MCCB Tripping While Star to Delta Changeover

02/03/2014 6:58 AM

Motor type-schrule cage induction motor. Kw . 60, volt.600, Olr setting 70 amp. Starter model automatic star delta starter (telemecanique) This motor is used for hydraulic powerback control .Normally this motor is taking 5o amps only at operating time. At star connection motor takes only 23 amps and hydraulic pump capacity solenoid valve also deenergised condition and this valve will be energised while changeover to delta connection. Oneday motor startup time , panel 100 amp mccb was tripped 2 times while delta contactor energising period.But at star connectio motor running fine with usual load amps.One time incoming breaker (100 amps) also tripped at main switchboard. Motor IR value checked, found ok. Motor terminal tightness, and all connector tightness checked found ok. So that three leads of outgoing delta contactor is removed and stat putton pressed, and at that times star contactor and delta contactor both are holding perfectly one by one.After connecting all the leads and checked, but again mccb tripped while delta connection changeover period.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor
Engineering Fields - Power Engineering - Thermal Power Plant Electrical Engineer

Join Date: Sep 2010
Location: INDIA
Posts: 18
#1

Re: mccb tripping while star to delta changeover

02/03/2014 9:32 AM

Hii Stanesuresh,

From your troubleshooting results, it is clear that there is neither problem in Starter (as control trial OK) and motor ( as IR found ok). Please make sure that resistance of 3 windings is balance. But i think problem lies with the Hydraulic pump(jam or alignment problem).

So, for a de-coupled trail of the motor( alone). In star mode, initially any motor will draw high current due to inertia of pump, but with in 3 to 5 secs of time it should reduce to Inoload/1.732 . As your motor current is not reducing you better take Decoupled trail of motor.

Register to Reply
Associate

Join Date: May 2007
Location: Serbia
Posts: 44
Good Answers: 4
#2

Re: MCCB Tripping While Star to Delta Changeover

02/03/2014 11:01 AM

Stanessuresh,

there is always transition spike when motor from star go to delta connection..This spike can be a reason for your problem and breaker tripping.Sometime installation of the timer and 0,5 sec. time without voltage on motor terminal before delta connection is good remedy for that problem.

Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: MCCB Tripping While Star to Delta Changeover

02/03/2014 1:06 PM

This is a very common problem with Open Transition Star-Delta starting and why I never use it. The transition spike, in addition to tripping breakers or blowing fuses, has also been known to damage equipment; that current spike also represents a torque spike as well. I once had it snap the shaft of a 500HP refrigeration compressor motor.

Star-Delta (Wye-Delta here in N. America) is actually a bit of a scam in terms of reduced voltage starting. The peak current surge at transition is never better than the normal DOL starting current, it is just of shorter duration and therefore not noticed as much. But because of the open transition, the peak current and torque spike can actually be WORSE than just starting DOL.

Increasing the transition delay may help, then again it may make it worse, it all depends on the residual magnetism in the motor and the point in the sine wave at which the transition takes place. You can try "rolling" the conductors to take advantage of the natural slight differences in motor winding resistance and changing the phase shift a bit.

There are numerous papers available on the internet describing this phenomenon and the things you can do to eliminate it. The old methods was to use a "closed transition" Y-Delta starter, but that requires a 4th contactor, another timer and transition resistors, so it is now less expensive to just use a solid state starter, which does NOT have any transition.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Participant

Join Date: Dec 2016
Posts: 1
#10
In reply to #3

Re: MCCB Tripping While Star to Delta Changeover

12/06/2016 2:39 AM

Hello, I have a similar phenomenon in my factory. The open transition star-delta starter has been working perfectly for over 4 years, why will it just start this continuous tripping of mccb. I have checked the circuit for all the possible causes of short circuit but none was found, I have replaced the breaker but the issue is not fixed. what do you advice I do next? Replacing the circuit with a close transition star delta is not the issue because the circuit in question has being working for years.

Register to Reply
Active Contributor

Join Date: Jan 2008
Location: East of Eden
Posts: 15
Good Answers: 1
#4

Re: MCCB Tripping While Star to Delta Changeover

02/03/2014 10:48 PM

I agree with all of the previous commentators and in my youth in the UK have seen oscillograms of a star delta drive system seeing up to 17 times the motor's nameplate Full Load Current in the transition period.

