Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/12/2014 8:48 AM

Hello every body

Greetings from India!

We are motor rewinder and service providers for H.T induction motors of Kirloskar, ABB, CG, BHEL etc.

Motor Details: 3.3KV / 750 KW / RPM 1475 / Make : Kirloskar

Application: Paper mill

One of our customer is facing problem for "Frequent failure in Stator winding and rotor bar coming out of rotor in operation"

Motor is S1 duty and Customer uses more than 15 times switching(ON/OFF) per day.

Since supplied by manufacturer, after installation 1st motor failure occurred

after 1 year

After rewinding both stator and bar replacement of rotor it was failed within 9 - 10 months of operation.

(We have followed all parameters and tests of winding as per manufacturing spec)

What will be the cause of failure?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#1

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/12/2014 9:13 AM

Bar stressing is always load related. I think your client needs a new motor class (S ?) Motor must survive continous rotor... locking after shock overloading it to lockup. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/12/2014 10:44 AM

assuming the windings were done correctly I'd be going right at voltage, supply voltage and the switching of that voltage on and off. does it have external motor protection?

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/12/2014 12:15 PM

This is what solid state soft starters are for. I used to call them electrical solutions to mechanical problems. Most likely it is started DOL and the starting torque is so high against a high inertia or high friction load that all of the stress from the torque in excess of accelerating torque gets exerted on the rotor, and the cage is the weakest link. The other possibility is that they are using Star-Delta starting and the transition spike is doing the same. Either way a smoother application of torque over time us the cure.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/12/2014 11:18 PM

Are the materials used in construction up to the standards?.

__________________
pnaban
Register to Reply
5
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#5

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/12/2014 11:27 PM

Remember that every time we start a motor Direct on Line, the amount of heat generated in Rotor Cage Winding is equal to Inertia of Rotor +Coupling + Pump. This results in

1. Sudden expansion of rotor bars and heavy thermal stress on joints of bars with Ring.

2. Weakening of bar to ring joint due to centrifugal forces once hot rotor reaches rated speed.

Combined effect of both is failure at bars.

You did not mention whether failure of Stator was due to mechanical rubbing of broken bar with winding or due to other reason.

Also when we Start a motor on DOL, the surge current produces sudden magnetism in overhang portion of stator coils - result repelling force within adjacent coils and individual coils tending to open resulting in stress on Eye of Diamond Shaped Coils. Resultant failures are:

3. Inter-turn short in stator winding at location of Eye or in the overhand portion.

Remedies to 1 and 2 above are:

1. Reduce number of starts not more than 3 in a day. (Normally we allow maximum 2 consecutive starts on HT motors - then wait for 30 minuets to cool down and if fails again next start after 6 hours)

2. One solution to reducing frequent starting can be install by pass to the pump and pressure breaker rather than stopping it.

Soft starter of series inductor may not help as poor power factor may result in longer time for starting current and as said above heat equal to inertia has to be lost in the rotor. Though reduced rate of heating but also will be reduced rate of cooling as longer starting time.

3. Installed forced cooling on motor (Low voltage blower) to force cool the motor after it is started direct on line so that it is cooled down quickly and ready for next start. The Blower shall be started before the start of motor so that it maintain relatively cooled rotor during start up.

Solution for Stator overhang failures are:

1. If failures at observed at eye - give single layer of double lapped capton tape on alternative turns in portion of eye over normal inter-turn insulation.

2. If failures in the portion where conductor comes out of stator slots or in other portion of overhand - add surge ring to support overhand against Mechanical Jerks.

One method to see behaviour of machine on start is to take Video of machine and watch at slow speed later to know where corrections are needed.

I am not a rewinder or your competitor in India, but one of my friend who also does similar business to you - nearly 80 years and still a active rewinder - has been referring me problems and I have been given him free solutions (he is a friend). Hope above may be of use to you.

Best of luck.

Register to Reply Good Answer (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #5

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/13/2014 11:31 PM

Does the starting current depend on inertia of load connected,in this forum many have mentioned that it depends on R & X of winding only,because at the moment of starting there is no back emf. I donot remember the title of the tread.Please provise some equation for I in terms of moment of inertia,slip,R,X,V etc

__________________
pnaban
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#10
In reply to #9

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/14/2014 2:14 AM

Inrush current does not depend upon inertia.

It is function of X

Starting torque is a function of Rotor resistance.

In case inertia is relatively higher and resistance of cage is relatively low, meaning low starting torque and long starting time - which in turn longer time for which starting current will stay.

So net result is more heat loss in Rotor. As I said before the Sigma of heat loss in the rotor while starting is equal to Kinetic Energy build up in the rotor due to inertia.

For high inertia Induction Motors practice is to use Slip rings> Double Cage Rotor>Deep cage Rotor (giving in descending order).

