Anonymous Poster #1

Earthing Truck

04/02/2014 3:06 AM

Why we use earthing truck in MV switchgear not in LV Switchgear?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Earthing Truck

04/02/2014 7:43 AM

For safety.

Earthing is a requirement for MV work to be carried out in most cases.

If earthing is required for LV it would normally be carried out manually.

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 3)
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#2

Re: Earthing Truck

04/02/2014 10:36 PM

LV earthing is only for audio equipment or scientific signal processing and such. It is for shielding and noise control rather than safety.

__________________
Most people are mostly good most of the time.
Reply Off Topic (Score 4)
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#3

Re: Earthing Truck

04/03/2014 12:13 AM

Some of the answers are misleading. MV or medium voltage switchgear, which is for 1100 volts AC to 15000 volts usually has normally got all the conducting surfaces taped or insulated so there is no way to put safety grounds on. The use a a good grounding truck or what some people might call earthing truck across the pond is used to ground usually the load side of the breaker. The best ones allow the unit to be racked in and the lack of power tested before a ground switch in the device is operated or manually engaged. The use of these devices require a good knowledge of the system to be sure that no backfeeds exist or someone does not rack them into a live bus. Deaths have occurred from error.

LV or low voltage switchgear can have voltages up to 1100 volts but are usually below 1000. This type of switchgear does not require taping of outgoing cables as a normal rule and it is a simple to thing to simply remove the back cover after de-energizing and locking out the feeder and installing grounding cables on the outgoing feeder before work is performed.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Earthing Truck

07/24/2024 6:17 AM

It's a bit difficult to answer without talking to the <...we...> first.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); Deefburger (1); PWSlack (1); TonyS (1)

Previous in Forum: Connecting Lightning System With Earthing/Grounding System   Next in Forum: Design a Buck Converter

Advertisement