mixing wires in conduit

06/30/2007 2:50 AM

I want to install ug-fed irrigation (sprinklers), area lighting on standard (120VAC), and surveilance camera on my grounds. Have dug trench and laid in (in addition to drain) one Sched-40 PVC (for water under pressure), and two electric conduits--preparing next to hook them togethere and back fill. In one electric conduit will be pulled three wires for the AC lighting. In the other I want to run (both):

  1. wires to power the 24VDC sprinkler zone valve(s) (these will operate 1 x 1/2-hr/day max), and
  2. video and 1-channel audio signal wires for the camera.

Question: Respecting 2., any problems with this wire routing? If so, what? And is there a preventative?

Thank you.

Posted in General, meaning C&E and/or EE.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: mixing wires in conduit

06/30/2007 2:52 AM

Correction:

Question: Respecting 1. and 2., any problems with this wire routing? If so, what? And is there a preventative?

Reply
Commentator

Join Date: Jun 2007
Posts: 64
Good Answers: 3
#2

Re: mixing wires in conduit

06/30/2007 11:27 AM

You have two conduits. Run ALL of the power cables/wires in one conduit and run your video and audio in the other conduit. This will provide maximum insurance against interference.

You probably will not have a problem with your original scheme, except that when the power switches off and on, you do have a risk of a momentary glitch in your video and audio. That also depends on how well you shield your video and audio cables.

The rules to minimize interference:

* Shielding

* Distance -- Distance away from power conductors or other sources of interference

Reply
Anonymous Poster
#3
In reply to #2

Re: mixing wires in conduit

06/30/2007 11:50 PM

Just a note in case the project is to be inspected: The low voltage is not permitted to be run in the same conduit as the 120v.

Reply
Anonymous Poster
#4

Re: mixing wires in conduit

07/01/2007 9:01 AM

I have tried this but now I always run them seperately, long lenghts of ac power wires running in parralel with low voltage cables will induce large voltages in your low voltage video cabales unless you are very good at screening. these voltages may (probaly will ) damage your low voltage equipment.

Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#5
In reply to #4

Re: mixing wires in conduit

07/02/2007 8:00 AM

Exactly. The low voltage video wires have to be completely shielded from the AC wires and, as one poster already pointed out, the low voltage wires have to be in a different conduit from the AC mains. The reason for the former is interference and power induction and the latter because the low voltage devices won't have the necessary safety circuits to handle the AC should the two make contact.

The low voltage run (assuming the conduit is not conductive) has to be shielded with a braided shield around a pair (or other multiple) of wires. The wires don't have to be twisted in this application, so that's a bit cheaper.

__________________
Eric
Reply
Anonymous Poster
#6

Re: mixing wires in conduit

07/02/2007 1:47 PM

Make sure you separate Class I and Class II wiring to comply with the National Electrical Code. If I recall, Class I is 50 volts and above, or anything over 100 watts.

Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member

Join Date: Apr 2006
Posts: 261
#7

Re: mixing wires in conduit

07/02/2007 5:50 PM

Before running the DC and Video in the same conduit, insure that it's clean DC.

D.C. derived from a transformer/rectifier bridge power supply will have a considerable
ripple which may effect your video signal.