05/06/2014 12:23 AM

I want to know the amount of energy saved upon installing an active harmonic filters in a building. Also, if i could be enlightened if any state governement penalises the individuals on exceeding the harmonic limits.

Register to Reply
Pathfinder Tags: cost benefit analysis harmonic
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: cost benefit of harmonic filters

05/06/2014 1:01 AM

It is guaranteed that the amount of energy saved will not exceed the amount that is being wasted, the quantity of which you haven't stated.

The only way that you can be enlightened is by contacting the AHJ (Authority Having Jurisdiction) in the state government of your choice, another thing that you have failed to share with us.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: cost benefit of harmonic filters

05/06/2014 2:19 AM

Start with something basic:



    Then if more power is needed, move up to the big 'uns:

    What? Huh?
    Oh harmonics? Whats that?

    Beats me.
Register to Reply Off Topic (Score 4)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: Cost Benefit of Harmonic Filters

05/06/2014 10:49 AM

harmonics are harmless, forget themhttps://www.youtube.com/watch?v=j-zczJXSxnw

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Cost Benefit of Harmonic Filters

05/06/2014 3:40 PM

Harmonic currents can damage electrical equipment on site (power factor correction capacitors for example). Your not going to see any energy savings eliminating them however (think electrical noise rather than lagging power factor).

What state? US, India, Mother Russia?

__________________
jack of all trades
Register to Reply
Participant

Join Date: May 2014
Posts: 2
#5
In reply to #4

Re: Cost Benefit of Harmonic Filters

05/07/2014 12:19 AM

so what would be the benefit of using the harmonic filters? why do we need to invest money into that?

I am from India and here there is no penalty by any of the electricity regulators.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #5

Re: Cost Benefit of Harmonic Filters

05/07/2014 12:35 AM

Well reducing maintenance due to poor power quality causing premature failure of electronic equipment in your workplace springs to mind.

Modern equipment generally has good harmonic filtering built in and so it generally isn't as big a problem as it used to be, but I am sure that in certain circumstances if poor quality equipment is installed in or near your workplace or certain large loads that produce large amounts of harmonics are present then separate harmonic filters could be of benefit.

For the average business owner, I don't see the need or point (although I am sure the people trying to sell you harmonic filters would say something different).

__________________
jack of all trades
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: Cost Benefit of Harmonic Filters

05/07/2014 1:12 AM

It's an operational benefit, not a cost benefit per se, though it could indirectly translate into one. The problem lies primarily in transformers which are subject to high harmonic currents, these currents are known to create additional losses which lead to overheating and shortened life.

Transformers known as K-rated are designed to accommodate this extra heat load and reject it safely without overheating, but of course they cost more than an equivalently sized regular transformer. In a plant with many transformers subject to loads rich in harmonics, it becomes an exercise in engineering economics to evaluate whether it is more economic to upgrade to K-rated transformers or to use harmonic filters to trap the harmonics at the source and keep them from reaching the transformers throughout the plant.

In either case the dissipation of the harmonic energy results in heat which represents a loss, but the location of the loss is being localized rather than being spread throughout the plant and possibly affecting other harmonic sensitive loads.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Participant

Join Date: Aug 2016
Posts: 3
#8

Re: Cost Benefit of Harmonic Filters

09/16/2016 8:39 PM

Look at the classical paper "Costs and Benefits of Harmonic Current Reduction for Switch-Mode Power Supplies in a Commercial Office Building", published on IEEE Transactions on Industry Aplications, Vol. 32, Nº. 5, Septembre/October, 1996, Thomas Key and Jih Sheng Lai.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #8

Re: Cost Benefit of Harmonic Filters

09/16/2016 10:30 PM

Yes, it is a good idea for you to reread it. When you do you will note that the conclusion points to why the proper place for the filtering to take place is in the circuitry of the SMPS (Switch Mode Power Supply); i.e., suppress the harmonics at their source, not after they have escaped into the power distribution of the office.

