Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 6:33 AM

Hello, I am doing arc fault test as per IEC 61641 in the busbar zone. This is a low voltage switchgear panel. I am sleeving my main bus with PVC and using a barrier between the phases. Will this barrier help in fast quenching of arc or will it have no effect. I want my arc to be extinguished in 4-5 milli seconds to avoid high pressure build up. should I use the barrier, since rest of the busbar is sleeved.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 10:26 AM

It sounds like you are doing this test without the guidance of someone who has done this before. The best advice anyone can give you is to stop right now and engage the services of a qualified consultant, otherwise the liability will be on you and your company when this happens.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 10:51 AM

Good grief!

:-O

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2012
Posts: 20
#4
In reply to #1

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 12:49 PM

I dont understand where the problem lies. Whether sleeving of busbar and providing phase barriers is insufficient. So what else is required. I have performed this test in the past, where there we no arc products coming out of the panel, but the arc took a little long to self extinguish and hence there was too much pressure build up, causing the structural components to get slightly bent and damaged. However, there were no effects of arc like burning of indicators or creation of holes, melting of copper etc. I just need some way to reduce the pressure build up.

Relief flaps are already provided. I want to know whether the phase barrier plays any role in early extinguishing of arc. I feel my question is pretty straight forward. your concerns are highly appreciated. Thanks

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 5:49 PM

The problem lies between the chair and the monitor. You say that you've done this in the past, yet you want to know if the phase barrier plays any role in extinguishing the arc.

Phase barriers are there to provide physical separation between, and to prevent inadvertent contact with, live parts, tools, and operators. Once an arc is struck the phase barriers are there to minimize the probability of the arc jumping to other phases/metallic, parts, etc.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 12:10 PM

No. Stop what you are doing. Since you ask this question, you are not qualified for this type of work. You will kill somebody if you continue. You might even kill me.

As the French guard said in Monty Python and the Holy Grail, "I fart in your general direction. Your mother was a hamster and your father smelled of elderberries."

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Off Topic
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 10:45 PM

You seem focussed on pressure reduction. This can be done by using vents with spring-loaded lids of soe kind. A better solution is to look at tripping the incomer in the event of an arcing fault, There are photocell sensor-based devices for this. This is one step earlier and therefore better than pressure reduction. However, the best is to prevent any arcing fault happening in the switchboard....why should there be any chance of this in a well-designed busbar chamber at all ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#7
In reply to #6

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 11:11 PM

IEC 61641 tests the safety of a switch when an arc fault happens, not how to prevent an arc flash. The link shows how one of the certified testing companies performs a test on one of their designs. (No surprise here, their design passes.) In contrast here are some other tests done at another certified firm that are IMHO marginal at best.

This type of design work is not for amateurs to glean information from a public forum so they can pass their school work. I shudder to think that somebody with the responsibility to design what looks like this caliber of safety rated equipment would come to a public forum for critical information.

Can we please not help counterfeiters to undercut legitimate fabricators of safety equipment.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Off Topic
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #7

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/22/2014 11:54 PM

Ah yes, the beautiful MNS system i had seen at Ladenberg when i was working for ABB Heidelberg. i did convince the Indian management to bring the MNS to India. Regrettably, it was preferred by a small premium market. The bean counters predictably shut down the line after some time. However, since arc faults keep happening in inferior switchboards, ABB India did a tidy business in Arc Monitors.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#9
In reply to #7

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/23/2014 3:57 AM

@Redfred, thanks for posting one of our videos :) While possibly in your opinion marginal, this board was tested successfully. What more can be asked of it?

This design had no additional protection and had bare conductors. The challenge was to maintain the IEC 61439 tested design and pass IEC 61641 tests also, without any modifications, which it did.

Assuming the OP's board has passed the product test standard, fitting additional components, such as PVC barriers / covering busbars etc. would almost certainly make the initial temperature rise tests void. You need to consider the complete requirements when developing and understand what your outcomes need to be at the start.

Register to Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#11
In reply to #9

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/23/2014 5:25 AM

@ redfred, apologies those tests are all failures to show what can happen if you don't design / test your assemblies.

I thought you had given the link to our 61641 videos

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#12
In reply to #11

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/23/2014 7:03 AM

Glad to hear "from the horse's mouth" some further feedback on that video I found. I was not sure if the first test in that series was a pass or fail result. This one test is why I made my comment of marginal at best.

Keep up the good work Craig.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#13
In reply to #7

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/23/2014 7:37 AM

I rarely care why any of my comments get marked OT. This is one of those few times that I want to know why I've been marked OT. A friend and colleague was injured by a low voltage arc flash using equipment built prior to this standard being made. Several months prior to this incident a system I designed also had an arc flash where everything was contained and nobody got hurt. This caused me to be in the awkward position of formally adding my perspective to the incident report. This is why I'm passionate about electrical safety.

Equipment that passes IEC 61461 testing provides a critical level of safety.

Whoever you are that marked my passionate comments as Off Topic I defy you to explain yourself, COWARD!

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 4)
Active Contributor

Join Date: May 2012
Posts: 20
#10
In reply to #6

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/23/2014 4:19 AM

I also understand that there is very little chance of happening in a well designed busbar. However, it is the end customer who requires this, and also IEC specifies the intended locations for testing.

Register to Reply
Commentator

Join Date: Apr 2011
Location: KCM, chingola; copperbelt; zambia; southern africa.
Posts: 75
#14

Re: Internal Arc Fault Test Inside Switchboard As Per IEC 61641

05/29/2014 8:45 AM

CR4 ADMIN: Deleted Post

Vulgar/Rude/Improper Behavior: This post was deleted because it did not adhere to the behavioral policies of the site. Please review Section 14 of the CR4 Site FAQ and the CR4 Rules of Conduct.

__________________
an error does'nt become a mistake if corrected!
Register to Reply Off Topic (Score 6)
Register to Reply 14 comments

"Almost" Good Answers: