Transformer Synchonization

07/11/2014 12:32 AM

We have Two nos Transformer 1000KVA, 11KV/415V, Kirloskar Make OLTC, Connect with same Make AVR, is it Possible their Synchronisations!

Register to Reply
Pathfinder Tags: 1195
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Transformer Synchonization

07/11/2014 3:51 AM

Same vector group modulo 4, same wiring rotation?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Transformer Synchonization

07/11/2014 9:46 AM

Sounds like you want to parallel these transformers. In addition to Tornado's query on vector group, are the transformers otherwise identical; same ratings, impedances, tap changer settings. etc. If so then it should be "easy", but you also have to ensure that your surrounding switchgear can handle the quadrupled short circuit forces.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
3
Participant

Join Date: Jul 2014
Location: Chennai, India
Posts: 3
Good Answers: 1
#3

Re: Transformer Synchonization

07/14/2014 8:18 PM

Check that both transformers are identical in all electrical aspects and powered by the same source at the primary side. Ensure that the secondary side busbar, cables, switchgear etc are rated to withstand cumulative fualt MVA by both transformers, yes you can parallel both.

But keep it mind to parallel and operate both transformers at the same tap position. This is to avoid reactive circulation current and unneccassary heat developed.

parallel operation of transformers are normal in many utilities, but before that do proper fault calculations and short circuit withstand capacity study for all secondary equipments.

Note : - if both transformers are powered by different sources then dont parallel it. First consult a experienced protection engineer.

Good luck.

__________________
Sundar
Register to Reply Good Answer (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Transformer Synchonization

07/14/2014 11:30 PM

Welcome to CR4! And good answer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#5

Re: Transformer Synchonization

08/06/2014 5:03 AM

Yes, if you have following as the same

Same impedance or close by eg. 10.7% and 10.5%

Same Voltages

Same Vector groups

Correct Same Phasing on Transformers

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); RAMConsult (1); Sundar30 (1); Tornado (2)

Previous in Forum: How to Calculate Disel Fuel Consumption   Next in Forum: Can it Handle?

Advertisement