Dear Sirs,
I have result of power transformer assessment during tested the Polarization Index (PI). The result of PI measured between HV to LV of that transformer @5kV-DC was 7.5. Do you have anything experience to be shared regarding this PI measurement result. I will look forward your kind advice. Highly appreciated to share this discussion.
Thanks,
Kuncoro
Re: Polarization Index of Power Transformer Measurement
02/16/2014 11:58 AM
what do you expect from the message?
02/16/2014 3:26 PM
What does it means 7.5 regarding of the PI measurement as I know the highest PI result to show an excellent insulation is 2-4. Thanks,
Good Answers: 131
02/17/2014 8:19 AM
Your understanding is incorrect. Polarization index may be higher than 4, and when it is, it generally indicates excellent insulation condition. See the following explanation. It gives a good summary of the different elements contributing to the current that is measured during the PI test, and how they impact the result:
http://www.electrical-testing-safety.co.uk/regulations/polarisation-index
03/06/2014 2:36 AM
Thank you for your kind advise regarding this subject. Is that the reference as you mentioned as similar s alike IEEE, NETA standard? If so, How can I have it either softcopy or hardcopy book by purchasing of that book.