Depending upon the squirrel cage rotor construction under the thermal stress of Star/Delta starting there may be cracked bars but if ALL lines and phases SIMULTANEOUSLY checked and are balanced and there is no change in the noise that the motor produces, then that possibility could be counted out.

From what you have stated my preference would be to check out what is being driven as the primary culprit, starting at the coupling and alignment et al as already proposed.

Sizing of the star delta run up period in star should see the unit reach 80% of normal running speed.

Easy to check using a strobe tacho and stop watch.

You are sure that no one has altered the timers of the starter?

You could as a precaution undertake the current injection testing of the MCCB and the starters associated overloads but this involves time, cost and an outside contractor with the appropriate test gear.

And if nothing significant is found then as I have seen in recent times replace the Star/Delta unit with a variable speed unit (inherently soft starting).

But if the problem is mechanical it is an expensive learning curve.

__________________
Everybody is a genius awaiting discovery
Register to Reply Score 1 for Good Answer
Participant

Join Date: Feb 2014
Posts: 1
#5

Re: MCCB Tripping While Star to Delta Changeover

02/04/2014 12:12 AM

To me it sounds like the it is cross phasing due to incorrect wiring. This will only manifest itslf in Delta, not Star.

Register to Reply Score 1 for Off Topic
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#6

Re: MCCB Tripping While Star to Delta Changeover

02/04/2014 4:19 AM

if you have not changed any wiring before problem occurred check the full load current from previous data if available or increase the amp setting of MCCB.

This may be because of aging of motor or MCCB

check the power circuit for any loose connections

if my 1st point matches increase the amp setting to 110AMP if possible

also check the time delay setting of starter to change from star to Delta

__________________
key questions why, what & how - just think
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: MCCB Tripping While Star to Delta Changeover

02/04/2014 7:19 PM

Please go thro the below mentioned paper of mine:

MOULDED CASE CIRCUIT BREAKERS FOR THREE PHASE SQUIRREL CAGE MOTOR STARTER APPLICATIONS - SOME SELECTION CONSIDERATIONS

- by: K. Sivakumar, Manager - Design & Training, Megawin Switchgear -P- Limited, Salem

(Paper published in the July 2012 issue of Electrical India magazine)

Introduction: Motors - AC three-phase squirrel cage induction motors, in particular - consume about 75% of the total electric power consumed in any industry. And, they are the vital elements in any production process, being the prime movers of the various mechanical and process drive applications. As such, smooth starting and protection of such motors are of prime concern to any electrical system design engineer and/or switchgear application engineer.

Motor Starting Current: Any electrical design engineer and/or switchgear application engineer is only too well aware of the starting current or the locked rotor current encountered while starting any induction motor. The magnitude of such starting current can vary from about 5 times to 8 times of the rated full load current of the motor, depending upon the motor design & construction. The magnitude of the starting current for any given motor is given by the motor manufacturer in the motor catalogue or data sheet.

While the magnitude of the starting current is the phenomenon of the motor, the duration of the starting current is the phenomenon of the connected load or the driven load. For example, if for a given motor, the starting current is 6 times its rated full load current, then, if the motor is driving a centrifugal pump, this starting current of 6 times the rated full load current, might last only for about 10 seconds or less. Else, if the motor is driving a centrifugal blower, this starting current of 6 times the rated full load current, might last, for about 20 seconds or even more, depending upon the inertia of the blower's rotor.

Careful consideration must be given to both the magnitude and the duration of the starting current, while selecting starter components like the short circuit protective device (SCPD), switching device like a contactor, overload protective device (OLPD), etc., so that there are no nuisance trippings of the OLPD and/or the SCPD and no damage to the starter components.

And, many a times electrical designers and switchgear application engineers do pay due attention to this issue of starting current (magnitude & duration) and do select the starter components accordingly. Thus, nuisance tripping and/or damage to the starter components are avoided.

But....

Motor Inrush Current: There is a much more severe and unrealised component of the motor starting current, which still causes nuisance tripping and/or damage to starter components. It is the magnetising inrush component of the motor starting current. Any electrical person is aware that a transformer draws a very high magnetising inrush current at the time of switching-on. This is due to the core excitation requirements. One must also have studied that an induction motor is nothing but a transformer, with a short-circuited, rotating secondary. Haven't we? Thus, there would be inrush current while switching-on an induction motor too, as in the case of a transformer. Note that this inrush current can be experienced by the motor even during transition from star to delta in an open-transition type star-delta starter.

