Anonymous Poster #1

Capacity of T/F

07/17/2014 11:10 AM

If a distribution transformer of 11kv/433v is lying in front of you & there is no number or rating plate on it. What is the simple way to determine the capacity of that t/f ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Capacity of t/f

07/17/2014 11:36 AM

Whatsa t/f ??

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: Capacity of t/f

07/17/2014 12:28 PM

Go back to the manufacturer with the site name and the date it was supplied, Murphy. They ought to be able to find something in their records that might suffice.

Or check the installation's single line diagrams. It ought to be on those.

Or check its maintenance records. It ought to be in there.

Or check the voltage and protection settings both sides of it. That might give you a clue.

Otherwise it's scrap. Order a replacement and make sure you take better care of its documentation and its label next time. Shame on you! Why tear the label off? That's plain silly. And why throw its documentation away? Ridiculous!

__________________
Good moaning!
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Capacity of t/f

07/17/2014 1:18 PM

Open it up and count the turns?

Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: Capacity of t/f

07/17/2014 1:52 PM

This ought to be interesting. I think I'll sit back and watch.

Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Capacity of T/F

07/17/2014 3:58 PM

A rough indication of the t/f (transformer) rating can be found by looking at how large it is. You know the voltages and I am assuming it is a standard oil-filled type so physical size would be a good rough indication of capacity.

Have a look on the internet for similar transformers and find one that is of similar size, its capacity should be similar to the capacity of the transformer you are trying to figure out.

Alternatively contact your local power board (or similar), they may be able to tell you.

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: Capacity of T/F

07/17/2014 10:46 PM

That's OK, but depending on the age of the transformer it's of no reassurance.

I moved and reused a 50 year old 500KVA 11/.55KV transformer, it was bigger than a modern 1000KVA unit.
With modern design tank sizes have shrunk tremendously.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#13
In reply to #6

Re: Capacity of T/F

07/20/2014 3:24 PM

That's why it has to be of similar construction (and yes age) if you want a rough idea only. It is only a rough guide.

__________________
jack of all trades
Reply
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#7

Re: Capacity of T/F

07/18/2014 7:17 AM

If there is no rating plate on it, how do you even know the voltage it operates on?

__________________
rogerggbr
Reply Score 1 for Good Answer
Commentator

Join Date: Mar 2014
Posts: 75
#8
In reply to #7

Re: Capacity of T/F

07/18/2014 9:23 AM

It is possible to know the voltages by knowing where it's installed.

Reply
Commentator

Join Date: Mar 2014
Posts: 75
#9

Re: Capacity of T/F

07/18/2014 9:24 AM

Why do you want to determine that?

Reply
Participant

Join Date: Jul 2014
Posts: 1
#10
In reply to #9

Re: Capacity of T/F

07/18/2014 12:56 PM

Some junior staff brought to return/deposit as a damaged one but I have to take entry of its capacity in kva & oil capacity also

Reply Off Topic (Score 5)
Commentator

Join Date: Mar 2014
Posts: 75
#11
In reply to #10

Re: Capacity of T/F

07/18/2014 1:06 PM

For what purpose?

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #10

Re: Capacity of T/F

07/18/2014 2:19 PM

Have the junior staff call the agency who is returning it and have them identify it.

It's inconceivable that you would accept a damaged unit without supporting documentation from the returning agency.

I sense either negligence or incompetence here.

<Beam me up Scotty>

Reply Off Topic (Score 5)
Reply to Forum Thread 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (1); Blackpaper (3); Crabtree (1); jack of all trades (2); lyn (2); Pjagga19 (1); rogerggbr (1); SolarEagle (1); TonyS (1)

Previous in Forum: Type of CT Suitable for Oil Filled Transformer   Next in Forum: How We Can Improve The Power Factor Of Induction Generator?

Advertisement