Constant voltage supply for motor applications

06/18/2007 10:55 PM

Dear Sir,

Due to transiant dips in the supply voltage in our factory, 60 HP DC motor driver goes to fault mode (under voltage). Is it there any device, which we can get steady volage out put for motor applications other than UPS for this kind of application?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Constant voltage supply for motor applications

06/19/2007 4:32 AM

If the motor continues to deliver sufficient shaft work despite the occasional low voltage, is it time to reduce the undervoltage trip setting?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#2

Re: Constant voltage supply for motor applications

06/20/2007 1:11 AM

Some drives will allow setting the undervoltage trip point.

There is also a rated supply voltage and then typically +/- 10% around that. In some installations I have deliberately tapped the supply transformer on the high side.

Is this a regen SCR phase controlled drive? Or is it non regen etc.

Regen drives operating at close to maximum voltage are not very tolerant of voltage brownouts or dips. Non regen are much more tolerant.

Some of the drives use the control voltage to sense undervoltage and this can be handled with a small PC UPS.

Then there are the "serious" power dip ride through arrangements. In one installation they had a synchronous machine with a very large flywheel. On a power bump or short power outage the flywheel would hold the machine for almost 1 minute as the frequency shifted from 60 hz down to 50Hz. We had to prove our drives would track the frequency shift to qualify as a supplier.

Register to Reply
Member
United States - Member - Florida Engineering Fields - Power Engineering - Power Systems Studies, Arc Flash, Power Quality, Generation Safety - ESD - Arc Flash Hazard & Training

Join Date: Apr 2007
Location: USA
Posts: 6
#3
In reply to #2

Re: Constant voltage supply for motor applications

06/20/2007 7:58 AM

GW you are right on here. Raising the taps on transformers can help a lot. You need to know your power system and what is causing the voltage dips. The flywheel synchronous generator is being done in many industries. I know in the Pulp & Paper industry it is done. The UPS on the control voltage can get you in trouble. The undervoltage is there to protect the drive from overcurrent. AC & DC drives are really current rated devices. Placing the UPS on the control voltage will remove this protection from the drive. Be careful.

__________________
RELEASE THE POWER
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#4
In reply to #3

Re: Constant voltage supply for motor applications

06/20/2007 10:50 AM

Careful is the key.

The particular drive I was playing with had both AC line feedback for synchronizing the gate firing and inverting fault avoidance etc, but on a brown out it gave up because the control circuit dropped out first (duuh) with the low voltage dc supply going undervoltage. That was a fun one to figure out! Drive was plated for 230/460 VAC, you changed taps on the control transformer, and the rest was software scaling.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#5

Re: Constant voltage supply for motor applications

06/20/2007 3:18 PM

This requires DC Filter Capacitor Bank of thousands µF to filter Ripples in rectifier O/P

And

support In-Rush current taken by a motor @ start; if it is not thru a "Soft-Starter" .

If the the motors are at different loctions & you have a single-DC-Power-Source then it will be better to have individual Capacitor Banks close to the motor-start-gear.

Or have suitable DC power sources just close to each motor-starting-gear

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#6

Re: Constant voltage supply for motor applications

06/25/2007 5:39 PM

Use of constant voltage transformer can solve your problem . These transformers are fitted with servo controlled tap changing which gives smooth control of voltage correction at the out put of the transformer. I have been using them for our Electroplating plants and certain critical machines where voltage fluxuation was giving me regular breakdowns. In your case you need not do voltage correction for motors since it is expensive but can purchase a small capacity servo controlled voltage Stabiliser for the control panel only.On load tap changing transformers are also available with automatic voltage correction which can be installed at your substation. For more information contact manufacturers.