Unarmoured 6.6kV in Underground

03/02/2014 12:16 PM

Hello f riends

Am using un-armoured 6.6KV 3C*70 sq.mm power cable, my cable goes underground for nearly 4 meters and ten to connect a motor. Do I have to use GI conduit for cable or PVC pipe in underground...??? what is reccommended...?? am having GI CONDUIT pipe for the cable dia... Am excavating 1 meter and then laying the cable..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Un-armoured 6.6kv in underground

03/02/2014 12:41 PM

Are there any codes in your area?

Do you have to comply with them?

Where are you?

Use GI conduit.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Unarmoured 6.6kv in Underground

03/02/2014 7:53 PM

Only you know the situation, we don't. You have to do a risk assessment before you do anything.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#3

Re: Unarmoured 6.6kV in Underground

03/03/2014 12:36 AM

Make the trench, lay the PVC pipe on a previous mortar base, say about 50 mm , then cover the pipe 50 mm over top of pipe.

It will avoid some rodents to byte the pipe and the cable .

GI conduit will not last on natural terrain

That is from my back ground at same case.

__________________
devitg
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#4

Re: Unarmoured 6.6kV in Underground

03/03/2014 12:55 AM

You seem using the underground motor 6.6 Kv for which cable needs tobe carried there.

See the codes of the area ... GI pipe with proper solid earthing will serve the purpose but GI may need to be replaced may be in 10 yrs due to corrossion. Better if HDPE is used but there is a threat of rodents hence PCC may be needed at least in firswt 2 meters. codes may not be restricting much as such. be sure of proper earthing. check what suits better in your area...

__________________
Let us discuss the practical issues not the classroom.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#5

Re: Unarmoured 6.6kV in Underground

03/03/2014 6:10 AM

Whether you use PVC duct or GI conduit - end result is that you are derating your current carrying capacity of your cable as compared with directly buried.

Normally cross section area of 6.6kV and higher voltage cables has sufficient margin over required area to take nominal load current - reason being of two criteria, rated current and Fault level - X section has to be selected on basis of Fault level - which is higher.

In case above holds good - that even when in duct and buried in ground - x section is sufficient to take the current with all de-rating factors applied - would prefer to use GI Conduit. Reason being that it will take care of any electromagnetic interference with controls cables running in the vicinity and resulting nuisance - specially under starting condition of motor when the current is 6 to 7 times rated current.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Unarmoured 6.6kV in Underground

03/04/2014 1:05 AM

Our solution it is as shown in the attached sketch. The embedded conduit bends has to be suitable to the cable diameter and permissible bending radius[usually 12 times the overall diameter].The conduit inner cross section area has to be about 4 times the cable overall cross section area.[nevertheless according to NEC only 2.5 times it is required].

It seems to me it is impossible to attach the sketch. Sorry!

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Unarmoured 6.6kV in Underground

03/04/2014 2:41 AM

The problem it was the browser!

__________________
Julius
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); devitg (1); lyn (1); M.R.Iyengar (1); powersolutionsFBD (1); TonyS (1)

Previous in Forum: Electrical Question   Next in Forum: Load Calculation in Amps

Advertisement