Please share your experience on the following --
1) Whether resin cast CT (for example bar primary & 25 /50A secondary) can be used in mineral oil filled transformer.
2) What are the different types of CTs recommended for mineral oil filled transformer.
Thank you in advance for your help
Re: type of ct suitable for oil filled transformer
07/17/2014 8:58 AM
Excuse my ignorance, but what does CT stand for again?
07/17/2014 9:15 AM
Current Transformer
07/17/2014 9:26 AM
The transformer manufacturer is the best source of information, and the telephone is the quickest route to it.
07/17/2014 10:03 AM
A current transformer inside a oil filled transformer does not make sense to me.
Do you mean a CT instead of an oil filled transformer? Sort of as a replacement, alternative transformer?
Good Answers: 444
Re: Type of CT Suitable for Oil Filled Transformer
07/17/2014 10:16 AM
You need to be sure that the resin will withstand the oil that it is immersed in. Not all insulating materials can withstand constant immersion in hot transformer oil. Only the manufacturer should be relied upon for advice.
07/17/2014 2:34 PM
Pls, pardon my act of question in question! Pls. What are functions of current transformer in the circuit.
Good Answers: 444
07/17/2014 4:42 PM
Measure the current in a circuit without breaking the circuit to insert the meter.
Good Answers: 181
07/17/2014 10:33 PM
A UK company http://www.dk-moriarty.ltd.uk/ they will advise.
I've only ever installed one in tank CT in forty years, what are you doing?
07/18/2014 12:12 AM
Epoxy or any other resin cast are generally not used in oil of any type.
We manufacture CT's and for use in oil the CT's are not cast or varnished.
They are insulated with polyester (Melinex or Mylar) tape and then wrapped with a cotton tape. These are supported in an insulating frame over the cable or bushing and the oil is the actual insulation for the CT.
These are frequently used in transformers and the like, with one CT at each end of each coil to quickly identify any earth or leakage fault in the coil. Sometimes they are matched to the CT at the first circuit breaker to identify a fault between the coils and the circuit breaker
fsmit@dyne.com.au
08/19/2014 11:06 AM
Meramec makes bushing CTs for "in-oil" applications such transformers. Both metering and protection class.
http://www.meramec-electrical.com/pdfs/products/OBCT_sheet_web.pdf
See IEEE C57.13.1 for specific details