Transformer Load Reaction

04/18/2014 10:47 AM

In 3 phase 11KV/440V,1000KVA Transformer,connected load only 100kva,(means 10%).only.In such conditions,What will happend in the Transformer and it will react to powerfactor or impedance or else?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Transformer load reaction

04/18/2014 12:24 PM

The only time a transformer "cares" about the load is when the load is greater than the the rating. So if you load it to only 10% of its rating then it will just pass the power through with no problem. The power factor on the high side will be be the resultant of the high side voltage and the current as it passes through both the load impedance and the transformer impedance, with a small voltage drop through its internal impedances.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Dec 2010
Posts: 4
#2
In reply to #1

Re: Transformer load reaction

04/19/2014 12:37 AM

Thankyou

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Transformer load reaction

04/19/2014 8:15 AM

At 10% check the output voltage,if high adjust off-load tap.

__________________
pnaban
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Transformer load reaction

04/19/2014 8:34 AM

At 10% load, the cable losses will be 1/100 compared to full load, Guv, so who gives a monkeys about power factor!

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); pnaban (1); rajanbt (1); RAMConsult (1)

Previous in Forum: Diffe. Between Solar Panels V/S Building Integrated Photovoltaic Products   Next in Forum: Energy Meter Running With Neutral Wire

Advertisement