Grounding of MV Switchgear Panels

05/30/2014 4:13 PM

Dear All,

Recently we have made a grounding pit with four (4) copper coated rods each of 1.5 meter length connected all in parallel. Then checked the ground resistance of copper rods independently with Kyoritsu Earth resistance tester using 3 wire method (Fall-of-potential), the resistance was 12.54Ω.

Later on we connected the grounding rods with the grounding cable coming from panels and again checked the resistance of the grounding rod from the same point as we checked earlier the result was 1.55Ω. Now I have the following questions.

1. Why is the difference in two readings?

2. Which one is the correct grounding resistance?

3. Is the 2nd method is correct or not?

Please guide me accordingly.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: GROUNDING OF MV SWITCHGEAR PANELS

05/30/2014 4:21 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Aug 2008
Posts: 19
#2
In reply to #1

Re: GROUNDING OF MV SWITCHGEAR PANELS

05/30/2014 5:55 PM

Thanks a lot SolarEagle (Guru), I got my answers from this reference guide.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: GROUNDING OF MV SWITCHGEAR PANELS

05/30/2014 7:03 PM

I think that it would be appropriate when someone performs research for you and supplies you with correct answers, the least you could do is vote SE a GA.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#5
In reply to #3

Re: GROUNDING OF MV SWITCHGEAR PANELS

06/01/2014 9:58 AM

Then why not give him one yourself Lyn?

__________________
Most people are mostly good most of the time.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: GROUNDING OF MV SWITCHGEAR PANELS

06/03/2014 7:57 PM

OK.

Register to Reply
Power-User
Fans of Old Computers - PDP 11 - New Member

Join Date: Mar 2007
Location: In a mushroom field somewhere in Canada. Kept in the dark and fed sh--, well you know.
Posts: 312
#6
In reply to #3

Re: GROUNDING OF MV SWITCHGEAR PANELS

06/02/2014 7:41 AM

CR4 ADMIN: Deleted Post

Abuse/Attack: This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ and the CR4 Rules of Conduct.

__________________
Dirt is for vegetables. Pavement is for racing.
Register to Reply Off Topic (Score 5)
Associate

Join Date: Apr 2014
Posts: 51
#4

Re: Grounding of MV Switchgear Panels

06/01/2014 2:16 AM

You checked individual pit resistance 1st that comes 12.54 ohm

now you checked grid resistance of four parallel earthing pits so resistance should be 12.54/4 i.e. approx 3 ohm.

Both methods of measurement resistance are ok

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Deefburger (1); lyn (2); manzoor14 (1); navdeep_goyal (1); SolarEagle (1); unclefastguy (1)