Tan Delta Test on 3.3kv Motor?

02/08/2014 4:46 AM

Please tell me, is it required to perform Tan delta test for 3.3kv motor also?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#1

Re: Tan delta test on 3.3kv motor?

02/08/2014 6:44 AM

It is if somebody in a position to require it says so

__________________
Give masochists a fair crack of the whip
Register to Reply Good Answer (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Tan delta test on 3.3kv motor?

02/08/2014 9:39 AM

What else is included in "also"?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#3

Re: Tan Delta Test on 3.3kv Motor?

02/08/2014 11:32 PM

Just on basis of Tan Delta test on insulation one can not certify that equipment is suitable or not for service.

Tan Delta test is a diagnostic tool to check state of insulation. Hence it is useful if base reference test report is available. That is when the test was performed on new machine or after its winding has been rewound. And by repeating the test during annual PM schedule one can compare and predict condition of insulation.

Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (1); powersolutionsFBD (1); Tornado (1)

Previous in Forum: Drive Fault - Low Voltage Message   Next in Forum: Loose Neutral of a Plug & Socket Lead to Smoke & Melting

Advertisement