One can call this, the 'transient component' of the motor starting current. (This could be a misnomer, as motor starting current itself is transient in nature). May be, one can call the inrush current as a 'sub-transient component', the starting current as the 'transient component' and the running current as the 'steady-state component' of motor current. The magnitude of such magnetising inrush current in motors would vary, depending upon the point of the voltage waveform at which the motor is energised, the amount of residual flux in the motor, etc. It could reach a value as high as 12 times the motor rated current. And, the duration could be a few cycles too.

Under such conditions, the SCPD provided in the motor starter might sense this high magnitude current as a fault & could cause nuisance tripping and the motor could never be started. Due consideration must be given to the inrush current too, while selecting switchgear components for motor starter feeders.

Various Starter Component Combinations: Today, an electrical system engineer has a wide choice of switchgear components, while designing a motor starter. One can choose between:

i) Switch + Fuse + Contactor + Overload Relay

ii) MCCB + Contactor + Overload Relay

iii) MPCB (with 'built-in' overload & short circuit protection) + Contactor

Among the above three combinations, we will consider the MCCB + Contactor + Overload Relay combination in this paper, because many a times, it is observed that there is ample scope for wrong selection of MCCB for this application.

MCCBs for Motors: It is observed that when a customer wants to provide an MCCB for his motor feeder, either as a fresh application or as a replacement for an existing Switch-Fuse combination, he simply calculates (or refers to a switchgear selection chart) the required rating of such an MCCB. Then he simply procures the most economical type of MCCB available in the market place, without realising that it might not be suitable for the given motor application. Thus, he ends up having nuisance tripping of the motor and/or damage to the starter components, thus causing avoidable production downtimes.

While selecting an MCCB for motor application, it MUST be ensured that the Instantaneous Release setting in the MCCB is set to a value higher than the highest anticipated magnetising inrush current, while switching-on the motor.

How to calculate this value?

Typical Magnitude of Staring Current (Ist): 6 to 8 times the motor rated current (IrM)

Tolerance for Locked Rotor Current as per IS 325 (Table-1): + 20%.

So, the maximum anticipated starting current: 1.2 x 8 = 9.6 IrM

Transient inrush current (peak): √2 x 9.6 IrM = 13.57IrM

Also, vide IS/IEC 60947-2, Clause 7.2.1.2.4, there is a tolerance of +/- 20% in the values of current for tripping of the circuit breaker by short-circuit releases. This means that, even with the -20% tolerance, the MCCB shall not trip for the above magnitude of the magnetising inrush current. This also means that the effective setting of the instantaneous release setting in the MCCB should be above 13.57 / 0.8 = 16.96 IrM; But, this is peak value. Whereas the instantaneous setting in the MCCB is in RMS value. Hence, the above value has to be converted to RMS value; (i.e.) 16.96 / 1.414 = 11.99 IrM; Thus, the instantaneous setting in the MCCB has to be above 11.99 IrM or say, it should be 12 IrM. Assuming that the rated operational current (In) of the MCCB is the same as that of the rated full load motor current (IrM), then, the instantaneous setting in the MCCB shall be set to 12 In.

Selection of MCCB: Now, assuming that the user selects a conventional feeder protection MCCB - the instantaneous release setting in these MCCBs range from 3 In to 9 In. Even with MCCBs with modern Electronic / Numerical Protection Releases, the instantaneous setting range is 6 to 10 In. Thus, there is a chance that the MCCB might trip during switching ON of the motor, due to the inrush current, even if kept at the maximum possible instantaneous setting.

It is to be noted that such spurious tripping might not happen all the times. Depending upon the instant of switching and the residual flux in the motor, if the inrush current is more than the instantaneous setting made in the MCCB, then only it would trip. Otherwise, it wouldn't. Hence, one might hear complaints from the user about this strange "arbitrary" tripping behaviour of the MCCB's during motors starting ("sometime it trips, sometime it doesn't").

To ensure that the MCCB wouldn't trip at all for the above inrush conditions, one must select an MCCB, whose instantaneous release setting is more than the worst case magnetising inrush current, as calculated above. One might opt for a special Motor Protection Type MCCB, whose instantaneous setting is fixed at 12 In.

