Problem In 11k/440v Transformer

04/21/2014 9:31 AM

HELLO CR4 users

I am facing problem with one of my 11k/44v transformer

when it is charged it is giving a voltage at LT as follows (when no load is connected)

Vry - 420V

Vyb - 420V

Vbr - 420V

Vrn - 230V

Vyn - 230V

Vbn - 230V

Vrgrnd - 230V

Vygrnd - 230V

Vbgrnd - 230V

when transformer is on load

Vry - 420V

Vyb - 420V

Vbr - 420V

Vrn - 230V

Vyn - 230V

Vbn - 230V

Vrgrnd - 420V

Vygrnd - 3V

Vbgrnd - 420V

Please suggest me where problem lies

__________________
key questions why, what & how - just think
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: problem in 11k/440v transformer

04/21/2014 10:15 AM

Looks like the load Vy is shorted to ground to me. A measurement of the currents will tell a qualified electrician what is your problem. Hire a qualified electrician.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: problem in 11k/440v transformer

04/21/2014 10:31 AM

I agree with Redfred. What concerns me more is... based on the reading of the phase to the netural and to ground on the un-loaded secondary, the secondary star point (the neutral) is tied to ground (as it should be), so... why does your protection system (the fuses and the other overcurrent devices) not trip? You should never be able to see a load phase conductor shorted to ground as you do now.

Get someone in there fast.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #2

Re: problem in 11k/440v transformer

04/21/2014 4:04 PM

Actually it's possible if we remove the assumption that the secondary neutral is grounded. The data as presented indicates it's a wye-delta transformer, not uncommon when continuity of service under first-fault conditions is the goal.

As we know in a delta connection there is no neutral, so the first solid ground fault pulls that phase to system ground and reads zero volts. The other two phases rise approximately to √3 times the prefault voltage with respect to ground, in this case it should be 1.73x230≈400 Volts. the readings were probably made with a DVM (Digital Volt Meter) which often gives erroneous readings on anything other than a balanced system due to things like stray capacitive pickup, induced voltages, and harmonics that an analog meter is insensitive to.

Most modern ungrounded systems have some form of unbalanced voltage monitoring to alarm on first fault conditions. Otherwise a much bigger problem arises when the second fault occurs, that's when PPE (Personnel Protective Equipment) and arc-flash calculations take over.

Message to OP, heed everyone's advice and get out of there now and let qualified personnel take over.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#16
In reply to #6

Re: problem in 11k/440v transformer

04/23/2014 6:13 PM

Agreed... if one of the phase conductors read a low voltage to ground at the load end, why does it not read the same low value at the supply end?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#3

Re: Problem In 11k/440v Transformer

04/21/2014 11:23 AM

Can I ask you whether a SAT (site acceptance test) has been performed before on your Tx/Tr? For e.g one Vector-Group check/test...

__________________
--
Register to Reply Score 2 for Off Topic
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#4

Re: Problem In 11k/440v Transformer

04/21/2014 1:36 PM

In no load conditions, you are measuring a "ghost voltage" from Vy to grnd, most likely thru carbon deposits in a damaged connection, thats why it drops to 3V under loaded conditions without tripping the protections.

Warning: Stop trying now and get the transformer serviced, or a nasty arcflash will ruin the whole unit and cause a potentially deadly situation.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5

Re: Problem In 11k/440v Transformer

04/21/2014 3:12 PM

The problem seems to be a failure to de-energise the equipment and call in a qualified Electrician, Boss.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7

Re: Problem In 11k/440v Transformer

04/21/2014 11:47 PM

My guess, site unseen......

  • The neutral is not grounded.
  • The ground is connected to the Y phase.
  • Until the neutral is grounded there will not be a short cct on Y phase, hence no protection is popping or unprotected conductors glowing.

Disconnect the ground wire from the Y phase, measure again (phase to earth will be wandering a lot as you now have an isolated trafo) and then deck the neutral and measure again.

I had to check this with a pencil and a bit of paper. Once you see it drawn the voltage readings listed are in accord with my guess.