Maximum Torque is when R = X in the rotor. Because X is a function of speed (induced frequency in the rotor, hence it is maximum at standstill and less at load as frequency induced in rotor is slip speed).

In slip ring type rotor R is adjusted by external resistance.

In double cage rotor due to skin effect inner cage carries most of current at start and is relatively of higher resistance (smaller cross-section).

Deep cage is similar to double cage having common conductor and end ring. Due to deeper cage at start current is concentrated at bottom of rotor conductor subjecting a higher resistance of cage at start due to skin effect at 50Hz.

Sorry for adding longer explanation. I may be wrong somewhere but mostly correct as I studied Induction motors in 1969-70 during my Graduation and here since you posted a question - theory of machine starting flowing in my mind.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11
In reply to #10

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/14/2014 3:31 AM

When you inertia,is it inertia of rotor & load together?.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#12
In reply to #11

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/14/2014 3:59 AM

Inertia of Drive Train - which includes rotor coupling any gear box and driven equipment etc.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/13/2014 12:24 AM

What will be the cause of failure?

The answer is in the subject heading......Kirloskar.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#8
In reply to #6

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/13/2014 3:55 PM

I do not agree the problem is Kirloskar . I have used many Kirloskar motors with out failure. Their quality is very good, and have a good name in Indian market and supposed to be very reliable. Here it is the problem of the person designed the pump house and lack of coordination with the manufacturer by user and the contractor who installed the system . The user must have contacted M/s Kirloskar in first time the motor failed.

I agree with power solutions reply.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/13/2014 10:18 AM

Too many starts & stops with too much mechanical stress created by the attached load.

Install a VFD, Soft-Start, or hydraulic coupling between the motor and the load.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#13

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/17/2014 5:19 AM

Another important fact regarding failure of Rotor Bars of Squirrel Cage - if these are Cu bars .

Pure Cu hardens when it is cold worked.

If the bars are loose in slot - these will vibrate - resulting in Hardening. Hard Cu is brittle or more when Notch Brittle. As a result the crack will occur where where bars come out of end rings.

To check if fatigue is the cause of failure - do a dye penitrant check at location of joints of bars to ring and you may find cracks at some of joints developing on thinner side of rotor bars. If it is so - then bars are loose and fatigue is reason of failure.

We can not anneal the bars in situ as heating and quenching (process of softening of Cu) will bend the shaft.

Hence suggest to replace the bars. I learnt from that Bars are not pure Cu but Silver Cu Alloy (In ratio of 50:50). I am not very sure about this and you can check with a Metallurgist.

Another solution which I had tried on ID and FD fans motors in 1973 - 74 is to press Cu bars with a blunt end chisel tool of 20 mm width on Hydraulic press at number of points between slot portion (not air vents). This spreads the bars on top portion. This is possible when slots are open at top.

Full background of above case is that at time I was working in Electrical Maintenance of Thermal Power Plant of Tata Electric in Trombay (my first job started in 1972). We had AEG Germany make 3.3kV motors of 1954 construction for ID and FD fans. These were dismantled and inspected every 3rd year. During this period I noticed that 2 to 3 bars usually will be found broken. Action take was:

1. Hit lightly broken bar with a mallet and Cu piece and it moved down - this indicated that particular bar was loose.

2. Hit one of end ring with Mallet and listen to noise at other end with screw driver - it produced noise like we hear from Tuning Fork - indicated most of the bars were loose.

3. Took Old blunt Chisel from Stores - got it heated shaped and size to width of top opening in the rotor slots.

4. Placed rotor on a Hydraulic press and pressed each bar at a time at number of locations in slot portion to put Indent impression - expanding the bar.

With above solution- problem got eliminated. I left Tatas in 1881. After 1981 I did not have chance to work on Motors and thus forgot this particular occurrence - which is similar to you have experienced.

Hope above is of some use.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#14
In reply to #13

Re: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm

03/21/2014 6:06 AM

powersolutionsFBD mentioned all possible reasons for the motor failure and also given cheking and solutions.I would like to add a few more reasons and checking as mentioned below:

1)What is protective relay deployed for the above motor and whether the subject relay was actuated and trip indication?

2)How much Hot Start were done and whether the same were compatible with motor specification?

3)Whether there is any voltage imbalance? and how much it is?

4)Whether the motor is started with vaccum contactor and capacitor bank is parmanently connected across the motor terminals?

5)Present of harmonics(Power Quality issue) in power distribution system.

Regards,

Manindra

__________________
Manindra
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Fredski (1); JRaef (1); manindra (1); pnaban (3); powersolutionsFBD (4); SHOCKHISCAN (1); SimpleMind (1); V.I.Abraham (1); Wal (1)

Previous in Forum: Voltage Multiplier   Next in Forum: Static Bypass Switch in LV Busbar Repair

Advertisement