Short Circuit Strength of Power Transformers

03/12/2014 1:33 PM

If there are two transformers (a) 5 MVA 33/11 KV DY11 OIL IMMERSED PERCENTAGE IMPEDANCE=7 percent and current density= 2.5 amps/mm and L.T.TURNS=180 and the second transformer (b) 5 MVA 33/11 KV DY11 OIL IMMERSED PERCENTAGE IMPEDANCE=7 PERCENT and current density=2.5 amps/mm and L.T.TURNS=168 I would like to know which one of these two transformers has more chances of passing the Short circuit test(Dynamic and Thermal ability) and why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Short circuit strength of Power Transformers

03/12/2014 1:46 PM

Flip a coin.

Less insulation to fail with 168 turns.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: Short circuit strength of Power Transformers

03/12/2014 3:37 PM

And there was I thinking that fuses and overload breakers were there to protect the things. Silly me.

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Short Circuit Strength of Power Transformers

03/12/2014 3:53 PM

The best people to ask are the manufacturers.

As Crabtree has said the protection should operate before damage is done. A hypothetical question, do you ask out of interest or is it your homework?

Homework, CR4 has rules regarding this.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5
In reply to #3

Re: Short Circuit Strength of Power Transformers

03/12/2014 5:40 PM

Worryingly this isn't a homework question, Vinod has said previously he works as a transformer designer.

CR4 Link

__________________
jack of all trades
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: Short Circuit Strength of Power Transformers

03/12/2014 9:57 PM
__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Short Circuit Strength of Power Transformers

03/12/2014 4:15 PM

So, the point of the test is to discover which of these transformers survives an unprotected short circuit and which one catastrophically self-disassembles? Please make sure that all other CR4 readers are at least 1km away from it before carrying out the tests.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#7

Re: Short Circuit Strength of Power Transformers

03/12/2014 11:08 PM

And how many years have you been designing transformers? In this thread, you don't seem to know where to place the transformer cooling fans and in this thread, you don't seem to know your suppliers and now your wondering which transformer will self destruct during a short circuit?

Are you even sure your a "designer" of transformers, because you sure sound like your still in school

I agree with PW Slack, "Please make sure that all other CR4 readers are at least 1km away from it before carrying out the tests."!!!!

And as Tony S stated,

GA's Tony and PW

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#8

Re: Short Circuit Strength of Power Transformers

03/12/2014 11:36 PM

At a first glance, lesser turn would have better capability against the short circuits - reason being if turns are less then the area of cross section of coil shall be more - resulting in bigger dia of coil - more area and better cooling.

Having said above mechanical strength depends upon number of factor including ratio of height to dia, coil supports and gap between adjacent coils etc.

Register to Reply
Member

Join Date: Sep 2013
Posts: 8
#16
In reply to #8

Re: Short Circuit Strength of Power Transformers

03/15/2014 12:58 PM

I think you are quite right and very close to what I have thought all along .Your answer has given me confidence' Now to put it more specifically I had read that "all short circuit forces depend on Ampere Turns " In this case the Amperes are of short circuit current ie Turns multiplied by short circuit current in Amperes . Now short circuit current will depend on percentage impedance , since the impedance is the same in both cases then the short circuit forces will be less in the case of transformer with LESS TURNS Hence I THINK THAT THE TRANSFORMER WITH LESS TURNS WILL BE safer in short circuit test conducted at an accredited test house Do you think I am thinking on the right lines Please let me know your opinion about what I have written above regards Vinod

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#17
In reply to #16

Re: Short Circuit Strength of Power Transformers

03/15/2014 1:08 PM

What makes you think that less impedance would be safer? Less impedance results in more current flow...therefore hotter wires and more likely catastrophic melt down and failure.

__________________
If it was easy anybody could do it.
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#19
In reply to #17

Re: Short Circuit Strength of Power Transformers

03/18/2014 6:32 PM

I see no answer from the OP to my question. A lot of people equate heat with resistance...in fact, it is an inverse relationship.

