Sir is it adviseable to took oil sample from hermetically sealed transformer or what will happen after. thanks,
Rene
Re: hermetic sealed transformer
05/04/2014 12:13 AM
No, unless you suspect a problem, or the life cycle of the oil has expired.
What do the transformer specifications and operators maintenance manual say?
Why do you ask?
Good Answers: 67
05/04/2014 2:26 AM
Why was your reply marked off-topic? Your questions are perfectly natural and reasonable questions to ask in light of the OP's post.
To the OP: Well? What do those docs say and why do you ask?
05/04/2014 3:04 AM
Somebody didn't like it?
05/04/2014 7:14 AM
I always like your answers Lyn! Sometimes it's the only entertainment I get in a day, and very often enlightening!
05/04/2014 10:28 AM
Good Answers: 67
05/04/2014 2:00 PM
You want entertainment?
Do what I do: start trouble.
Good Answers: 67
05/04/2014 1:58 PM
I reckon so. Gave you a GA to wipe the slate.
Good Answers: 445
05/04/2014 1:28 AM
Yes, it is advisable to take oil samples for doing dissolved gas analysis (DGA) on a routine cycle for power transformers of sufficient size. This will enable you to see any developing trends in the breakdown of the oil or insulating materials.
A hermetically sealed utility power transformer has no intentional connection with the outside air, as opposed to one that has breather on it. If you do your gas collection correctly via a factory installed sampling point it will have no adverse effect on the life of the transformer, and should improve ii if you monitor the results and take the necessary corrective action should the DGA start showing signs of trouble.
Good Answers: 131
05/05/2014 8:19 AM
Not only should the oil be analyzed for dissolved gases, but also do aa general oil quality screen. Testing for dissolved moisture will point out if your hermetically sealed unit is not actually sealed as well as you think (sprung a leak somewhere!). Tests such as interfacial tension, acidity, specific gravity, and color number will point out deterioration of the oil due to oxidation, impurities, overheating, and other factors. The cost of the tests is cheap, and the information you get from them can help you head off a costly transformer failure by pointing out repairs or corrections that will not cost you nearly as much as a new unit.
Re: Hermetic Sealed Transformer
05/05/2014 10:00 AM
I thought the idea of having a hermetically sealed transformer was to avoid contamination of the oil.
I think the oil has a X hours rating, and this is long enough to last the life of the transformer. Unless the transformer has been run at well above its rated capacity for a long time, the oil should remain "good".