Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

06/17/2007 7:47 AM

We have conveyor panel in which one frequency drive operate 4 nos induction motor of 3 KW each protected by MPCB, we are facing problem that whenever there is fault in the motor like : earth fault/short circuit/single phasing etc this leads to failure of drive

Drive Name Plate: 15/11 kw, AC Drive make: ABB, Type: ACS 550-01-031A-4, I/P: U1=380-480 volt, I1: 31 Amp, F1: 48 - 63 Hz, O/P: U2=3 Phase AC, In/I2hd=31/23 Amp, F2 = 0-500 Hz

Input MCB: 40 Amps

Application: Conveyor motor

Motor Rating: 3 Phase Induction motor, 3 KW, 1415 RPM, 415 VAC

MPCB Rating: 4 – 6 Amps

One Frequency Drive operate 4 Motors of 3 KW rating

Cable length from drive to motor max. 20 mtr

Failure in the Drive is IGBT and Semikrone Diode, When Fault occurs Main MCB 40 Amps On input side trips

Please look into the matter to resolve the problem at the earliest

Waiting for your favorable Reply.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

06/17/2007 4:11 PM

Well yes, when there is a fault in the motor such as a phase to ground or loss of phase, the variable speed drive output section driving the motor(s) will most likely fail causing a short circuit on the input resulting in the operation of the circuit breaker.

Are you regularly having motors fail due to phase to ground faults?

Are you using screened cable to connect the motors to the drive? (you need to you know, it is in the manual).

__________________
jack of all trades
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#2

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

06/17/2007 11:44 PM

In my experience it is not uncommon for a failed motor to also damage the VFD.

A classic was a system of 6 vfd's on a common (ungrounded) supply transformer. If a motor went to ground most of the vfd's were destroyed. It turned out the voltage feedback from the vfd output was referenced to ground. It was also protected with MOV's to ground. So when the motor grounded (became corner grounded) the feedback was skewed with respect to earth ground, blew the MOV's which ionized the air and, well, it let out all the smoke that was designed into the circuit. Only problem was, it raised the common reference circuit also, and blew up all the other drives.

Very expensive.

Solution was to simply ground the Y point of the transformer (a code requirement in the installation anyways). Now the fault was resticted to one vfd. So damage has now been significantly reduced.

Motors going to ground is still a problem and appears to be a manufacturing problem.

Reply
Commentator

Join Date: Feb 2007
Location: Wales UK. Tel. +44(0)1446 741180
Posts: 72
#5
In reply to #2

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

07/05/2007 10:37 AM

Cant you detect a ground fault or single phasing condition , then trip the drive supply before any damage ensues?

I am thinking that maybe this is an application that can be served by a current detector I have developed. Using a current transformer it will detect fault current to earth> 200mA and provide a Volt-free output via an opto-triac device.

It is a totaly passive device, powered by the fault current alone.

__________________
INDI-LINK makes 'Light' of 'Current' events, a veritable window into wiring.
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#6
In reply to #5

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

07/05/2007 10:57 AM

My suspicion is there exists a large peak overvoltage from the PWM converter and the insulation system can't withstand it. There should be a filter and the cables to the motor installed to specification for VFD's to minimize the transient voltage levels. It is a standing wave problem better handled by minimizing the source of the problem.

However, I am interested in your device, and would apreciate a link to some info.

Reply
Commentator

Join Date: Feb 2007
Location: Wales UK. Tel. +44(0)1446 741180
Posts: 72
#7
In reply to #6

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

07/05/2007 12:10 PM

I'm having to send a separate desciption of the photo I sent you as I dont have your e-mail details.

In the photo you see two of my current detectors, one is intended for invasive insertion into a circuit, the other uses a current transformer for non-invasive means to detect current. The size of the C.T. can be much bigger to accomodate larger cable or eaven all three phases in a multi phase supply but of course C.T's only serve in AC applications.

1. The threshold of detection for C.T.Type (1 to 100 ratio) starts at I>200mA and I Max. of 1kA. 2 Volt-free outputs are also provided.

2. Detection threshold for invassive type is + or - 3mA but can pass >10 Amp if required. The polarity of current is also determined via one of the Volt -free outputs. This type can be used on dc or ac systems and can be resitively shunted to raise current det. threshold.

The purpose of these devices is to act as almost solid wire to allow the free unhindered flow of current between its 2 main terminals just as a wire 'LINK' but the flow of that current to energise a system of LED's acting as an 'INDI'cator. It is powered by the line current and needs no other power supply.

In use there is a fractional volts loss across the device in the order of < + or - 1 Volt, it is this voltage that serves to power the LED's via 2 *10 Voltage magnification circuits. The elevated voltage serves to power a series visible and I.Red LED. The I.Red LED being the TX. part of an opto-coupler device. There are two such circuits , one for each polarity of current.

There is much more to say but I am really not used not used to authering tech. manuscripts. if you need to know more just say so.

Hope you find it interesting.