Taking a stab in the dark here....your electrician was just a mechanical assembler with no real electrical knowledge and G/Y(ground) was connected to Y as it was the nearest colour match..... or yellow sheathed conductors are used for ground as well....

You get that.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#8

Re: Problem In 11k/440v Transformer

04/22/2014 1:07 AM

Vy seems to be shorted to ground on load. need to check the same. Eliminate one by one load on Vy and check if the voltage is improved above 3 V. You neeed to see if the problem is on load side as well. Check one by one breakers by switching off and checking the voiltage.

Also check if some lighting load and other single phase load is taken in this Vy and some short circuit some where to the ground. This could be serious as the system is not tripping even when grounded some where. Looks like there is no protection circuit on this phase load side. Also seems mostly the load is on Vy only as there is no data as how much load is given and what is the distribution across pahses. dont see iny dip in voltage, seems there is no substantial laod or loading factor is very low. If the total load is on single/ two phase only. Thoroughly check the load pattern on Vy.

__________________
Best Regards, Shivaram
Register to Reply Score 1 for Good Answer
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#9

Re: Problem In 11k/440v Transformer

04/22/2014 1:40 AM

What is system earthing for Transformer. I guess IT (Insulated Earth)

In that case Your transformer is healthy. (Equal voltages on phases)

When load is connected one of the phase, which got earthed in load, pulls that phase voltage near to zero and other phase reads heigher.

Check Load....

__________________
When was last time you did something for first time.
Register to Reply
Active Contributor

Join Date: Jul 2012
Location: kathmandu,nepal
Posts: 13
#10

Re: Problem In 11k/440v Transformer

04/22/2014 2:00 AM

when transformer is at load condition...according to your measurement..it shows y phase to ground voltage drops 3 volts and remaining phases are showing more voltages..it means you have a problem of y phase body leakage when it comes on load ...if the load has such problem... check that load's insulation phase to ground ...then transformer..then supply LT line's insulation..then you can find the problems.

Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#11

Re: Problem In 11k/440v Transformer

04/22/2014 4:04 AM

Ground is not properly connected at TR. Check the voltage between Phase to TR structure body and note down the voltage, then check the voltage between phase and substation main ground. If you get the correct voltage between phase and the main substation ground then problem is with ground connectivity with TR. And if the same voltage persist as shown in your readings then TR must be tested on site. I faced the some how similar volt drop on load problem and that was due to the Tap changer terminal burnt out.

__________________
There are no shortcuts on the road to a great experience.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#12
In reply to #11

Re: Problem In 11k/440v Transformer

04/22/2014 4:27 AM

OP did say that his measurements were performed and noted with no loads attached.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13
In reply to #12

Re: Problem In 11k/440v Transformer

04/22/2014 4:49 AM

Why is that OT?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#14

Re: Problem In 11k/440v Transformer

04/22/2014 9:03 AM

1.I would confirm my readings first, if they are taken from a reliable spot.

2. Is the Y neutral point grounded well.

3.Is the frame grounded well.

4. Is the cable connections correctly done especially the neutrals and earths.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#15
In reply to #14

Re: Problem In 11k/440v Transformer

04/22/2014 9:52 AM

Valid points that must be done by the on site technician but questioning the validity of the data is evading the question instead of answering the question.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 6)
Associate

Join Date: Apr 2014
Posts: 51
#17

Re: Problem In 11k/440v Transformer

05/17/2014 4:27 AM

Everyone is saying Y-phase is grounded how it's possible

Can you ground a live phase to ground

Go and try it you might very severe fault even at the cost of life.

If live phase get grounded it leads to very high current and transformer protections will get tripped.

Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#18
In reply to #17

Re: Problem In 11k/440v Transformer

05/17/2014 5:41 AM

I guess they said Y neutral point is grounded. It means the star point of winding.

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abasins (1); Aseer (2); binod panthee (1); Crabtree (1); Happy singh (1); navdeep_goyal (1); North of 60 (2); pillay (1); RAMConsult (1); redfred (2); shivaganti (1); Wal (3); Yahlasit (1)

Previous in Forum: Duty Type of Universal Motor   Next in Forum: Unbalanced Load Lose Calculation

Advertisement