Unbalanced Load Lose Calculation

04/22/2014 2:34 AM

Dear experts,

We know that there is a power lose because of having unbalanced 3phase load, how can i calculate the power and money lose because of unbalanced load in a building or a factory MDB. Thanks in advanced

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Unbalanced Load Loss Calculation

04/22/2014 7:15 AM

For your edification, the word is "loss", not "lose".

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Participant

Join Date: Apr 2014
Posts: 3
#2
In reply to #1

Re: Unbalanced Load Loss Calculation

04/22/2014 7:47 AM

Thanks for your edification for my misspelled

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Unbalanced Load Lose Calculation

04/22/2014 9:45 AM

Don't try to calculate it. Measure it.

Register to Reply
Participant

Join Date: Apr 2014
Posts: 3
#4
In reply to #3

Re: Unbalanced Load Lose Calculation

04/22/2014 9:49 AM

Yes, but i like to know how much i lose power and money because my load is unbalanced, this is what i have asked to do in my work.

Thank

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Unbalanced Load Lose Calculation

04/22/2014 10:08 AM
Register to Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Unbalanced Load Lose Calculation

04/22/2014 1:41 PM

Please describe the tariff structure applied to this unbalanced load.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: Unbalanced Load Lose Calculation

04/22/2014 3:40 PM

Your 3 phase meter does not know, nor does it care, about the degree of imbalance, it will still only record the amount of energy consumed. Your utility might though, and charge you a penalty for being severely unbalanced. Unbalanced loads can also lead to poor power factor, another area where you can be penalized by the utility. As PWS pointed out, only the tariffs will tell you if this is the case.

The place where an "extra" charge might occur is through the extra heating that your motors might be experiencing as a result of the imbalance, and the additional loss of life that the heating may be causing. Calculating this is problematic, it's much easier to take Lyn's suggestion and actually measure the difference between balanced and unbalanced operation at the same mechanical loading. Rent a power quality meter and balance your loads, and/or hire an electrical engineer to guide you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Unbalanced Load Lose Calculation

04/23/2014 6:27 PM

If you're that worried by losses caused by imbalance install transformers with a Zig-Zag secondary.

I dread to think what they will cost.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #8

Re: Unbalanced Load Lose Calculation

04/23/2014 7:02 PM

...and it will be money wasted. A zig-zag transformer does not magically balance the circuit nor eliminate the losses, it will however provide a low impedance path for trapping the resulting third harmonic/zero sequence currents, similar to what a delta winding does.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

JohnDG (1); lyn (2); PWSlack (1); RAMConsult (2); TonyS (1); Vince_123 (2)