How to Read Graph for Circuit Breaker Testing

06/07/2014 1:18 AM

I have been testing Siemens Circuit breaker Using Megger Current injection test , I have observed the following values
Long time setting = .5 , Rating Plug In = 1600 A on injected 1250 A current we obtained the following values of trip time
1. 138 seconds cold , 156.5 sec hot 2.156.9 sec cold , 157.2 sec hot 3.159.0 sec hot , 154.5 sec hot
again on setting short time setting to 1.25 and injecting 2200 A we obtained the following values
1.791ms , 503ms 2.344ms , 343ms 3. 41 ms , 344ms

Please tell how to compare these values with the graph and conclude about the circuit breaker being ok or not .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: How to Read Graph for Circuit Breaker Testing

06/07/2014 8:01 PM

Why are you testing the CB if you can't correlate the results? Seems a bit pointless to me.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2012
Location: Sanskrit
Posts: 57
#2
In reply to #1

Re: How to Read Graph for Circuit Breaker Testing

06/08/2014 2:01 AM

I am trying to learn

Register to Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4
In reply to #2

Re: How to Read Graph for Circuit Breaker Testing

06/08/2014 3:50 AM

I agree with post#3.

I also recommend spending time with a qualified company engineer or contractor to gain experience in the field.

There are many variables to be considered;too many to list here.

No substitute for experience once you have a firm grasp of the basics.

You must do the "grunt work" first.

Everyone starts with no experience at the bottom of the totem pole.

Those that maintain their interest and curiosity ultimately end up at the top.

You have far to go, But you are on the right track.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
3
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#3

Re: How to Read Graph for Circuit Breaker Testing

06/08/2014 3:38 AM

The figures look too high as a very quick estimate The best solution for you to understand us to draw the curves on the graph for your settings, using what is already there as a template. So you have set the plug at 0.5. Draw a very fine line between the minimum and maximum settings where the curve goes from the vertical line to the angled line. Now draw a vertical line down at 0.5, stop when it crosses the line you just drew. Now draw a parallel angled line starting where your two lines cross. For now just take it down to the bottom of the page You now have a basic thermal curve. To read it correctly you work out the ratio of injected current over rating. So 1250/(1600x0.5) = 1.6 estimate that across the bottom, draw a vertical line from there and where it crosses your curve should be the trip time. A couple of points though. 1) you have not included the tolerance band, so it's not going to be exact, the catalogue should tell you what it would be 2) they generally either work or don't work. If you are getting strange times. Until you are confident, assume it's your error, not the OCR 3) as said above. It's vital that you understand how to setup and read the curves. Spend lots of time practicing before you even consider doing this on a real job.

Register to Reply Good Answer (Score 3)
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#5

Re: How to Read Graph for Circuit Breaker Testing

06/08/2014 1:51 PM

It may be a good idea to, physically and visually, verify the current transformer ratios. I have often found discrepancies, contractors are sometimes very unreliable when they know they won't have to maintain the system in the years to come. Your results do look a little on the high side.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#6

Re: How to Read Graph for Circuit Breaker Testing

06/08/2014 4:58 PM

It appears that you are attempting to measure the trip time of a breaker at 2200 A(rms), using a chart that goes to 100 A (rms). I think you need a different chart.

Register to Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#7

Re: How to Read Graph for Circuit Breaker Testing

06/08/2014 5:19 PM

It's the correct graph 1 = 100% rating.

Register to Reply
Commentator

Join Date: Apr 2011
Location: KCM, chingola; copperbelt; zambia; southern africa.
Posts: 75
#8

Re: How to Read Graph for Circuit Breaker Testing

06/11/2014 5:03 AM

are you sure you cant read that simple graph, whats there? time and current like what you got all the symboz are there!!!!!!!!!

__________________
an error does'nt become a mistake if corrected!
Register to Reply Off Topic (Score 5)
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: