Generator Not Producing FLC (Full Rated Current)

02/17/2014 7:14 AM

Hi there,

Could you please help me with following query related to Genset. I have a 50kVA genset

Standby Ratings :

kVA =50

Kw = 39.8

Amps = 69

P.F. = 0.8

If i connect Genset with external LOAD BANK (unity power factor load), the maxium current i can draw from genset at full load is 55.4amps. At standby mode when load is variable and pure resistive (unity PF) , i am not able to draw 69amps Full rated current from Genset. What could be the reason, Please share your knowledge. I would appreciate your time.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#1

Re: GENERATOR NOT PRODUCING FLC (FULL RATED CURRENT)

02/17/2014 7:33 AM

It's because your load bank has unity power factor. Between PF 0.8 and 1 the power is constant, so current falls as PF rises. 69 x 0.8 = 55.2 amp, so your 55.4 is just what is expected.

__________________
Give masochists a fair crack of the whip
Register to Reply Good Answer (Score 4)
Member

Join Date: Feb 2014
Posts: 8
#2
In reply to #1

Re: GENERATOR NOT PRODUCING FLC (FULL RATED CURRENT)

02/17/2014 7:39 AM

Thanks for the answer.

How could i draw rated current i.e. 69amps? I tried overloading Genset and it didnt help.

Register to Reply
3
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#3
In reply to #2

Re: GENERATOR NOT PRODUCING FLC (FULL RATED CURRENT)

02/17/2014 7:52 AM

Use a genset that is rated higher! If you need 69 amps you are looking for one that can supply 87 amps x PF 0.8!

__________________
Common Sense Dictates
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #2

Re: GENERATOR NOT PRODUCING FLC (FULL RATED CURRENT)

02/17/2014 7:54 AM

Connect it to a 200 AMP load.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #2

Re: GENERATOR NOT PRODUCING FLC (FULL RATED CURRENT)

02/17/2014 8:50 AM

You could put an inductance in series with the load bank, calculated to give PF 0.8 or lower.

Note that the PF 0.8 is a rather arbitrary figure. In practice if the PF of the load is > 0.8, maximum current is lower, if it's < 0.8 max current is constant at 69 amp, power is lower.

__________________
Give masochists a fair crack of the whip
Register to Reply
Member

Join Date: Feb 2014
Posts: 8
#6
In reply to #5

Re: GENERATOR NOT PRODUCING FLC (FULL RATED CURRENT)

02/17/2014 9:04 AM

Thank you very much Codemaster.

"Note that the PF 0.8 is a rather arbitrary figure. In practice if the PF of the load is > 0.8, maximum current is lower, if it's < 0.8 max current is constant at 69 amp, power is lower." that would support my argument.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #2

Re: GENERATOR NOT PRODUCING FLC (FULL RATED CURRENT)

02/17/2014 12:32 PM

Apply some loads whose PF is 0.8, such as motors. Then you can get more amps out without bumping up against the kW limit.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Generator Not Producing FLC (Full Rated Current)

02/17/2014 9:25 AM

What is the thinking behind carrying out this test?

  • Is the generator manufacturer's published rating inadequate evidence for having selected the right one?
  • Is it to prove the circuit overload protective devices work correctly without using the manufacturers' evidence?
  • Some other reason?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Feb 2014
Posts: 8
#8
In reply to #7

Re: Generator Not Producing FLC (Full Rated Current)

02/17/2014 9:35 AM

Hello PWSlack,

Customer wants to see the Genset generating 69amps per phase while connecting to the full load.

As the Genset data plate says stand by current rating = 69amps.

Customer is questioning if Manufacturer gives 69amps rating why can't he draw 69amps from Genset.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Generator Not Producing FLC (Full Rated Current)

02/17/2014 9:47 AM

OK. That question has been answered above. The next step is to educate the Customer with the answer and point out that the only useful load that the Customer can have is the non-reactive part, which is lower than the amps stated owing to the power factor on the equipment and cabling connected.

Do keep in mind that in such a position the equipment is operating right on the edge of the settings of its circuit protective device(s). If a margin is required to sustain the load during minor peturbations and excursions above that setting then a larger genset is in order, as suggested above. Which is probably why the Customer wants a test - a suspicion that it just ain't big enough.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15
In reply to #8

Re: Generator Not Producing FLC (Full Rated Current)

02/19/2014 7:02 PM

Engines are rated by shaft power kW, deducting the generator losses gives the maximum rated electrical power kW of a genset.

Generators are rated by volts and amps. For the stator (usually output) winding the current heats winding resistance and sets the limit at which insulation gets too hot. For the rotor, the current needed (and thus heating) is determined by the power factor - an 0.8 lagging power factor load needs substantially (~x 2) more rotor current than a unity power factor (resistive) load - the load current is 25% greater at 0.8 power factor.

The standard power factor for generators is 0.8 lagging. This corresponds to the power factor of the typical industrial load.

You should also know that the "headline" brochure kW rating is often not "continuous", but the maximum for 1 hour, with a life penalty if used more than occasionally.

Register to Reply
Active Contributor

Join Date: Jan 2014
Posts: 15
#11

Re: Generator Not Producing FLC (Full Rated Current)

02/17/2014 10:44 PM

You have said it that you are using an unity power factor load bank, there is such a thing in the market called inductive load bank, where you can test the genset at 40 kW unity p.f. and add a 30 kVAR inductive load to get a 50kVA load. The problem is the consultant ( or whoever he is) do not know electrical formula because he is only looking at the alternator nameplate details.

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#12

Re: Generator Not Producing FLC (Full Rated Current)

02/17/2014 11:22 PM

Hi Strava,

Let me explain you why you are not able to load the DG set to the Full Capacity on Unity PF.

Your Generator is Rated 50 KVA @ 0.8 PF, which means it can be loaded to 40 KW load and the Engine has been selected to deliver this 40 KW only.

Now if we calculate the KVA for 40 KW at Unity PF it Would be 40 KVA and hence the Full load Current remains at 55.6 Amp.

If you try to load the Genset above this 40 KW the Engine will be overloaded and speed will droop, DG will Trip.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Generator Not Producing FLC (Full Rated Current)

02/18/2014 10:09 AM

It just ain't big enough, is it? Someone has screwed up, perhaps?

How embarrassing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Feb 2014
Location: India
Posts: 11
#14

Re: Generator Not Producing FLC (Full Rated Current)

02/18/2014 11:57 AM

what is the terminal voltage of the Generator at the time of loading?

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); Charles Tham (1); Codemaster (2); IdeaSmith (1); lyn (1); PWSlack (3); Straya (3); TNEB kathirasan (1); Tornado (1); vishram lele (1)

Previous in Forum: Frequency Response of Electromagnetic Voltage Transformers   Next in Forum: Electrical Power System

Advertisement