Transformer Vector Group for Power Transmission

05/04/2014 1:48 AM

A transformer connected at Factory site is Dyn11 (33KV/11KV) secondary earthed through NGR limiting fault current to 25 Amps and receiving power from Utility (Grid) transformer YD11 (132KV/33) with secondary earthed through Zig-zag transformer and earth fault current limited to 525 Amps.

The system appears perfect as long Factory site import power from grid.

Can same system be used to export power from Factory Site to grid?

Other information:

1.The connection between Factory site and Grid substation is through power cable protected with SOLKOR Rf pilot wire protection.

2. Factory site 33 KV SWGR is provided with 59V (Neutral Voltage displacement relay set at 20%)

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Transformer Vector group for power transmission.

05/04/2014 6:11 AM

Yes, so hire a consultant to help with it, Boss.

__________________
Good moaning!
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2
In reply to #1

Re: Transformer Vector group for power transmission.

05/04/2014 6:24 AM

Expecting better Answer....

__________________
When was last time you did something for first time.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6
In reply to #2

Re: Transformer Vector group for power transmission.

05/04/2014 9:19 AM

A schedule of charges, perhaps?

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Transformer Vector group for power transmission.

05/04/2014 7:51 AM

The first people to talk to would be the utility company. It won't be the first time they've turned round and said they don't want the site to export power. At the same time they will tell you if it's possible.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#4
In reply to #3

Re: Transformer Vector group for power transmission.

05/04/2014 8:30 AM

Expecting further better Answer....

__________________
When was last time you did something for first time.
Register to Reply Score 2 for Off Topic
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5
In reply to #4

Re: Transformer Vector group for power transmission.

05/04/2014 9:18 AM

Expect onwards.

__________________
Good moaning!
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#14
In reply to #5

Re: Transformer Vector group for power transmission.

05/04/2014 2:50 PM

Give a sincere try.....Boss

__________________
When was last time you did something for first time.
Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12
In reply to #4

Re: Transformer Vector group for power transmission.

05/04/2014 2:25 PM

How much are you paying members of CR4 as consultants?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: Transformer Vector group for power transmission.

05/04/2014 10:39 AM

You are expecting an answer that is to your liking. In truth talking to the utility is the right answer, if they do not want to let you export your power you cannot do so, regardless of any technical information that you can provide.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#9
In reply to #7

Re: Transformer Vector group for power transmission.

05/04/2014 11:51 AM

PPA (Power purchae agreement) is in place with Utiliy. so export is no problem...

Answer please if can answer question asked,

__________________
When was last time you did something for first time.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11
In reply to #9

Re: Transformer Vector group for power transmission.

05/04/2014 1:51 PM

Since you obviously know more about your situation than any of us care to know, why don't you tell us what your doubts are and why you think it won't work, and why you think vector group is even relevant in an already working situation; otherwise the answer still lies with your utility. Better yet, why don't you try it and see what happens.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#13
In reply to #11

Re: Transformer Vector group for power transmission.

05/04/2014 2:49 PM

System is commissioned and Importing power at the moment. Export is expected to start in 3 months with plant commissioning.

When Plant site importing power, transformer secondary at grid is earthed. so no problem. Any earth fault in interconnecting cable between Utility transformer and plant transformer would allow earth fault current through Zig-zag transformer and tripping source transformer.

When plant start to export transformer at plant site (11/33) would act as source and secondary is Delta.

What about protection for cable faults (Single phase to ground fault, etc). No return path for earth fault current to reach Delta connected secondary of transformer at plant site.

__________________
When was last time you did something for first time.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#15
In reply to #13

Re: Transformer Vector group for power transmission.

05/04/2014 3:04 PM

It's a bit late to start worrying about the consequences now, you're committed.

I doubt very much you will get any help from fellow members in the future.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#16
In reply to #13

Re: Transformer Vector group for power transmission.

05/05/2014 10:59 AM

One of the problems I see is - assuming your generators will be connected to 11kV bus, you need to have selection scheme between transformer neutral and generator (only one of generators will be earthed if more than one generator at 11kV bus) earthing.

You may have to go in for islanding protection to save generation (and the plant) in case of grid disturbances.

33kV cable 1-ph-ground faults cannot be supplied by the plant generation due the delta on 33kV side of 33/11kV transformer. This may not be a concern as the fault will still be supplied by the grid transformer and will be isolated as originally planned.

Hope the above is useful.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#8

Re: Transformer Vector group for power transmission.

05/04/2014 11:40 AM

Happy singh:

As you have requested I have the answers you want:

1. The dog ran to the wet creek and plugged in the transmission line. addendum- Don't want to have anyone attempt to insult me so answer is coded.

2. The dog ran back from the CR4 insane asylum to develop respectful answer for electrical engineering at 33KV SWGR 59v or 20% Addendum- This also is an attempt to not have anyone try to insult me so answer is coded.

In Summary- "You can catch more flies with sugar than you can with vinegar." (Famous quote from the distinguished chemist, Wiley T. Coyote) Interpretation- You can get many more good answers, like my disguised one is, with cooperation than you can with sarcasm. Interpretation of Interpretation- Lay off the Acetic Acid and cooperate and you will get my good answer and a lot of others like it.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#10
In reply to #8

Re: Transformer Vector group for power transmission.

05/04/2014 11:53 AM

Give it a real try.... and it is not coded

__________________
When was last time you did something for first time.
Register to Reply Score 1 for Off Topic
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (3); Happy singh (6); old salt (1); raghun (1); RAMConsult (2); TonyS (3)