86 Lockout Relay: Trip Breaker Or Close Coil Inhibit?

02/12/2014 5:31 PM

I'm commissioning an LV switchboard. The manufacturer prewired an 87T trip / 86 lockout relay setup. The 86 LOR is setup to shunt trip main incoming breaker.

With this setup, if the operator does not reset the LOR he/she will be able to close the tripped breaker only to have it instantly trip again due to LOR being in trip position. Is this setup common or acceptable?

Usually we see the 86 LOR wired to trip main breaker but also open a contact in the close coil circuit so that the breaker is inhibitted from closing until 86 LOR is manually reset.

The same would happen on the MV breaker. I'm about to wire it and want to have the same setup on LV and MV breakers.

Thanks for your input!

Register to Reply
Pathfinder Tags: 86 lockout 86 LOR 87 trip Shunt trip
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: 86 Lockout Relay: Trip breaker or close coil inhibit?

02/13/2014 3:43 AM

Quite normal with manual spring assisted closings. The shut trip operates the moment the closing mechanism starts to move. Makes a hell of a noise

Electric closing it depends on the manufacture. Reyrolle the gear I mainly worked on I altered the closing circuit so it went via the lock out relay to prevent it even attempting to close. The normal set up it would attempt to close.

MG and ABB it was normal for the LOR to disable closing.

You don't say what the make is so try asking the manufacturer or even RTFM.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Feb 2014
Posts: 10
#2
In reply to #1

Re: 86 Lockout Relay: Trip breaker or close coil inhibit?

02/13/2014 11:57 AM

Tony, thanks for the reply.

On the LV side it is a Schneider Electric (Square D) 6000 A switchboard. The breakers are manual.

On the MV side it is an ABB gear with ADVAC breakers and electric closing coil.

We will leave it up to the customers for the MV side. LV side will remain with shunt trip only.

Thanks again!

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3
In reply to #2

Re: 86 Lockout Relay: Trip breaker or close coil inhibit?

02/13/2014 12:02 PM

I think you've answered your own question. The LV breakers are manually operated (except for the shunt trip, which the 86 activates). There is nothing electrical that a contact of the 86 can block in the close mech.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Active Contributor

Join Date: Feb 2014
Posts: 10
#4
In reply to #3

Re: 86 Lockout Relay: Trip breaker or close coil inhibit?

02/13/2014 1:19 PM

Yes Peter, there is nothing that the 86 can block or inhibit on the LV.

The question now is if we should just trip on the MV breaker or inhibit close coil when 86 is tripped.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5
In reply to #4

Re: 86 Lockout Relay: Trip breaker or close coil inhibit?

02/13/2014 3:53 PM

If there is any automatic reclosing on the MV breaker, you should use a blocking contact in the close circuit. The other reason to possibly add a block close is if you are concerned that something could remove the trip signal from the breaker without having reset the relay and/or lockout. In this case it gives an additional measure of confidence that the breaker won't be closed onto a fault.

Other than that, the trip contact from the 86 should do the job. If the trip is held and the breaker gets a close signal, it will try to close, but will the mech will cycle right into the trip - it's called a "trip-free" condition. The contacts don't actually close, but the mech goes through the (beginning) motions of closing, but then goes right back open again.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2014
Posts: 10
#6
In reply to #5

Re: 86 Lockout Relay: Trip breaker or close coil inhibit?

02/13/2014 4:23 PM

I was not familiar with the "trip-free" condition. Our concern is not allowing to close the breaker to a fault. That is, after all, the whole purpose of the lockout relay.

The way I understood it was that the breaker actually closed only to be immediately tripped again. The trip-free condition makes much more sense though. Thanks!

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#11
In reply to #6

Re: 86 Lockout Relay: Trip breaker or close coil inhibit?

03/30/2014 10:55 PM

Although the breaker will attempt to close the shunt or UV coils will operate the moment the mechanism starts to move. The main contacts will never reach the point of closing the circuit.

I'm not sure about ABB but with Merlin Gerin MasterPac ACB's unless the UV coil is energised the mechanical closing button is disabled.

They're from the same stable so I can't see there being a difference.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#7

Re: 86 Lockout Relay: Trip Breaker Or Close Coil Inhibit?

02/14/2014 12:56 AM

An auxiliary relay (anti pumping relay) can prevent alternate tripping and closing of the circuit breaker if closing command persists during fault. This trip free mechanism is ensured by the anti pumping relay which prevents hunting (i.e. continuous closing, opening operation) of the circuit breaker. The function of this relay is to cut off the supply to 52C (CB closing coil) until the tripping condition is eliminated and the trip lockout relay 86 is reset.

Register to Reply Score 1 for Off Topic
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#9
In reply to #7

Re: 86 Lockout Relay: Trip Breaker Or Close Coil Inhibit?

02/16/2014 6:32 AM

The anti pumping relay cannot know by its own that the fault condition is eliminated. It only prevents continuous close trip of the breaker in the event if somebody gives close command & couldn't release the button in such a short time.

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#10
In reply to #9

Re: 86 Lockout Relay: Trip Breaker Or Close Coil Inhibit?

02/17/2014 7:27 AM

When the trip lockout relay (86) is reset after the fault is identified and eliminated, fresh command can be given for closing the circuit breaker. The NC contact of anti pumping relay in the closing circuit will permit the circuit breaker to close provided the spring is charged.

Once the anti pumping relay is latched, the supply to closing coil of the circuit breaker will be cut off as long as the closing command is present.

Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#8

Re: 86 Lockout Relay: Trip Breaker Or Close Coil Inhibit?

02/14/2014 6:21 AM

In some old breakers, repeated attempts to close with a lockout present (in our case Buchholz Relay fault) could result in overheating of the trip coil such that the armature jammed and the breakers did not trip.

Our transformer was in the open air and the sunlight had caused discolouration of the glass such that the oil level appeared adequate. After two failures to close, the foreman said he would fix it and the Inspection team went to lunch. When we returned, it deemed fine until, being inquisitive by nature, I tried the trip button. It wouldn't trip. I tripped it by hand. The armature proved to be stuck!

Register to Reply Off Topic (Score 6)
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: