Hi All,
I have this week been datalogging a 30KW 3-phase induction motor which drives the HPU on one of the machines that we build. Supply is 400V 50HZ. Motor is connected in delta and is started unloaded DOL. My mission in doing this is to identify possible energy savings.
Everything seems to operate OK, but I get a slightly puzzling set of line current measurements : a typical set would be phase A = 50.6A, phase B = 54A, phase C = 56.7A.
Line voltages are all close to equal - less than 2V differences. The feeder circuit has been carefully checked for any obvious problems with circuit breaker, control contactors and feeder cables. All check out OK, and the voltages at the motor terminals are all very close to the supply voltages so I think that it is unlikely that the feeder circuit is at fault.
I guess this leaves the motor.
I am wondering if there is any wisdom to be had as regards how out-of-balance the line currents can be before it becomes a problem? Here, the imbalance is a little over 10%, and this seems (to me) a bit on the high side.
I know that it is often the case that telephoning or emailing the supplier/manufacturer is the best way to get answers to questions such as these, but in this case the manufacturer is a large global company with a well-established reputation for being Generally clueless when asked for technical support, so I'm not going to waste time asking them.
Thoughts, anyone?
Good Answers: