Motor Tripping on Locked Rotor?

05/24/2014 4:14 PM

Dear all, One of the motor tripping sometime on load jam protection provided in abb relay.....which is set to 1.84xin for 100ms with 350/1a ct.....checked pump numbers of time pump shaft rotates freely.......smoothly.....also at a triping current trends shows normal....there is no sign of over current before tripping takes place on load jam protecion.....that is also during motor runing condition Anybody faced similar problem ...or had any clue.....???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: motor tripping on locked rotor?

05/24/2014 5:04 PM

have you mesured the draw with a meter?it might just be a bad control, or its settings

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: motor tripping on locked rotor?

05/24/2014 5:31 PM

I have a clue.

1. Motor current normal.

2. "no sign of over current before tripping takes place on load jam protection; also during motor running condition"

3. "pump shaft rotates freely, numbers of time."

4. "protection provided in abb relay"

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2009
Location: Australia
Posts: 277
Good Answers: 45
#3

Re: motor tripping on locked rotor?

05/24/2014 10:38 PM

You seem to be saying that everything looks normal but that one of several motors is tripping out. On the assumption that there is not a "invisible/quick physical overload" situation that is properly being protected against, then the load protection relay is faulty OR the motor has to have an internal short that is giving too high a "normal" current (which you seem to say is not the case) OR the relay is an earth leakage type and there is a very small amount of leakage in the motor. An alternative to "leakage in the motor" is that the earth and neutral supplies are crossed or "cross leaking". The later case would more likely be quick and immediate, rather than just occasionally.

The one thing I can guarantee is that there will be a reason !!!!

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12
In reply to #3

Re: motor tripping on locked rotor?

05/25/2014 8:27 AM

basic troubleshooting and elimination is escaping him

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#4

Re: motor tripping on locked rotor?

05/24/2014 11:06 PM

You have a relay that is tripping on a load jam condition. Your motor is mechanically seizing then. It might be seizing because a bearing is failing and intermittently locking up. Your mechanical load might seize the motor then shatter under the impact leaving a freely moving motor after the trip. Measure a trip with a time based instrument. Believe your instrumentation or go home.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: motor tripping on locked rotor?

05/24/2014 11:18 PM

There has never been any indication of an over-amp of the motor.

Tigerdon is chasing his tail.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#9
In reply to #5

Re: motor tripping on locked rotor?

05/25/2014 6:24 AM

Until proper testing is performed, I believe the controller is working properly to protect motor and wiring. It seems far more likely we have an ESO condition than a false tripping controller.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6

Re: motor tripping on locked rotor?

05/25/2014 12:09 AM

could be a faulty controller! if you have another swap it out. If you have some means of trending the motor operation while running that might shine some light on the problem.

Or you do have a overload problem and your controller is not giving you the right message.. again swap the controller out!

One other thing what are you pumping? Does the density change?

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Apr 2014
Posts: 3
#7

Re: motor tripping on locked rotor?

05/25/2014 1:09 AM

Check the wiring through the circuit.

Ive had this issue before and found burnt or loose connections in the connection box on the motor or along terminal strips (which melt and sometimes cross phase or ground)...

Register to Reply
2
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#8

Re: motor tripping on locked rotor?

05/25/2014 6:03 AM

One of the phase conductors is not connected to the motor.

__________________
Good moaning!
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10

Re: motor tripping on locked rotor?

05/25/2014 7:24 AM

I think all the possibilities have been covered by previous posters here.

Assuming that wiring, fuses and phase direction have been properly set:-

I think personally that the current sensing has either been set too low and/or the timing has been set too fast.

I will wait and see what the final result is.....

The OP has NOT supplied full details to assist us up to now either......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#11
In reply to #10

Re: motor tripping on locked rotor?

05/25/2014 8:01 AM

This is a common occurrence here. I always find it a little odd when somebody is baffled by a problem how often they bring the least amount of information to a forum.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#13

Re: motor tripping on locked rotor?

05/25/2014 9:32 AM

1.84xIn for 100ms. Hmm, seems odd to me. A locked rotor situation is more like >6In for >6 secs (6000 ms!). Is this a recommended setting ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#14
In reply to #13

Re: motor tripping on locked rotor?

05/25/2014 10:37 AM

Recommended by whom: the motor manufacturer, Gary in the mail room, the system engineer, that cute receptionist?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#15
In reply to #13

Re: motor tripping on locked rotor?

