High Resistance Grounding

02/18/2014 12:32 PM

What are the pros/cons of high resistance grounding versus solid grounding and low resistance grounding? What is the preference for different applications? What complications does high resistance grounding introduce in drive system applications?

Thank you.

Register to Reply
Pathfinder Tags: HRG
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: High Resistance Grounding

02/18/2014 12:48 PM

Errrr surely high resistance grounding isn't grounding at all???
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2
In reply to #1

Re: High Resistance Grounding

02/18/2014 1:05 PM

I think he is referring to situations where a series resistance would be placed in the ground path to limit the fault current, for example transformers protected by a NER (Neutral Earthing or Grounding Resistor).

__________________
jack of all trades
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Feb 2007
Location: Next to the Prime Merridian (51°29'34.50"N 0°13'32.85"W)
Posts: 780
Good Answers: 1
#6
In reply to #2

Re: High Resistance Grounding

02/18/2014 3:18 PM

You mean the (1Mohms) resistor via which the earth-mat is connected to ground on benches...?

__________________
Making mistake is part of learning.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #6

Re: High Resistance Grounding

02/18/2014 7:13 PM

Well I was thinking more of 22kV 500A neutral earthing resistors connected to transmission sized grid transformers (the other end of the spectrum) for example.

__________________
jack of all trades
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: High Resistance Grounding

02/18/2014 1:08 PM

Many if not most situations have the grounding method dictated by local electrical standards, in which case you have to use one over the other.

What do you mean by "drive system applications"?

__________________
jack of all trades
Register to Reply
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: High Resistance Grounding

02/18/2014 1:18 PM

Some good resources on neutral grounding theory and practice including resistance grounding are available at Post Glover's (recently merged with IPC Power Resistors) technical library site. Check out the documents at the following link, especially the "Historical Development of Neutral-Grounding Practices" by John Dunki-Jacobs, one of the most recognized names in the field.

Post Glover Technical Library

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: High Resistance Grounding

02/18/2014 1:35 PM

What is the subject of your question?

Grounding or drives or just a general electrical interview topic?

The question seems rather broad, unless you have a specific application in mind.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: High Resistance Grounding

02/18/2014 3:27 PM

There is a whole article in Wikipedia on earthing systems. Doesn't that warrant a look-in?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#9

Re: High Resistance Grounding

02/18/2014 10:59 PM

Here copied from one of my previous replies (http://cr4.globalspec.com/comment/642965):

There are primarily three types of grounding system which are:

(1) Solid grounding - The neutral point of the system is grounded without any resistance. If the ground fault occurs, high ground current passes through the fault. Its use is very common in low voltage system, where line to neutral voltage is used for single phase loads.

(2) Low Resistance grounding (LRG) - This is used for limiting the ground fault current to minimize the impact of the fault current to the system. In this case, the system trips for the ground fault. In this system, the use of line to neutral (single phase) is prohibited. The ground fault current is limited to in the rage from 25A to 600A.

(3) High Resistance Grounding (HRG) - It is used where service continuity is vital, such as process plant motors. With HRG, the neutral is grounded through a high resistance so that very small current flows to the ground if ground fault occurs. In the case of ground fault of one phase, the faulty phase goes to the ground potential but the system doesn't trip. This system must have a ground fault monitoring system. The use of line to neutral (single phase) is prohibited (NEC 2008, 250.36(3)) in HRG system, however, phase to neutral is used with using the additional transformer having its neutral grounded. When ground fault occurs in HRG system, the monitoring systems gives alarm and the plant operators start the standby motor and stop the faulty one for the maintenance. This way, the process plant is not interrupted. The ground fault current is limited to 10A or less.

There are other two types such as Corner Grounding (for Delta system) and Ungrounded system but they are not commonly used.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#10

Re: High Resistance Grounding

02/19/2014 8:26 AM

Hope you are not sitting at your exam desk texting and hoping for an answer.....

__________________
If it was easy anybody could do it.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: High Resistance Grounding

02/19/2014 8:38 AM

Good point. The exam would be over before anything useful arrived! :-D

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#12
In reply to #11

Re: High Resistance Grounding

02/19/2014 9:10 AM

Exactly!

__________________
If it was easy anybody could do it.
Register to Reply Off Topic (Score 5)
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Isti80 (1); jack of all trades (3); lyn (1); msamad (1); PeterT (1); PWSlack (2); user-deleted-1105 (1); Yusef1 (2)