:12 AM
You don't have to, the nameplate is your validation as long as you operate within its parameters.
01/27/2014 12:33 AM
What's the matter; don't you trust anything?
I suppose you could load a motor at FLA x SF for say 1000 hours and see if it fries or not.
Good Answers: 42
01/27/2014 3:27 AM
NEMA MG1 ch.14.37.1 states:
"When the motor is operated at any service factor greater than 1, it may have efficiency, power factor, and speed different from those at rated load, but the locked-rotor torque and current and breakdown torque will remain unchanged.
A motor operating continuously at any service factor greater than 1 will have a reduced life expectancy compared to operating at its nameplate horsepower. Insulation life and bearing life are reduced by the service factor load".
IEC 60034-1 states "duty" instead of "service factor"-there are 10 duty types from continuous running, short-time, intermittent periodic and so on, and the "duty" maximum equivalent load is the continuous load [rated]-overload is forbidden, I guess.
Julius
Good Answers: 170
01/27/2014 11:20 AM
Don't confuse people.
Service Factor & Duty are two different things. Even a motor whose duty is S1 can have a service factor of either 1 or 1.1 or 1.15 or 1.2.
01/27/2014 8:11 AM
Read the nameplate. Don't waste you time. (And ours)
01/27/2014 6:30 PM
overload it and see
Good Answers: 42
01/28/2014 1:11 AM
Sorry electricalexpert65, I don't see any reference to the "service factor" in IEC60034-1 [except for S10 where the maximum-not average-it is limited to 1.15 of S1 [continuous load]. However, I was wrong admitting the "duty" instead of "service factor" since are not similar definitions.
NEMA MG-1 is referring to "duty" indeed, but only as Continuous Rating and Short-Time Rating. (ch.1.40).
Julius
01/28/2014 1:23 AM
Load the motor as per the name plate SF for few minutes and find the temperature rise of the motor; the temperature should not exceed above the insulation class of the motor.
Good Answers: 117
01/28/2014 2:43 AM
why do you need to re-validate what is already stated?
Good Answers: 25
01/28/2014 6:52 AM
Here is link to give inf. required by you:-
http://electrical-engineering-portal.com/motor-service-factor-sf-defined-by-nema