05/25/2014 10:45 AM

since he already stated the shaft turns freely its clear the roto is NOT locked

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#16
In reply to #15

Re: motor tripping on locked rotor?

05/25/2014 11:25 AM

The motor, even if unloaded, will draw 6-8 times In won't it ? And this high current will last for several seconds. So, my (perhaps ignorant) doubt.... what does 1.84 In for 0.1 sec do ? Has ABB recommended this setting?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #16

Re: motor tripping on locked rotor?

05/25/2014 12:23 PM

Its as you say, wrong.

The cute receptionist does not have a clue!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Apr 2014
Posts: 3
#24
In reply to #13

Re: motor tripping on locked rotor?

05/26/2014 1:12 AM

Locked rotor would indicate a physical obstruction.

You'd find that in a bearin or gearbox.

Even without power applied.

Its an issue with one of the phases missing...they arent looking into it completely. Only other item is a contactor with something loose in it but even that can be found without current. They should follow the path of the current until they find it.checking and tightening each part of the circiut. It shouldnt be THAT long...lol and if it is, well there ya go! :)

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#26
In reply to #24

Re: motor tripping on locked rotor?

05/27/2014 2:11 PM

You are assuming the "tripping on locked rotor" is actually meaning there IS a locked rotor condition. At a setting of only 184% FLC, that is NOT defining this as a real locked rotor condition.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#27
In reply to #26

Re: motor tripping on locked rotor?

05/27/2014 2:31 PM

You are so right!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 79
#18

Re: motor tripping on locked rotor?

05/25/2014 12:58 PM

settings provided by engineering by coordinating motor performance curve with relay curve........ at a time of motor starting"in abb relay " startup supervision" function starts and block other function like earth fault and over current during starting phase..... however these last up to motor starting time which is very less ..compared to load jam prorection which is povided with 100ms .....

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19
In reply to #18

Re: motor tripping on locked rotor?

05/25/2014 2:10 PM
  • settings provided by engineering by coordinating motor performance curve with relay curve........ at a time of motor starting"in abb relay " startup supervision" function starts and block other function like earth fault and over current during starting phase..... however these last up to motor starting time which is very less ..compared to load jam prorection which is povided with 100ms .....

There is no motor protection scenario that would require tripping at 184% current in 100ms, so this is either a conscious decision to provide very strict mechanical protection for something else in the drive train, or the result of someone not knowing their rear orifice from a hole in the ground...

When a motor is called upon to RE-accelerate a load after a step-change, first the motor slows, which decreases the mutual induction between the stator and rotor, which then allows an increase in current. The increase in current then creates more torque, which re-accelerates the load back to stasis. If the load needs the full Break Down Torque from the motor to accomplish this, that is 200-220% of Full Load Torque, and since current follows torque, the motor will need to draw 200-220% current. Your setting of 184% however is restricting that from happening. So if there is ANY kind of step change in load, it is likely to cause that trip. Therefore unless there is some overriding compelling risk of mechanical damage due to a brief application of BDT, then this setting is, in my opionion, foolish.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#21
In reply to #19

Re: motor tripping on locked rotor?

05/25/2014 3:25 PM

GA

And funny too, thanks.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Member

Join Date: Nov 2011
Posts: 5
#20

Re: Motor Tripping on Locked Rotor?

05/25/2014 3:18 PM

Since it appears that all possible areas have been exhausted try doing a single phase test on the rotor. Here is how:

1. Disconnect motor from mechanical load. Provide appropriate safety protection for shaft

2. Apply 1/2 rated voltage to two leads of the motor with a clip on ammeter to watch the current.

3. Apply voltage and have someone slowly turn the rotor. If the ammeter jumps at certain points in the rotation then you have a short or break in the rotor bars. If it rotates around with no ammeter deviations then I do not know.

4. Warning the amps could be higher than expected so gage your power supply wires the same as your feeders and feed from an appropriate sized breaker

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#22
In reply to #20

Re: Motor Tripping on Locked Rotor?

05/25/2014 7:33 PM

Welcome to the asylum Gord.

As you may notice in this very thread, the idea of measuring what is actually happening instead of purely theoretical speculation will, at times, be considered too mundane, and almost pedantic here.

I'm with you on this one. Measure what is actually needed and then set trip relays to allow it to happen.

Once again, welcome to the asylum.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: Sep 2011
Location: Mumbai-India
Posts: 1
#23

Re: Motor Tripping on Locked Rotor?

