Starting Current of Motor Through VFD

05/17/2014 6:24 AM

Hi every one,

Can you please let me know the formula for calculating the starting current of a 100 kW compressor motor started through a VFD starter?

Thanks in advance.

heyram

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: starting current of motor through VFD

05/17/2014 8:19 AM

nope

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: starting current of motor through VFD

05/17/2014 8:22 AM

For the 2nd time.

The manufacturer's literature will give all the information you need.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: starting current of motor through VFD

05/17/2014 10:20 AM

There isn't really a formula for this. The rule of thumb is about 2.5 to 3 x FLC.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Apr 2014
Posts: 51
#4

Re: starting current of motor through VFD

05/17/2014 10:36 AM

VFD has an application that it acts like a starter with reduced voltage starting which will limit high in-rush current.

You can go through article below and find the same:-

http://electrialstandards.blogspot.in/2014/05/benefits-of-vfds-other-then-power-saving.html

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: starting current of motor through VFD

05/17/2014 12:16 PM

Not every situation can be defined by a mathematical formula.

Not every problem can be solved by a mathematical formula.

If you are compiling load information for a transformer, to be safe, use the FLA (full load amp) of everything that the transformer will supply, plus a safety factor, plus any anticipated future loads.

This figure can be calculated by simple addition.

Register to Reply Score 1 for Off Topic
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: starting current of motor through VFD

05/17/2014 12:47 PM

Of all types of ways to start an AC induction motor, ONLY a VFD can possibly do so without exceeding the motor full load amps, as long as you have all the time in the world to accelerate it, and your load does not require 100% of the motor torque as load torque.

To accelerate a load from a stop, you need enough torque to move the mass (inertia) of the connected load + the motor inertia, then to overcome the friction and any other minor influencs such as windage, plus just a little more. When someone SIZES a motor, those same issues go into the full load torque requirements as well, except the extra. That "little more" is referred to as "Average Accelerating Torque" (AAT), which factors into the RATE of acceleration. The rate of acceleration is determined by the maximum acceleration time you can live with. That then is a factor of what you require at the LOAD side, as well as what the MOTOR can withstand thermally. The motor thermal limitation is a factor of the current applied to it and the thermal time constant inherent it it's design, meaning the rate at which it can cool itself. When running at full voltage and full speed, the current is equal to the torque output (and efficiency), so it is primarily load dependent. But when started with ANY method other than a VFD, the current is very high compared to the work being performed, so there is excessive heating taking place, which is limiting the time you can take to accelerate it. So tarting is always a game played between the load acceleration time and the thermal damage curve of the motor.

But when you have a VFD, the drive is capable of making the motor create its rated Full Load Torque at ANY speed, even theoretically zero speed (requires a special version). So that means that since the motor can deliver its rated torque continuously during acceleration WITHOUT exceeding the Full Load Amp rating of the motor, which it can technically do so forever. So then since you do NOT need to worry about the motor thermal constant during acceleration, you are left with ONLY the requirements that the LOAD may have for acceleration rate. If there are none, you can take a minute, an hour, a day, a week, a month or a year to fully accelerate that load, it's all the same to the drive and motor.

Caveats: 1) the motor must be designed such that it's thermal constant does not rely upon a shaft connected cooling fan, because when the motor is turning slow, so is the fan, and generally the fans are designed to cool the motor when it is at full speed, so the convection cooling is reduced at slow speeds. So you must use at least a TENV motor design, or better, a motor with a blower that is powered separately from the motor shaft so that it delivers full cooling all the time. 2) simplistic V/Hz drives are not going to be able to accurately control torque below about 25% speed, so acceleration at the low end like that can often require upward of 150% current. Vector drives mitigate that.

Bottom line, there is no formula that you can use, it is totally dependent upon external issues affecting your maximum acceleration time. So once you determine THAT, you can use standard load acceleration formulae to calculate the AAT you will require, then from that you can determine the effect that torque will have on the motor thermal model, which will become the limiting factor on the acceleration time. But if the motor thermal limit is below the external load acceleration time limits, then you need not be concerned.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #6

Re: starting current of motor through VFD

05/17/2014 1:56 PM

All true, accurate and explains exactly why a VFD works so well on an induction motor. However, this is not exactly what the OP asked for. The OP asked for a formula for calculating the starting current using a VFD on an induction motor. To do this I prefer using the Steinmetz model of an induction motor. A careful analysis of this motor will reveal that this model is valid for any frequency with but a few simple caveats. Some of the loss parameters will change in a second order relationship if eddy current loops in the stator laminations become to severe and the slip between stator and rotor does not induce a stalling effect. For those willing to plow through a more nuanced model that includes these effects they should look here.

Here is a nice paper using the Steinmetz model that includes the mechanical loads of a compressor.

You will find many equations in these papers that should allow someone with the necessary mathematical skills to calculate any current from start to locked rotor condition.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#8

Re: Starting Current of Motor Through VFD

05/17/2014 11:47 PM

What kind of compressor????

__________________
devitg
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#9

Re: Starting Current of Motor Through VFD

05/19/2014 1:03 AM

What kind of VFD? A simple one like variable frequency may reduce inrush quite a bit but may increase motor heating due to longer startup times so it may not be the best solution. Without knowing the type of VFD we cannot answer. If it is a high quality variable speed drive that can regulate the quadrature and in-phase current components separately, it could be capable of actually starting faster than across the line and never exceeding the running amps of the motor. It is a long time ago, but the first time I saw it demostrated I was truly amazed. If you want an answer you must give the drive and motor specifications, we simply cannot answer this question blindly. The manufacture of the equipment can answer it, because he has the specs.

Register to Reply
Associate

Join Date: Jan 2009
Posts: 44
#10

Re: Starting Current of Motor Through VFD

05/19/2014 11:17 AM

Hi all,

Thanks everyone for the useful replies.

I wanted to know the current rating so as to find the voltage regualtion of my trfo when both the compressors start together. (worst case scenario). As on date the client is prfering to have only conventional start delta starter.

These compressors are oil free screw air compressors.

Register to Reply
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#11
In reply to #10

Re: Starting Current of Motor Through VFD

05/19/2014 12:06 PM

As you do you not answer the kind of comppresor , and as most of them, by this time, are rotative compressor , this kind of compressor start at almost no load , until it reach a given oil pressure , since there,it begin to have full work current.

I answer again , what kind , or brand and model it is?

Or it is confidential.

__________________
devitg
Register to Reply
Associate

Join Date: Jan 2009
Posts: 44
#12

Re: Starting Current of Motor Through VFD

05/22/2014 8:41 AM

It is Altlas Capco make. But I am not sure about the model No.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

4wsilver (1); devitg (2); Fredski (1); JRaef (1); lyn (1); navdeep_goyal (1); redfred (1); shivvaram (2); TonyS (1); Tornado (1)