__________________
If it was easy anybody could do it.
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#20
In reply to #19

Re: Short Circuit Strength of Power Transformers

03/30/2014 2:31 AM

I think this person is still in school and facing questions that he either cut school or fell asleep during the lecture and didn't take notes on the subject

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#18
In reply to #16

Re: Short Circuit Strength of Power Transformers

03/16/2014 9:59 AM

Instead of this thoughtless mind, or is it mindless thought, experiment why don't you contact an "accredited test house" and let them tell you what their experience is, then report back what they say.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Short Circuit Strength of Power Transformers

03/13/2014 2:31 AM

I agree with powersolutionsFBD.

Let's say both transformer magnetic flux density will be the same then less turns larger iron column-better dynamic stability, but since will be more iron, iron losses will be a little more.

Lesser copper on the windings-lesser copper losses. My opinion: the total losses will be lesser if the number of turns is less.

__________________
Julius
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#11
In reply to #9

Re: Short Circuit Strength of Power Transformers

03/13/2014 4:27 PM

Well more turns would supply more resistance which would result in lower amperage, and less heat. Thats just copper losses though. Impedance on a higher winding transformer would be higher, and result in less current. More iron in the core on a larger transformer would result in more hysteresis and eddy current losses. In a dead short, well........I would flip a coin and stand well back.

__________________
If it was easy anybody could do it.
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#10

Re: Short Circuit Strength of Power Transformers

03/13/2014 12:23 PM

Option (A) is at advantage with a higher turn ratio and probably >= Option (B) impedance with some decimal points that can not be approximated.

__________________
There is peace in silence and achievement in plans.
Register to Reply
Member

Join Date: Sep 2013
Posts: 8
#12

Re: Short Circuit Strength of Power Transformers

03/13/2014 10:35 PM

Guys, my question has something to do with ampere turns and short circuit forces. I have read somewhere that short circuit forces are proportional to Ampere turns and this is what I want to understand. Please think on these lines and give me a sound and logical technical answer Thanks vinod

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13
In reply to #12

Re: Short Circuit Strength of Power Transformers

03/13/2014 11:06 PM

Why?

Your question has "something" to do with what you "have read somewhere".

Go back and read it again. Then perform the same searches/research we would to arrive at a, "sound and logical technical answer" to your question.

Or, flip a coin.

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#15
In reply to #12

Re: Short Circuit Strength of Power Transformers

03/14/2014 2:22 AM

Pl do not waste our time. Think beyond what you have read such as; Is the reaction due to short circuit is between two transformers (two magnets) that you are talking of overall ampere turn, OR it is between adjacent turns and between limbs and you will get the answer? If it is between adjacent turn then number of turns do not matter.

Once again do some more of reading or visualize the situation yourself before posting your question. And if posted be clear with background in mind so that we do not waste our time unnecessarily.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#14

Re: Short Circuit Strength of Power Transformers

03/14/2014 12:07 AM

Go with the one with more turns. Since they both have the same rating, the current carried is the same in both cases so the conductor can have the same cross sectional area, though you may want to increase it to account for the increased voltage drop through the longer length (this helps the following argument).

Assuming that the conductor is the same size in both cases, there is 7.15% more copper to heat up so it will be able to sink more heat which when coupled with a greater surface area immersed in the oil, increases the rate of heat rejection to the oil; both effects contribute to a greater thermal withstand capability.

Mechanically, more windings means that the forces will be spread out over a greater mass, which when coupled to a longer conductor length, yields a lower force per winding turn; therefore there will be less deforming force per unit of copper.

Another way to look at it; assuming that the style, winding factor, and diameter are the same, yields a taller coil, more surface area = better cooling, plus the deforming/hoop stresses are spread out over a greater area as well.

The above assumes that all other things are equal since it's possible to use different combinations of winding factors (disc, multilayer, sheet, parallel, interleaved, etc.) and core structures (core, shell, three or five limb) to design a special needs transformer that will prove this simplistic analysis wrong.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Register to Reply 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Crabtree (1); Dickson (1); dj95401 (2); jack of all trades (1); lyn (2); powersolutionsFBD (2); PWSlack (1); RAMConsult (2); TonyS (2); vinod manchanda (2); Yusef1 (3)