Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 4:28 AM

Can someone explain me fundamentals of why so?

Register to Reply
Pathfinder Tags: Un v/s Breaking Capacity
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 4:59 AM

What sort of arc do you want to achieve, Guv?

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #1

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 12:07 PM

A big one by the looks of the question.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#2

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 10:17 AM

At the risk of answering homework, a magnetically tripped breaker is designed for a specific voltage and current. Increasing the voltage across the sensing element will increase the magnetic field and cause the breaker to trip at lower current levels.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 2:39 PM

With power constant, as voltage goes up current goes down. Its the whole point of the transmission grid, step up the voltage so the cables can be thinner = cheaper.

Lower available current means lower prospective short circuit current. Circuit breakers are designed to handle the expected short circuit current rather than being over engineered to handle currents they would never see, again to save money.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 7:55 PM

Dear Jignesh, Hope you are my good ol' colleague from L & T. Hope you could identify me.

Now, arc is not current, but energy (I2rt) or let us say, power. Thus, the breaking capacity, in fact, is MVA. For a given breaker design, this breaking capacity MVA is constant. When MVA is constant, naturally, when voltage increases, current obviously, has to reduce.

Hope it is clear now.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2014
Location: Mumbai, India
Posts: 25
#6

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 11:08 PM

I don't think that it should be related to MVA (Voltage & Current). My question was that generally for eg, a circuit breaker as breaking capacity of 50kA@415V AC then why does it reduce say for eg 36kA@690V AC. It is my opinion that it cannot be just derived by cross multiplication but may have some relevant technical answer for reduced breaking capacity.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/11/2014 11:27 PM

It is a combination of issues. Mostly it is the energy issue raised by Eletricalexpert, because the energy in the fault translates directly to mechanical (magnetic attraction and repulsion) forces that the breaker must withstand without becoming shrapnel.

But there is also an element of higher voltage helping to sustain an arc longer. That's why the arc chutes on a 5kV air breaker are VASTLY different than the arc chutes on a 600V breaker. The difference between 415V and 690V are not as great, but it does make for the relationship of the MVA to appear non-linear.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#9
In reply to #7

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/12/2014 11:55 AM

Did I really misunderstand the poorly worded question so massively ? lol.

__________________
Smart as a post and twice as fast.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #6

Re: Higher Continuous Operating Voltage, Lower Breaking Capacity of Circuit Breaker

03/12/2014 4:24 AM

Dear Jignesh,

Yes! It is related to MVA. But, as put forth by Mr. JRafe, the relationship is not linear (i.e.) the current does not linearly reduce in proportion to the voltage rise. So, the question of cross multiplication does not arise. I haven't said so either.

Also, at higher voltages, the voltage across the contacts is also more and thus the restriking voltage. Hence, the breaker cannot have the same breaking capacity at higher voltage as the magnitude of the restriking voltage also is more.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); electricalexpert65 (2); jack of all trades (1); Jignesh Shah (1); JRaef (1); LongintheTooth (2); TonyS (1)

Previous in Forum: Discrimination Charts with XT Range of ABB MCCBs   Next in Forum: How to Calculate for Energy? Newbie

Advertisement