I have 2 generators rated 150MW each, 138KV, 0.85pf lagging, each with respective outgoing 138KV lines with individual line breakers with a bus tie breaker common to both rated 145KV, 1600A, 40KA/3s. Can my bus tie breaker and line breaker on one line handle 2 generators supplying a total of 300MW power if the other line is on maintenance?
Good Answers: 444
Re: Can it Handle?
07/11/2014 9:40 AM
You need to know the impedances of your system, transformers, and generators in order for you to perform those calculations. And don't forget the generator grounding means and the short circuit mechanical withstand of your buss.
Good Answers: 42
Re: Can it Handle?
07/13/2014 4:04 AM
I agree, of course, with RAMConsult. However, in a case when one of main breakers is not available but both generators will be in operation then, I think, the tie breaker is not overloaded. Only [one of] the main breakers are [is] 5% continuously overloaded. The short-circuit current -if the generators are islanded [no system connected]-IMO- the short-circuit current will be not more than 6 kA [rms].
Julius
Re: Can it Handle?
07/13/2014 3:56 PM
Congratulations, you win the "MOST OUT OF DEPTH AND DANGEROUS QUESTION OF THE WEEK!!!".
I hope this is a homework question, either way your on your own.
WTF!
Re: Can it Handle?
07/14/2014 6:34 AM
Did you ring the bus tie breaker manufacturer and ask?
Good moaning!
Location: I live in USA, Colorado in the houses of 7 Summits
Re: Can it Handle?
07/26/2014 5:12 AM
Here in these case one will not always trust to the power grid to supply the energy, I don't the one from both will handle two generators supplying a total of 300MV power, due to internet fault the load is being served from a transmission line.