Frequency Response of Electromagnetic Voltage Transformers

02/17/2014 2:23 AM

Dear Sir/Madam

I am doing a literature scan on the frequency response of EVT's. I have read that EVT's do not have a linear flat frequency response for frequencies above the fundamental (i.e.50/60Hz). I would like to enquire about the following:

1. Up to what frequency level can EVT's be used for power quality measurements (e.g. Harmonics) with satisfactory results?

2. Have you performed practical measurement tests using EVT's? What was the percentage accuracy of the results you obtained?

3. Beyond the frequency level which the accuracy of EVT's holds, what is the percentage deviation of meaurement results?

Your assistance will be highly appreciated.

Kind Regards

Thabiso

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2011
Location: Philippines
Posts: 105
Good Answers: 7
#1

Re: Frequency Response of Electromagnetic Voltage Transformers

02/17/2014 11:23 PM

I infer from the wording of the question that you are inquiring about transformers used for measurement rather than power supply.

Coming from an audio engineering background I am used to transformers covering a frequency range of >3 decades within a percent or two. What are the operating constraints you wish to accommodate?

Register to Reply
Member

Join Date: Oct 2013
Posts: 6
#2
In reply to #1

Re: Frequency Response of Electromagnetic Voltage Transformers

02/18/2014 1:31 AM

Hi NeilA

Thank you for the comment. The transformers in question are used for electricity transmission and distribution. The ratings of this transformers are typically 400KVA & 132KVA

Kind Regards

Thabiso

Register to Reply
Power-User

Join Date: Nov 2011
Location: Philippines
Posts: 105
Good Answers: 7
#3
In reply to #2

Re: Frequency Response of Electromagnetic Voltage Transformers

02/18/2014 4:25 AM

Understood,Thabiso. Can't help you on big power transformers!

Register to Reply
Member

Join Date: Jul 2012
Posts: 9
#4
In reply to #2

Re: Frequency Response of Electromagnetic Voltage Transformers

02/18/2014 7:05 AM

Check with a laboratory maintained by a power company. I used to work at the Public Service Electric and Gas Company laboratory in Maplewood, New Jersey USA. They guaranteed the frequency and voltage of the entire network at that location. They probably still have the information that you seek. They are listed in the phone book.

Register to Reply
Member

Join Date: Oct 2013
Posts: 6
#5
In reply to #4

Re: Frequency Response of Electromagnetic Voltage Transformers

02/18/2014 7:10 AM

Hi Nitroxpro

Thank you for the info

Register to Reply
2
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#6

Re: Frequency Response of Electromagnetic Voltage Transformers

02/18/2014 9:03 AM

I think they are likely to be much better than you imagine. Let's have a little tutorial on transformer frequency response. We'll start with the simplified AC small-signal model of a transformer, first figure:

At the center of the model we see the perfect transformer, which steps down the voltage by the ratio N, and steps up the current by the same ratio N, and which has infinite frequency response. A second very important element in the transformer is the magnetizing inductance, Lm. The current through this inductance provides the magnetic field that energizes the core and creates a voltage in the primary that holds off the AC line voltage. This is a non-linear inductance, but that doesn't concern us here now.

At high frequencies the reactance of the magnetizing inductance Lm grows high and we can ignore it. At very low frequencies the reactance of Lmfalls to very low values and creates a substantial load current on the AC source signal, see the 2nd figure below. This causes a voltage drop across the source impedance Zs plus the primary winding copper resistance Rp which in turn creates a drop in the secondary AC voltage. Although this current is 90° out-of-phase with the AC line (since it's an inductor), it can still be quite troublesome. That's the low-frequency-end of the frequency-response story.

In the model we see the expected primary and secondary copper-winding resistances, Rpand Rs but we also see two inductances Llp and Lls. These are labeled Ll (L-sub-ell) because they are leakage inductances, due to AC magnetic fields in the transformer that fail to go through both sets of windings. The windings are often interleaved to minimize this effect.

It's common to transfer all the leakage inductances to one side of the model to simplify analysis. To do this just multiply (or divide) the values by N2. Now we can imagine all of the transformer's leakage inductance effectively on the secondary side of the model, and we hook the transformer up to its load, 2nd figure.

The high-frequency response dropoff will occur due to the rising series impedance of the leakage inductance against the load impedance. For the case of a light load, or a rising load impedance at high frequencies, the winding capacitance Cw will form a resonance and double-pole rolloff with the leakage inductance.

High-voltage high-power transformers are designed to be very efficient. This means in part that they will have low leakage inductances compared to the source and load impedances. As a result I expect they'll have very good high-frequency response, perhaps well beyond 100x their intended AC-line operating frequency.

Low-power transformers, often wound with split bobbins, etc., and no interleaved-windings, generally have comparatively-high leakage inductances, and therefore may not respond much beyond 5kHz. They also often show rather poor efficiencies at 50 and 60Hz.

__________________
Thanks, Win
Register to Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#7
In reply to #6

Re: Frequency Response of Electromagnetic Voltage Transformers

02/18/2014 3:03 PM

What dullard scored this as an off-topic? Egads.

I went ahead and nullified said affront.

Good job Winfield.

BSR

Register to Reply Off Topic (Score 5)
Member

Join Date: Oct 2013
Posts: 6
#10
In reply to #6

Re: Frequency Response of Electromagnetic Voltage Transformers

02/19/2014 1:22 AM

Hi Winfield Hill

Thank you for the response and valuable information.

Kind Regards

Thabiso

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Frequency Response of Electromagnetic Voltage Transformers

02/18/2014 10:52 PM

Next time include the likes of IEEE and CIGRE in a "literature scan" about electric power engineering topics, there's plenty of data out there but you have to distinguish between an inductive and capacitive Potential Transformer. From an IEEE paper:

"...Measuring harmonics in high voltage power systems with inductive and in particular capacitive voltage transformers, CVTs, may cause large errors. Test carried out by The Norwegian National Grid Company (Statnett), Bergenshalvoens Kommunale Kraftselskap (BKK) and The Norwegian Electric Power Research Institute (now SINTEF Energy Research) revealed errors from 80% to +1200% (0,2-12 pu) of correct values. Inductive voltage transformers did have a relatively small error up to 29th harmonic (1450 Hz) while capacitive voltage transformers had large errors at a few hundred Hz. Carrying out calibration tests on voltage transformers and capacitive voltage transformers in particular may correct most of the errors. Still inductive voltage transformers should be preferred for harmonic measurements where possible..."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2013
Posts: 6
#9
In reply to #8

Re: Frequency Response of Electromagnetic Voltage Transformers

02/19/2014 1:19 AM

Hi Sir Robin

Thank You for the response valuable information.

Kind Regards

Thabiso

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: