MEGGER VOLTAGE OF THE 11KV AC, 3 POLE, 50 HZ, START CONNECTED ALTERNATOR'S COILS
Hi Guys, I got a job to repair of 5 each shorted coils of a 2.3
MW, 3 Phase11,000 VAC Star connected Alternator because of reverse power from
the main power supplier. The Management is insisting to Megger each coil at
10,000 VDC at 10,000 VDC after repair taking in to the account of
manufacturer's repair procedures. The coils are taken out of the Alternator.
When Meggering at 10,000 VDC at some points it shows short. If we can go thru
IEEE Standard 43-2000 it mentioned clearly that >5000V Megger should be at
2,500V to 5,000V. Please see the data give below.

IEEE Std. 43-2000 lists these safe minimum values for testing
insulation in rotating machinery.
I humbly request the expert advice of the Electrical Engineer
fellows and the peoples who are Involved in the winding of the High Tension
Alternators to overcome the problem.