Load Calculation in Amps

03/02/2014 2:37 PM

Hi i want to know i have electrical load of 180 kw in 3 phase an netural . I need to know what will be my amps on each phase.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: load calculation in amps

03/02/2014 2:45 PM

...and we need to know the voltage.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: load calculation in amps

03/02/2014 2:48 PM

Approximately 1/3 of the total amperage will be on each phase.

Some idea of the voltage would be helpful in your calculations.

Have you looked for formula on the web.

How to Search the Internet - Hannon Library

Try a search for "amperage calculations"

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Load Calculation in Amps

03/02/2014 8:01 PM

3 Ph 180KW:

12V Ph→Ph= 8660.254A
11KV Ph→Ph 9.447A

Can you fill in the obvious bit of missing information?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#4

Re: Load Calculation in Amps

03/03/2014 12:39 AM

Kw= Volt x Amper x square root of 3 x cos phi x 1000

__________________
devitg
Register to Reply
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#9
In reply to #4

Re: Load Calculation in Amps

03/03/2014 5:41 PM

It shall be
Kw= Volt x Amper x square root of 3 x cos phi / 1000

__________________
devitg
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5

Re: Load Calculation in Amps

03/03/2014 5:01 AM

It will depend on your voltage. You haven't stated your location so can't guess sensibly either.

My clue to you is Ohm's Law. Find out what voltage you are using and apply that law.

I'm a little bemused as to why somebody who doesn't know how to calculate this actually needs to know.

Are you an accountant trying to peer review an engineer's cable sizing calculation or something?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Load Calculation in Amps

03/03/2014 6:50 AM

If you only have 3 phase loads like motors, you should see about 1/3 of the load on each phase. Anything else could point to a problem.

If you have loads (single phase that is) connected between any phase and neutral, there is no telling without a clamp ammeter on each phase, what each phase is supplying.......it depends upon WHAT is connected and how well the loads have been balanced by the installer, what is switched on or off........

So there is no way anyone here can answer accurately for single phase loading......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#7

Re: Load Calculation in Amps

03/03/2014 8:45 AM

Dear Mr. atulsonpal,

It depends upon the Line Voltage and Power Factor. The equation is (as pointed out by other CR4 MEMBER) Sq.Root3 x V x I x Cos(fhi)

I presume (since you have indicated Power as 180 KW) the Line Voltage will be 420 and Power Factor is 0.8, and hence the only unknown I, as seen below can be calculated.

1.732 x 420 x I x (0.8) = 180 x 1000

and in the above equation - the only one unknown is I, which you can calculate.

DHAYANANDHAN.S

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Load Calculation in Amps

03/03/2014 5:02 PM

That would average 60kW per phase. Divide it by the voltage between phase and neutral, and "Robert is your mother's brother" or so it is said.

Next!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#10

Re: Load Calculation in Amps

03/06/2014 12:52 PM

If this is an operational unit, use a clamp-on amp meter on each leg.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#11

Re: Load Calculation in Amps

03/31/2014 1:51 PM

My apology in advance!You must be an engineer?

In order to do calculations; It is needed: 1) KW 2) Voltage 3) Frequency 4) 1 -phase or 3 - phase 5) 3 phase and Neutral means star connection i.e I (phase) = I (line) 6) What country? Like America has 208 V 3-phase and middle east 400 V 3-phase system 7) Etc.

__________________
--
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abasins (1); Andy Germany (1); devitg (2); dhayanandhan (1); lyn (1); old salt (1); PWSlack (1); RAMConsult (1); TonyS (1); Wal (1)

Previous in Forum: Unarmoured 6.6kV in Underground   Next in Forum: Conveyor Pre-Start Alarm

Advertisement