Anonymous Poster #1

Static Bypass Switch in LV Busbar Repair

03/12/2014 10:57 AM

In the repair of busway we are required to have a zero interruption schedule

My question is

Coming from 2 transformers with different source is it advisable to use a static bypass 4 pole switch

with 3 pole isolators in on each end ..... how about the Neutral of each transformer

I know its applicable in UPS but dont know in a 630 A static bustie that will only be manually operated????? ANY British standard or IIEE we can reference

We can apply load shedding on both ends of the 2 transformers with different source

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Static Bypass Switch in LV Busbar Repair

03/12/2014 12:48 PM

The only thing that I would advise you to do is to make sure that you have some form of mechanical interlocking scheme plus physical separation to ensure that the bus is never accidently fed from both sources. Failure to so will result in a safety hazard to personnel and equipment.

Quite frankly if you have to ask for guidance here, you shouldn't be doing the work there.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 3)
Active Contributor

Join Date: Aug 2013
Posts: 21
#2
In reply to #1

Re: Static Bypass Switch in LV Busbar Repair

03/12/2014 1:20 PM

Thanks for the solid advice will do Sir

Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Static Bypass Switch in LV Busbar Repair

03/13/2014 10:30 AM

Are the neutrals from both transformers common to each other and earth/ground?

If so, there would be no difference of potential between the equipment ground and earth-ground so there would be no reason to switch or "bypass" the neutral inside the work zone.

If the transformer neutrals are not shared and/or not common to earth-ground, then the neutral should be disconnected on both sides of the repair work and bypassed using the fourth pole of the switch.

To be safe and properly protect all personnel working on the bus; Be sure to earth-ground all bus conductors and neutral conductors within the zone/area being worked on with bare copper conductors that are sized large enough to carry the maximum fault current available from the system.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Anonymous Poster #1
#4
In reply to #3

Re: Static Bypass Switch in LV Busbar Repair

03/13/2014 10:57 AM

The neutrals are not shared since the essential come from different source as well as the Normal supply

Since this is a temporary installation we will not use the remote control operation but basically the mechanical part of the custom built static bypass switch

My only concern is the protection on the downstream

the 630 A cb will supply to a max 300 A as we will shed load like chillers and small pumps

Once manually initiated , will it affect the Undervoltage setting at he receiving end

owing to the 20 nanosecond changeover

your above statements hold true .....

the contractor are asking for any standard since they are insisting that it is applicable only for UPS systems and not 2500 A busways

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Static Bypass Switch in LV Busbar Repair

03/13/2014 3:32 PM

You have a wise contractor, he recognizes that a UPS system is not the same as a 2500A busway...and that 20ns changeover? That's an electronic, not mechanical, speed. The only thing in most ATS that's that fast is the speed of the solid state surge protection.

I suggest that you re-read the specs, most ATS have at least a 1 second delay to allow the larger motors' internal voltages to drop at least 50% to avoid closing in on a motor voltage that could be as high as twice normal if the connection takes place 180° out of phase with the incoming source.

For your own protection I hope that the contractor makes you sign a release and hold-harmless clause, then maybe you'll get a qualified consultant to guide you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Anonymous Poster #1
#6
In reply to #5

Re: Static Bypass Switch in LV Busbar Repair

03/13/2014 5:03 PM

Totally agree

difference in application makes the project in limbo as it is intended for both UPS and busway repair application during the tender stage however they the contractor admitted that its only for UPS

As for the speed of no break its electronic as they are talking of SCR s

but will double check again the specs

as for the waiver, its the contractor telling us the other way around

So im opting for remedies as the unit had been delivered already

Simulation test with a dummy load

20 to 30 deg out of phase triggering of downstream cb protection ???

Contingency plan for downstream spare parts / upstream as well / including the new unit / since all scenarios must be considered

Catastrophic failure - how to return power to the old busway

Worst scenario is just connect a point to point cable in parallel to busway for the repair

and hire a consultant/ Supplier of such to assess the unit prior to execution

Thanks for the comments suggestions

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); fidel (1); RAMConsult (2); SHOCKHISCAN (1)

Previous in Forum: Frequent Failure In Kirloskar Make Motor 3.3Kv / 750 Kw /1475 rpm   Next in Forum: Short Circuit Strength of Power Transformers

Advertisement