Hi,
I have a DC current shunt that is rated 50 mV @ 35 KA. There are two ABB
universal signal converters (CC-U/STD) that take the shunt voltage and convert
to 0-5 volt output . One ABB output goes to a local controller and the other
ABB output goes to the DCS. The DCS signal follows the current correctly up to
~24500 A then is clamped. The other ABB output follows the shunt current
correctly up to the scaled limit of 30000 A.
On the bench, the ABB converters are dead on. 0 volts in = 0 volts
out, 50mV in = 5.000 volt out. In the system, 0 amps = 0 volts but the
one ABB reads slightly lower than the set point at around 18000 A and stops
following the current above 24500 A.
The outputs go to an Allen Bradley I/O card on the PLC rack. The
output voltage of the ABB converter matches what the display reads from the I/O
channel. Is it possible that the I/O channel is limiting the output of
the ABB converter?
There are 6 of these units all setup the same. only this one reads
off. We changed the ABB converter
but there was no change in the display
On the next maintenance outage we were planning to switch
the ABB channels but I am concerned if we run above 25000 and the local
controller does not see that level.