3-Phase Induction Motor Line Current Balance

05/15/2014 11:11 PM

Hi All,

I have this week been datalogging a 30KW 3-phase induction motor which drives the HPU on one of the machines that we build. Supply is 400V 50HZ. Motor is connected in delta and is started unloaded DOL. My mission in doing this is to identify possible energy savings.

Everything seems to operate OK, but I get a slightly puzzling set of line current measurements : a typical set would be phase A = 50.6A, phase B = 54A, phase C = 56.7A.

Line voltages are all close to equal - less than 2V differences. The feeder circuit has been carefully checked for any obvious problems with circuit breaker, control contactors and feeder cables. All check out OK, and the voltages at the motor terminals are all very close to the supply voltages so I think that it is unlikely that the feeder circuit is at fault.

I guess this leaves the motor.

I am wondering if there is any wisdom to be had as regards how out-of-balance the line currents can be before it becomes a problem? Here, the imbalance is a little over 10%, and this seems (to me) a bit on the high side.

I know that it is often the case that telephoning or emailing the supplier/manufacturer is the best way to get answers to questions such as these, but in this case the manufacturer is a large global company with a well-established reputation for being Generally clueless when asked for technical support, so I'm not going to waste time asking them.

Thoughts, anyone?

__________________
paulusgnome
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Associate

Join Date: Apr 2014
Posts: 51
#1

Re: 3-Phase Induction Motor Line Current Balance

05/15/2014 11:52 PM

If there is line voltage difference is of 2V then there will be phase to phase voltage difference of 4 to 5 volts in 2 phases and 8 to 9 volts in other phase to phase voltages so means there will be voltage difference of 2 % so 2 % voltage difference will leads to 4-5% difference in currents so there isn't much differences so carry one there will be not be such a huge difference

Motor will be kept running smoothly.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: 3-Phase Induction Motor Line Current Balance

05/16/2014 12:25 AM

Current unbalance can be 6 -10 times the voltage unbalance ! There are many articles on the web about this, here is one example : Current unbalance

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: 3-Phase Induction Motor Line Current Balance

05/16/2014 4:53 AM

It is folly to look for energy savings here. Switching the motor off when not in use is a far better way of saving energy than looking at imbalance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#4
In reply to #3

Re: 3-Phase Induction Motor Line Current Balance

05/16/2014 5:09 AM

You misunderstand, the energy savings are aside from the imbalance question and are part of a much larger study of how to design high-efficiency hydraulic machines.

It looks as if the imbalance is reasonably normal, that even a small voltage imbalance can lead to the levels of current imbalance that I was seeing. All good then.

__________________
paulusgnome
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: 3-Phase Induction Motor Line Current Balance

05/16/2014 5:51 AM

Well, that makes energy savings and imbalance two separate topics, thereby clearing the misunderstanding.

High-efficiency motors are the way to go. Hydraulics are an inherently "lossy" way to transfer power though very convenient for certain applications. One of the most efficient ways of transferring power is the derailleur-gear-shift-based bicycle chain, which is why hydraulics have made no headway in powering bicycles.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#6

Re: 3-Phase Induction Motor Line Current Balance

05/16/2014 10:04 AM

Is this the only unit to display these imbalances ? Is the RPM a close multiple of the Frequency ? If so have you investigated the possibility that the HPU is changing torque requirements each rotation ? If the motor is more balanced during no load or disconnected operation, you might have a clue where to look. Are there indications of vibration, during what operations, and etc. Do you have a fast pressure transducer to track and compare hydraulic pressures ? I am grasping at straws here, trying to think outside the box.

__________________
Smart as a post and twice as fast.
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: 3-Phase Induction Motor Line Current Balance

05/16/2014 10:49 AM

Generally there are natural current imbalances in motor windings, especially at this size where the winding of the coils is random. Layering of the wraps, slight differences in magnetic permeability of the stator laminations, irregularities in the slot dimensions etc all play very small parts in creating differences in impedance and/or resistance in the circuit that create these small differences in current. But then these small effects can be amplified by relatively normal voltage imbalances to produce what appear to be higher current imbalances than you might expect. To verify if this is the case, simply "roll" your phases as they relate to the motor connections. Don't change the rotation, just shift each phase connection over by one. You should see different values under the same test conditions. I have people do this when they have problems starting Star-Delta motors where the transition spike causes breakers to trip. Exploiting these slight natural circuit impedance differences can sometimes mean the difference between a cheap fix and replacing an open transition Star-Delta starter with a more expensive closed transition version (assuming I didn't get to them in time to convince them that Star-Delta starting is a bad idea in the first place).