05/26/2014 12:01 AM

Please open the pump casing & check for any foreign object in it. I guess there must be small object in side. When you rotate pump with hand it is free because the rpm is not sufficient to lift that object but when pump is started the object is lifted & it gets trapped between the gap of impeller & casing tripping the pump on locked rotor.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#25

Re: Motor Tripping on Locked Rotor?

05/26/2014 1:29 AM

For fire pumps they select high tripping current rated protective device

__________________
pnaban
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Apr 2011
Location: KCM, chingola; copperbelt; zambia; southern africa.
Posts: 75
#28

Re: Motor Tripping on Locked Rotor?

05/28/2014 8:55 AM

funny being here, too many random engineers. the engineers in blankets their degrees is google.

do some secondary and primary injection test on your CTs and Relays, something is wrong with your wiring and physically check the bearings, some bearings dont show the restriction. it comes on and clears.

__________________
an error does'nt become a mistake if corrected!
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 79
#29

Re: Motor Tripping on Locked Rotor?

05/28/2014 10:16 AM

There is startup supervision during motor starting time which blocked overcurrent, earth fault& locd jam ........protection functions Sometime motor trippes during starting and some time after starting and running of say half an hour...however there is no sign of overload overcureent at a time of tripping on load jam ........

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#30
In reply to #29

Re: Motor Tripping on Locked Rotor?

05/28/2014 11:41 AM

The humble thermal overload relay which costs less than $10 perhaps, does not require blocking any protection function... single-phasing, locked rotor, general overload etc. It is incomprehensible to me as to why an expensive electronic relay needs to override certain protection functions while starting....effectively leaving the motor unprotected during starting ... strange.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#31
In reply to #29

Re: Motor Tripping on Locked Rotor?

05/28/2014 12:40 PM

<sigh> Sometimes I don't know why I even try...

Last time...

At a setting of 184% FLC for 100ms, I would not carachteristics that as an "overload". Any NORMAL operation can create a brief LOAD RESPONSE of that magnitude or greater just from a rapid step change in NORMAL loading. It is inherent in the way an AC induction motor works. So either your 184% setting is too low to avoid NUISANCE tripping during NORMAL operations, or someone has DELIBERATELY insisted on that setting for SOME OTHER HERETOFORE UNKNOWN REASON related to mechanics in some other part of the drive train system. THERE IS NO REASON FOR A SETTING THIS LOW THAT RELAES TO PROTECTING THE MOTOR ITSELF.

So have you inquired yet of whomever made that setting decision as to their reasoning? If not, do so. If you have and their response was (as I suspect) ambiguous because they do not fully understand the issues, as you apparently do not, then someone with more than 6 living brain cells must decide on a MORE APPROPRIATE SETTING for normal nuisance free operation.

<end rant>

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#32
In reply to #31

Re: Motor Tripping on Locked Rotor?

05/28/2014 1:11 PM

GA

Well RANTED put!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 79
#33

Re: Motor Tripping on Locked Rotor?

05/31/2014 12:45 PM

There is startup supervision during motor starting time which blocked overcurrent, earth fault& locd jam ........protection functions Sometime motor trippes during starting and some time after starting and running of say half an hour...however there is no sign of overload overcureent at a time of tripping on load jam ........

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#34
In reply to #33

Re: Motor Tripping on Locked Rotor?

05/31/2014 1:07 PM

Excuse me but there is a sign of over current conditions, the relay tripped. Unless you test the current drawn with a separate instrument that is sufficiently fast enough to capture and store the current during a tripped condition you cannot say that an overload did not happen.

Where does all of this lead us? If an independent current measurement shows the relay is making a false trip then you should replace the failing component (relay or CT). If the relay is tripping on a real fault then you must find the source of the momentary mechanical bind.

Repeating the same information is over and over will not help.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Member

Join Date: Aug 2015
Posts: 6
#35

Re: Motor Tripping on Locked Rotor?

09/03/2015 5:32 AM

according to given situation your relay is seem to be faulty...so connect and other load{less than Motor) with relay and check if relay trip then replace the relay...

Register to Reply
Register to Reply 35 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (5); barryg (2); brich (1); Crabtree (1); DmanEng (1); Fredski (3); Gord Graham (1); JRaef (3); kvsridhar (3); lyn (2); Nitin.Kulkarni (1); pnaban (1); redfred (6); shafi niazi (1); tigerdon (3); TrevorM (1)

Previous in Forum: High Voltage Surge Arrestors   Next in Forum: Can a Peltier Element Cause a Fire?

Advertisement