Contactor & Relay selection with Motor Protection Range MCCBs: It is also observed many times, that whenever a customer wants to replace his Switch-Fuse Combination in a motor starter feeder with an MCCB, he simply removes the Switch-Fuse Combinations and replaces the same with an equally rated MCCB. Unfortunately, the user does not pay any attention to the adequacy of the short time withstand capabilities of the contactor & the overload relay, with the revised SCPD (i.e.) MCCB.

It is to be noted that when a particular frame of contactor and relay were suggested for use with a switch-fuse combination unit, they were sized based on the I2t let through energy of the Fuse, which would clear a short circuit. As HRC fuses are fast acting (typically operating within 4 milli-seconds for a heavy short circuit fault), the energy let through would also be less during a short circuit and thus the contactor and relay would be subjected to a lesser degree of short circuit stresses. Hence, they would be sized accordingly.

But, when the switch-fuse combination is replaced with an MCCB of equal rating, now during a short circuit, the MCCB would clear the fault. Even with the most advanced current limiting type of MCCBs, the fault clearing time would be around 10 milli-seconds and thus the energy let through would be higher during a short circuit, than that with a HRC Fuse. Now, the smaller contactor and the relay - which were actually selected for the shorter let-thro with HRC fuses - could not handle the increased let-thro, now with MCCBs and thus would damage. Thus, what was Type-2 Coordination with Switch-Fuse combination gets converted into Type-1 Coordination with MCCB now. Thus, it leads to damage of starter components and increased production downtimes.

To avoid this, the adequacy of the contactor and relay to tolerate the increased let-through energy - during a short circuit - with an MCCB as a back-up switching and protection device must be verified & established. This can be easily established by truly following the Type-2 Coordination based Switchgear Selection charts with MCCB + Contactor + Overload Relay combination, which is published by the switchgear manufacturer.

Conclusion: It is hoped that the reasons for the arbitrary spurious trippings of MCCBs during motor starting are well understood now. It is also hoped and wished that proper selection guidelines be followed by customers and end users, while opting for an MCCB as a back-up switching & protection device in motor starter feeder applications.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 10
#8

Re: MCCB Tripping While Star to Delta Changeover

02/12/2014 1:57 AM

Please check the power factor.

If PF is legging then please connectet 20KVAR capacitor in startor in Delta Contactor (in Phase) and then start the motor .

Luxmi Maurya

981167818/2

Register to Reply
Member

Join Date: Apr 2012
Location: France
Posts: 7
#9

Re: MCCB Tripping While Star to Delta Changeover

02/21/2014 9:39 AM

Dear Stanessurech,

I have read carefully your problem and comment added in response of you question .

I found a lot of interesting information.

What I have understood by reading your question it appears you are facing issue when you go from Star mode to Delta mode.

If I am current in my understanding I will suggest to verify some point

1 - In general the Star starting time is around 15 to 20 Seconds

Do you stay in Star mode during this time? If you have a shorter starting time for Star sequence, you do not speed up enough your motor and when you switch do Delta mode your Inrush current still very high and you may trip.

2 - Does the wiring correctly done ( I suspect the answer is yes ). But if you have done maintenance on motor or some other operation in your installation you may have disconnected some power cable and do not set them back correctly ( you can verify this point easily )

Incorrect wiring phase sequence may lead to huge peak of current when you goes from Star to Delta mode.

You will found in attachment a typical Star/Delta wiring and I recommend following electrical wiring schematic for phase sequence.

3 - As some other person suggest and as you connect your load in the same time you switch your Delta contactor you may have also a locked rotor or overload in your compressor.

In this case your motor need more current to move the load and breaker may trip.

What I can suggest is to delay the load connection and let the motor speeding up to his nominal speed before being loaded.

4 You can also verify with current probe which current level you have on your main line ( downstream Circuit breaker ). This could highlight one of the above situation

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

commutator (1); electricalexpert65 (1); itsphani99 (1); JRaef (1); JRPIRIS (1); Luxmi Maurya (1); Olujimielegbede (1); Panta SD (1); parvathaneni (1); Stuart Gatland (1)

Previous in Forum: Total Load of Transformer   Next in Forum: Contactor Working

Advertisement