Secondly: current imbalance CAN indeed represent a loss of efficiency in the motor! When you have a current imbalance, you end up with higher negative sequence currents. Negative sequence current in an AC induction motor stator creates a counter rotating magnetic field in the rotor, which robs you of torque and causes rotor heating that is disproportionate to the stator current (which is how your overload condition is monitored, which is why imbalance protection is important). So for the motor to produce the same amount of shaft torque, the PU kW consumption will increase because the rotor will be running hotter, which is wasted energy. Generally we don't worry about it at a 10% current imbalance level from the standpoint of motor life, they are designed with that in mind. But by the same token to say imbalance is not related to efficiency is over generalizing the situation too.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#8

Re: 3-Phase Induction Motor Line Current Balance

05/16/2014 4:39 PM

Thanks for all the helpful replies.

The machine in question is now being dismantled and packed into shipping containers so I can't do any more testing now but when it is reassembled on site I will see what effect rolling the phases has.

This is not the first time that I have seen current imbalance in these motors but this was the largest that I could recall, hence my original question.

As far as the hunt for energy savings goes, if it were just as simple as using high-efficiency motors then the hunt would have been over some time ago. However, things aint that simple. We build large applianceware machines that make the doors, cabinets etc for domestic appliances. These are typically multi-stage machines that bristle with servos, vfds, pneumatics and hydraulics. The hydraulics do all of the heavy-lifting jobs - pressing, notching, piercing, clinching etc and not surprisingly use the lion's share of the electrical power consumed. All loads vary in a complex, repeating pattern with machine activity.

The broad questions that we are looking into in the quest for greater energy efficiency are along the lines of : 1) whether it is better to use just one big HPU for the whole machine, or to use several smaller HPUs, 2) how to best use hydraulic accumulators to maximise efficiency, and 3) what is the most efficient way to electrically control the motor(s).

This is an ongoing project and it has already given us some valuable information. There's quite a bit more play in it yet however.

__________________
paulusgnome
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#11
In reply to #8

Re: 3-Phase Induction Motor Line Current Balance

05/20/2014 4:33 AM

During reassembly/ installation at site please check the L-L inductance and resistance of the motor windings to identify the cause of current unbalance.

MANINDRA

__________________
Manindra
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#9

Re: 3-Phase Induction Motor Line Current Balance

05/17/2014 8:20 AM

More detail is nice. This does remind me of a warranty case where I was called in to support a sales engineer. We had supplied a motor but not the drive on an installation and the customer complained of noise and unbalanced currents in the motor. In this case the motor "drive" was a vfds by a competitor but was also new. When I heard the "motor noise" I suspected the drive and asked the customer to put the drive into bypass and run it straight off the power system. The noise and unbalance disappeared and I told them to contact the drive manufacturer. The problem turned out to be failed solid state device in the motor that was operating in parallel with several more good devices and allowed the drive to function, but did not allow it to do so correctly. The manufacturer of the drive remedied the situation quickly.

I am not suggesting that your problem is similar, but in the future it would be good to verify that you system is capable of supplying power in a balanced way, and then if you have unbalance in the motor, connect it directly to the power, bypassing the vfd. That way you can separate problems in the motor, connections, and vfd in to separate entities and correct problems rather than shipping them off to your customer, where the solution to any problem is much more costly than correcting it in a factory setting.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#10

Re: 3-Phase Induction Motor Line Current Balance

05/17/2014 10:09 AM

It would appear that none of the discussers has "hit the nail on the head" with respect to the problem. The problem we have here is of Positive and Negative Sequence. It is the Positive Sequence voltage (and power) that makes the motor rotate in the desired direction, . . . and it is the Negative sequence voltage (and power) that is trying to make the motor rotate in the opposite direction. You need to analyse the incoming voltage and determine how much negative sequence voltage you have. Any Negative sequence voltage will case the motor to be less efficient.

The useful power in the motor is (the Positive sequence power) - (Negative sequence power); while the power supplied to the motor is(Positive sequence power) + (Negative sequence power). One can see very readily that the efficiency of the motor will fall drastically with an increase in Negative sequence voltage and power. The standards do specify the limits of negative sequence for three-phase motor efficiency testing and operation.

If three-phase motors are to be installed on a system with excessive negative sequence, such installations may feature a "negative sequence regulator". Such a regulator will reduce the power consumption by increasing the efficiency of the motors.

Register to Reply
Register to Reply 11 comments