From the abstract of the article: "...Results show that an active-type harmonic elimination circuit, built into the common electronic equipment switch-mode power supply, is cost-effective based on energy loss considerations alone..."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: Cost Benefit of Harmonic Filters

09/17/2016 11:58 AM

One of the economic issues is capacity of equipment, primarily transformers. Harmonic current is typically not seen by revenue metering equipment, but it is nonetheless real. So if you have a supply transformer of 1MVA and your ITHD is 25%, effectively you can only use 750kVA out of that transformer, yet you pay for the fixed losses of a 1MVA transformer. The harmonic current doesn't show up directly on your bill, but the fact that you must have a larger transformer than you need definitely does. If you correct the harmonic current, you can either increase the use of your transformer, or use a smaller one and not pay for the extra losses.

A secondary issue is that although there may be no immediate tariffs on harmonics, there are usually requirements that you not create voltage distortion. Current distortion is what you pay for in your own facility, voltage distortion travels up stream and affects your neighbors bu causing current distortion in THEIR facility, even though they may not have caused it. That is why the IEEE519 specs call for controlling voltage distortion, and many people are unaware that it works both ways. YOU are not to cause more than 5% VTHD at the Point of Common Coupling, but conversely the UTILITY must guarantee to not allow more than 5% coming in. The only way the utility can do that is to require everyone nearby to limit it to 5%. How much authority they have to accomplish that varies by location, but at some point, they can always just refuse to deliver power to those who refuse to comply.

If you have your own generating capacity and don't buy from a utility, none of hat matters, but it will show up as extra fuel cost. Even if it is Hyde power, you will require more water flow PU of useable energy, which may have costs associated with it.

Bottom line, correction matters... The statement saying that it doesn't is just irresponsible.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2016
Posts: 3
#13
In reply to #10

Re: Cost Benefit of Harmonic Filters

11/20/2016 6:04 AM

Hi JRaef,

Could you explain to me, by way of expressing in mathematical formulas, what you have been taking into account linked to the effective use of 750 kVA for a 1 MVA transformer under 25% THDi, according the text below you have written before?

--------------------------------------------------------------------------------------

"Harmonic current is typically not seen by revenue metering equipment, but it is nonetheless real. So if you have a supply transformer of 1MVA and your ITHD is 25%, effectively you can only use 750kVA out of that transformer, yet you pay for the fixed losses of a 1MVA transformer."

Register to Reply
Participant

Join Date: Aug 2016
Posts: 3
#11

Re: Cost Benefit of Harmonic Filters

09/22/2016 5:06 AM

Aside from the Key and Lai article, published in 1997, according to the report "Installation of Compact Fluorescent Lamps Assessment of Benefits", prepared by Parsons Brinckerhoff Associates in 2006 for the New Zealand Electricity Commission, "the initial incremental costs of installing high true power factor (HPF) compact fluorescent lamps (CFL) is approximately 10 times less than the cost of capacitive compensation equipment which migh become necessary to counteract the degradation in power factor cause by using low true power factor (LPF) CFL.

Hence, taking into account that harmonic filters as well as electronics equipment is linked to a global production, what is the cost difference between HPF and LPF CFL? How can we evaluate the incremental cost of HPF and LPF electronics equipment (TV, PC, etc.)?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #11

Re: Cost Benefit of Harmonic Filters

09/23/2016 12:47 PM

Both studies reiterate my point that it is better to treat the problem at its source, rather than trying to remediate it at the system level. Evaluating the difference in the TCO (Total Cost of Operation/Ownership, etc.) will involve drilling down to the source costs, supply chain costs, installation costs, and operational costs, then comparing the results. Is your client prepared to fund such an involved study?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

chduarte (3); Fredski (1); gaurav3sharma (1); jack of all trades (2); JRaef (1); lyn (1); RAMConsult (4)

Previous in Forum: Cable Splicing   Next in Forum: Plugging in an Air Conditioner!

Advertisement