__________________
INDI-LINK makes 'Light' of 'Current' events, a veritable window into wiring.
Reply
Anonymous Poster
#3

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

06/18/2007 7:18 AM

Hello,

You didn't say if any of the 6 amp breakers are also tripping at the same time as the drive failure.

If they are not tripping first, before drive failure, I would check their trip speed rating to see if they are fast enough for a semi-conductor enviroment.

I, personally, would not use circuit breakers between the drive and the motors. I would use free standing electronic overloads, ABB makes these. I think you will find the trip speed is faster with these and you can use the dry contacts in them to shut down the drive, hopefully before damage.

Reply
Active Contributor

Join Date: May 2007
Posts: 18
Good Answers: 1
#4

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

06/18/2007 1:22 PM

I have always found that it is best to go to the source when you have fault issues with your Drives. The ABB Drives Customer Service phone number in the US is 1-800-752-0696. If you are unable to find a solution from the support team, there are other sources as well.....Robert Hansen, Manf. Rep for ABB Drives is a great resource in the NW Region of US-Cell 206-979-0586, email rhansen@carmodycompany.com, Fax 206-763-4084, 800-333-3103. Another is Jeff Coxen, Territory Mgr for ABB Drives, cell 253-224-7147. Hope this has helped.

MrHandyMan

Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

07/05/2007 6:35 PM

Nobody sitting at their desk banging on a keyboard is going to be able to diagnose your situation with any great accuracy. That said, I see a couple of blatant problems in your application right off the bat. It should be known that I work for a competitor to ABB so I have no particular need to come to their aid, but these issues can possibly help anyone using (or intending to use) VFDs in the manner you apparently are.

  1. I just re-read your ABB drive manual, they should have included specific instructions stating (at the very least) an advisory that if you have multiple motors, you put a load reactor on the output of the VFD upstream of the point at which you split off to feed the 4 separate motor protection devices (your MPCBs). Output reactors are a good way of protecting every VFD, (I call them cheap insurance) because they slow down the rise-time (by virtue of the inductive time constant) of the current flowing into a fault condition. That means that when you get some sort of a ground fault or bolted fault in ANY of the motor circuits, be it in the leads or the windings, the electronic protection systems within the VFD can have sufficient time to detect and react by blocking the transistor base signals, essentially cutting off the power flow. Without the reactor, the flow is almost instantly moving at the full capacity of the drive bus, in the case of the transistors (Semikrons as you put it) and in the case of the Diodes on the front end, potentially the full capacity of the power grid feeding the drive! There is no time for the VFD's microprocessor to detect, decide and act fast enough to prevent damage to its own components. Read this for more information; http://ecmweb.com/mag/electric_line_reactors_vfds/
  2. Complicating the above issue is that you have multiple motors. Not only do you now have (in your case) 4 times the number of fault points on the load side of the drive, but when any one of them faults, the remaining 3 will momentarily become generators out-of-synch with frequency coming from the drive, creating a severe voltage spike back onto the transistors of the VFD. That dv/dt spike can then cause the transistors to self commutate (turn themselves on) and leads to virtually instantaneous failure. Again, another reason for the load reactor.
  3. I do not believe you will find anyone stating that circuit breakers are the best way to protect a VFD from damage. Fast acting fuses (sometimes referred to as "semiconductor fuses") are recommended if you want to protect the drive. A circuit breaker is only the bare minimum device necessary to protect the circuit itself from a fire. Here is how it is worded in the ACS550 manual:
  • WARNING! Circuit breakers are not capable of providing sufficient protection because they are inherently slower than fuses. Always use fuses with circuit breakers, if you are not sure of the circuit breaker braking capacity and mains short circuit power.

In essence then, I believe your situation is not the fault of a defective or inadequate drive, but rather the results of someone having not properly investigated the proper issues in applying it. Perhaps the only culpability I see on ABB's part is their arrogance in wanting you to believe their drive can work on multiple motors without a load reactor. Most other VFD manufacturers I know of have that statement in their installation guide.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9
In reply to #8

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

08/12/2012 10:27 PM

Nice gesture to help somebody else's customer to read the manual.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Failure of IGBT & Semikrone Diode in the ABB ACS550 Drive

04/03/2023 9:33 AM

It sounds as though there is a maintenance problem to be solved: the <...earth fault/short circuit/single phasing...>. These things are not a feature of the <...frequency drive...>. Rather, they are a feature of the downstream cabling and whatever is connected to the end of it. Were threse things to be put right, <...earth fault/short circuit/single phasing...> is unlikely to occur, and the <...frequency drive...> will survive longer.

The practice of making one <...frequency drive...> operate <...4 Motors of 3 KW rating...> is not recommended, for a fault on any one of them will not be discriminated from the other three, meaning the <...frequency drive...> will continue to supply the fault, and the risk of its failure is higher than if four <...frequency drive...> units were in use. This feature is one of design, and a lack of proper attention to it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 10 comments